Hello Arno,
Can apply the patch directly or should I recompile nut?
Best regards,
Panagiotis
On 3/4/2015 5:06 μμ, Arnaud Quette wrote:
> Hello Panagiotis
>
> 2015-04-03 14:28 GMT+02:00 Panagiotis Kritikakos
> <panagiotis.kritikakos at nikitec.gr
> <mailto:panagiotis.kritikakos at nikitec.gr>>:
>
> Hello Arno,
>
> Question: have you also tested oldmge-shut?
> Otherwise, that might be interesting to do so and send back
> the results of these tests...
>
> Yes, I've tried this as well with worse results unfortunately.
> This driver seems to be even more unstable. When it gets able to
> set communication with the UPS (which is not always the case), it
> usually lost it again after a while.
>
> ~# /usr/local/libexec/nut/oldmge-shut -DD -a ups-filesrv01
> Network UPS Tools - Eaton / SHUT driver 0.70 (2.7.2)
> 0.000000 debug level is '2'
> 0.000882 entering upsdrv_initups()
> 0.001019 entering shut_ups_start()
>
> 0.028445 Communication with UPS established
> 0.028457 entering shut_get_descriptor(n 21, 9)
> 0.111394 shut_wait_ack(): ACK received
> 0.185328 entering shut_get_descriptor(n 01, 18)
> 0.273455 shut_wait_ack(): ACK received
> 0.423238 Device Descriptor:
> bLength: 0x12
> bDescriptorType: 0x01
> bcdUSB: 0x0110
> bDeviceClass: 0x00
> bDeviceSubClass: 0x00
> bDeviceProtocol: 0x00
> bMaxPacketSize0: 0x08
> idVendor: 0x0463
> idProduct: 0xffff
> bcdDevice: 0x0100
> iManufacturer: 0x01
> iProduct: 0x02
> iSerialNumber: 0x03
> bNumConfigurations: 0x01
>
> 0.423251 entering shut_get_descriptor(n 22, 1538)
> 0.525087 shut_wait_ack(): ACK received
> 9.705471 Unable to get Report Descriptor
>
>
> It there a possibility to be an issue of the UPS, or the
> connection between the serial port of the machine and the UPS?
>
>
>
> thanks for the confirmation with oldmge-shut. I'm not astonished on
> the results, but was worth a try.
>
> I've double checked the related code difference for mge-shut between
> 2.7.1 and 2.7.2.
> Again, the only diff I see is the one pointed previously (setline...).
> So, it would be great if you could test this patch (through some
> reboots) and report back.
>
> Then, I don't think it's an issue with the device.
> There is a long run TODO (mentioned in the header of libshut.c) that
> is the baudrate negotiation.
> The driver still communicates at 2400bauds, which is not that much for
> such verbose units. We could go at least for 9600 on these units,
> which is 4 times faster already.
> This may cause some slowness and behavior issues as you're
> experiencing, under some circumstances.
> For example, the test using a 5SC750 on Linux (Debian Jessie) shows
> that report descriptor (size 1538) takes ~10 seconds to be retrieved,
> which is quite long.
> Then, even if this "new"mge-shut is a lot better than the oldmge-shut,
> it can still be perfected on the error handling (and not optimal
> cases), which you may be hitting.
> And finally, the notification handling could also help to poll less
> the unit, while being notified of critical status changes.
>
> cheers,
> Arno
> --
> Eaton Data Center Automation - Opensource Leader
> NUT (Network UPS Tools) Project Leader - http://www.networkupstools.org
> Debian Developer - http://www.debian.org
> Free Software Developer - http://arnaud.quette.fr
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20150406/fc74c7da/attachment.html>
More information about the Nut-upsuser
mailing list