[Nut-upsuser] fsd fails to notify slaves

Charles Lepple clepple at gmail.com
Tue Apr 21 23:55:03 UTC 2015


On Apr 21, 2015, at 12:09 PM, dmanye <dmanye at urv.cat> wrote:

> Apr 21 17:45:23 jessie641 upsmon[532]: FSD set on UPS smt750i at 10.21.102.241 failed: ERR ACCESS-DENIED
> Apr 21 17:45:23 jessie641 upsmon[532]: Executing automatic power-fail shutdown
> Apr 21 17:45:23 jessie641 upsmon[532]: Auto logout and shutdown proceeding
> 
> i think the problem may be the first line. do you know what can be the cause?

The MONITOR line in upsmon.conf needs to correspond to one of the user definitions in upsd.users, and that user needs "upsmon master" or "upsmon slave" permission.

Note that entries in upsd.users should probably be called "roles" to avoid confusion with system users in /etc/passwd, but that is how everything is named at the moment.

-- 
Charles Lepple
clepple at gmail