[Nut-upsuser] APC SmartUPS switches off with no reason
Ivan Kuznetsov
kia at solvo.ru
Wed Jul 9 11:08:26 UTC 2014
Hello
One our customer has two Linux HP-branded servers powered from "clasic"
APC Smart-UPS 2200 RM 2U (p/n SUA2200RMI2U). It is connected to first
server via RS232c port with APC-branded cable. We have installed NUT
2.6.4 with apcsmart driver. This setup works fine for months. Two weeks
ago all the hardware powered from the UPS started to switch off
occasionally while on line power. The UPS switchs off too and need to be
turn on manually. No any warnings or so logged by NUT. UPS load is
<25-30%, battery is ok. With disconnected control cable the UPS forks as
desired, no switch offs for 6 days. When customer connects the cable
back the UPS switchs off after ~12 hours. It looks like the UPS recives
'instant poweroff' command via interface with no reason
What can be a diagnostic procedure?
--
Regards, Ivan Kuznetsov
SOLVO ltd
More information about the Nut-upsuser
mailing list