On 02.10.2014 03:42, Charles Lepple wrote:
> On Oct 1, 2014, at 5:07 AM, Tarvo.Tiits at automaatika.ee wrote:
>
>> Why is ups.status empty?
> If I understand the commit log for SVN r3590, then that revision was supposed to set the status to OL if the numeric state was 9 for ECO mode. It does not appear to do that:
>
> https://github.com/networkupstools/nut/commit/9cb2de3d9568aa382cc118b4385d97d5664c457b
>
> Is your UPS set to ECO mode? Can you do a snmpget on .1.3.6.1.4.1.4555.1.1.1.1.4.1.0?
>
UPS is on inverter, not ECO mode,
snmpget -v1 -c public 192.168.xxx.xxx .1.3.6.1.4.1.4555.1.1.1.1.4.1.0
SNMPv2-SMI::enterprises.4555.1.1.1.1.4.1.0 = INTEGER: 2