[Nut-upsuser] Socomec ITYS 3000 + Netvision upsmon output

Charles Lepple clepple at gmail.com
Thu Oct 2 12:15:29 UTC 2014


On Oct 2, 2014, at 1:53 AM, Tarvo Tiits <Tarvo.Tiits at automaatika.ee> wrote:

> On 02.10.2014 03:42, Charles Lepple wrote:
>> On Oct 1, 2014, at 5:07 AM, Tarvo.Tiits at automaatika.ee wrote:
>> 
>>> Why is ups.status empty?
>> If I understand the commit log for SVN r3590, then that revision was supposed to set the status to OL if the numeric state was 9 for ECO mode. It does not appear to do that:
>> 
>> https://github.com/networkupstools/nut/commit/9cb2de3d9568aa382cc118b4385d97d5664c457b
>> 
>> Is your UPS set to ECO mode? Can you do a snmpget on .1.3.6.1.4.1.4555.1.1.1.1.4.1.0?
>> 
> UPS is on inverter, not ECO mode,
> 
> snmpget -v1 -c public 192.168.xxx.xxx .1.3.6.1.4.1.4555.1.1.1.1.4.1.0
> SNMPv2-SMI::enterprises.4555.1.1.1.1.4.1.0 = INTEGER: 2

2 also is explicitly mapped to "". I'm wondering if your UPS has a different interpretation. Do you have a MIB file?

Also CC'ing Arnaud to see if he has any additional details. He may be interested in a full SNMP walk (please gzip and attach to the message).

-- 
Charles Lepple
clepple at gmail