[Nut-upsuser] OpenUPS2 support in the HID driver?
Toomas Suurmets (Priv)
toomas at suurmets.com
Fri Nov 7 07:33:39 UTC 2014
Hi Charles,
Thanks for these efforts!
On 7.11.2014 6:24, Charles Lepple wrote:
> On Nov 6, 2014, at 1:44 PM, Toomas Suurmets (Priv)
> <toomas at suurmets.com <mailto:toomas at suurmets.com>> wrote:
>
>> Hi,
>>
>> Debug output of driver is attached, started with OpenUPS2 input feed
>> online @ 12V and going offline at 15th second of debug run.
>
> Thanks, the voltages seem to only be off by a factor of 10:
>
> Path: UPS.PowerSummary.Output.Voltage, Type: Feature, ReportID: 0x21,
> Offset: 0, Size: 16, Value: 122.69
> Path: UPS.PowerSummary.Output.Current, Type: Feature, ReportID: 0x21,
> Offset: 16, Size: 16, Value: 0
> Path: UPS.PowerSummary.Input.Voltage, Type: Feature, ReportID: 0x22,
> Offset: 0, Size: 16, Value: 122.17
>
> Not sure about the current scaling - I assumed it was also 10x too high.
>
> I pushed a new version (0.4; ignore 0.3) which should fix the voltage
> scaling.
>
> The runtime estimate seems high, but you might need to plot that over
> time to see what the scale factor should be for that. NUT usually
> reports it in seconds.
>
>> Second attached file is debug output of unsuccessful UPS shutdown
>> captured with command:
>>
>> /lib/nut/usbhid-ups -a openups -x productid=d005 -u root -DDD *-k*
>> 2>&1 |tee openups-d005-shut.log
>
> Not sure what to tell you - there is no shutdown command listed in the
> HID descriptor. I CC'd the author of the driver - maybe the
> manufacturer can provide more information?
>
> Same thing with the configuration variables. There are a few
> non-standard HID usage IDs at the end of the log, but it is not clear
> how to make use of them.
>
> --
> Charles Lepple
> clepple at gmail
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20141107/a3027471/attachment.html>
More information about the Nut-upsuser
mailing list