[Nut-upsuser] Tripp Lite SMART3000RM2U (protocol 3003) running	time and charge?
    Charles Lepple 
    clepple at gmail.com
       
    Fri May 16 02:43:37 UTC 2014
    
    
  
On May 15, 2014, at 9:39 PM, Stefan Bruda wrote:
> What bugs be though is that I cannot seem to be able to read the
> remaining run time on battery.  The battery charge is also widely
> inaccurate (it drops to zero really fast and stays there).  I read
> somewhere that the usb.debug numbers may hold the key to this (at
> least to the running time that is), but I don't know what to do with
> them (and I can no longer find that piece of information...).
Here's where the battery.charge variable is calculated:
   https://github.com/networkupstools/nut/blob/master/drivers/tripplite_usb.c#L1099
   battery_charge = (unsigned)(s_value[5]);
(In that file, the 3003 protocol is denoted by "tl_model == TRIPP_LITE_SMARTPRO".)
Due to the command prefix characters in the protocol, the ups.debug.S hex values are actually indexed from 1 as follows:
              1  2  3  4  5  6  7
ups.debug.S: 31 30 30 00 28 30 0d '100..0.'
Hence, your s_value[5] yields 0x28 == 40%.
That said, a lot of information was either observed empirically, or taken from this email:
   http://lists.alioth.debian.org/pipermail/nut-upsuser/2005-September/000218.html
You will note that neither battery charge nor runtime is listed there.
It is possible that a better value for the state-of-chage could be calculated, similar to the other protocols:
   https://github.com/networkupstools/nut/blob/master/drivers/tripplite_usb.c#L1129
However, calculating runtime usually requires the UPS to do a battery test, and observe the voltage while under load. This unit might not be capable of doing that.
-- 
Charles Lepple
clepple at gmail
    
    