Greetings Charles;
I hope you had a nice Christmas, and will have a happy and prosperous new 
year in 2016.
You mentioned upsrw in a message earlier, so I ran it, and found the 
shutdown timeout was only 20 seconds.
gene at coyote:~$ upsrw myups
[input.transfer.high]
High voltage transfer point (V)
Type: STRING
Value: 140
[input.transfer.low]
Low voltage transfer point (V)
Type: STRING
Value: 88
[ups.delay.shutdown]
Interval to wait after shutdown with delay command (seconds)
Type: STRING
Value: 20
[ups.delay.start]
Interval to wait before (re)starting the load (seconds)
Type: STRING
Value: 30
That 20 seconds is insufficient to allow a gracefull shutdown on this 
system as it seems to need 40 or more seconds to begin a reboot by 
entering the BIOS post routine.
So I tried to reset that to 120 seconds, which the battery can do nicely, 
and I have a 20kw in the back yard that is up and running, lights back 
on in 16 or 17 seconds, so is 98% moot, but found I cannot, even as 
root, adjust this.
gene at coyote:~$ upsrw -s ups.delay.shutdown=120 myups
Username (gene): gene
Password: my user pw here
Unexpected response from upsd: ERR ACCESS-DENIED
Nut was never given a pw on this system. I, and ups however are members 
of group nut, and that has always seemed sufficient until now.
Obviously I don't have something adequately configured, the question of 
course is what?
Thanks.
Cheers, Gene Heskett
-- 
"There are four boxes to be used in defense of liberty:
 soap, ballot, jury, and ammo. Please use in that order."
-Ed Howdershelt (Author)