[Nut-upsuser] Ippon Smart Winner 3000 New
Андрей Тихомиров
admin at vampik.ru
Tue Mar 3 13:08:08 UTC 2015
Hello,
I've recently bought Ippon Smart Winner 3000 New (note the "New" in the
model name) and I can't make NUT to work with it.
Linux gateway 3.17.8-gentoo-r1 #1 SMP Mon Feb 16 13:46:11 MSK 2015
x86_64 Intel(R) Celeron(R) CPU 1037U @ 1.80GHz GenuineIntel GNU/Linux
Network UPS Tools 2.7.2
1) USB connection partially works using usbhid-ups driver, the problem
is that I can't issue any command to the UPS. Any command returns ERR
CMD-NOT-SUPPORTED error.
[nutdev1]
driver = "usbhid-ups"
port = "auto"
vendorid = "06DA"
productid = "FFFF"
product = "HID UPS"
serial = "S42140930054"
vendor = "PPC"
bus = "002"
# upsc nutdev1
battery.charge: 100
battery.runtime: 5329
battery.type: PbAc
battery.voltage: 82
battery.voltage.nominal: 72
device.mfr: PPC
device.model: HID UPS
device.serial: S42140930054
device.type: ups
driver.name: usbhid-ups
driver.parameter.bus: 002
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.product: HID UPS
driver.parameter.productid: FFFF
driver.parameter.serial: S42140930054
driver.parameter.vendor: PPC
driver.parameter.vendorid: 06DA
driver.version: 2.7.2
driver.version.data: Liebert HID 0.3
driver.version.internal: 0.38
ups.load: 9
ups.mfr: PPC
ups.model: HID UPS
ups.productid: ffff
ups.serial: S42140930054
ups.status: OL CHRG
ups.vendorid: 06da
# /lib/nut/usbhid-ups -DDD -a nutdev1
Network UPS Tools - Generic HID driver 0.38 (2.7.2)
USB communication driver 0.32
0.000000 debug level is '3'
0.001145 upsdrv_initups...
0.002890 Checking device (1D6B/0001) (004/001)
0.003366 Failed to open device, skipping. (Permission denied)
0.003806 Checking device (1D6B/0001) (003/001)
0.004149 Failed to open device, skipping. (Permission denied)
0.004454 Checking device (1D6B/0002) (001/001)
0.004797 Failed to open device, skipping. (Permission denied)
0.005128 Checking device (06DA/FFFF) (002/003)
0.534942 - VendorID: 06da
0.535595 - ProductID: ffff
0.536220 - Manufacturer: PPC
0.536590 - Product: HID UPS
0.537081 - Serial Number: S42140930054
0.537522 - Bus: 002
0.537977 Trying to match device
0.538536 Device matches
0.732116 HID descriptor, method 1: (9 bytes) => 09 21 11 01 00
01 22 55 05
0.732189 HID descriptor, method 2: (9 bytes) => 09 21 11 01 00
01 22 55 05
0.732199 HID descriptor length 1365
1.000679 Report Descriptor size = 1365
1.000731 Report Descriptor: (1365 bytes) => 05 84 09 04 a1 01 09
10 a1 00 09 12 a1
1.000750 00 09 13 85 20 75 08 95 01 15 00 26 ff 00 65 00 55 00
b1 03 06 ff ff 09 90
1.000767 85 21 b1 82 05 84 09 02 a1 02 09 60 85 27 75 08 26 ff
00 65 00 b1 83 09 60
1.000784 81 83 06 ff ff 09 74 b1 83 09 74 81 83 c0 05 84 09 58
85 24 b1 82 06 ff ff
1.000800 09 e3 85 e3 b1 82 09 45 85 25 75 20 27 ff ff ff 7f 66
01 10 b1 82 c0 05 84
1.000818 09 11 85 20 75 08 26 ff 00 65 00 b1 03 09 14 a1 00 09
15 b1 03 06 ff ff 09
1.000835 94 85 26 b1 83 05 84 09 02 a1 02 06 ff ff 09 79 85 27
b1 83 09 79 81 83 05
1.000851 84 09 62 b1 83 09 62 81 83 09 6d b1 83 09 6d 81 83 c0
c0 c0 05 84 09 1e a1
1.000868 81 09 42 85 14 66 01 f0 b1 83 09 40 85 15 67 21 d1 f0
00 55 07 b1 83 09 1f
1.000884 85 0b 65 00 55 00 b1 03 c0 09 1e a1 84 09 44 85 74 75
10 27 ff ff 00 00 66
1.000901 21 d1 55 07 b1 83 09 43 66 21 d1 b1 83 09 42 85 36 75
08 26 ff 00 66 01 f0
1.000918 55 00 b1 82 09 45 85 16 65 00 b1 83 09 40 85 72 67 21
d1 f0 00 55 07 b1 82
1.000935 09 1f 85 0b 65 00 55 00 b1 03 c0 09 18 a1 00 09 20 a1
81 09 1f 85 80 b1 03
1.000951 09 21 b1 03 09 02 a1 02 09 6c 85 81 b1 03 c0 c0 09 20
a1 82 09 57 85 8d 75
1.000968 20 15 ff 27 ff ff ff 7f 66 01 10 b1 82 09 56 85 90 b1
82 09 1f 85 80 75 08
1.000985 15 00 26 ff 00 65 00 b1 03 09 21 b1 03 09 02 a1 02 09
6c 85 81 b1 03 09 6b
1.001001 85 82 b1 83 09 6b 81 83 c0 06 ff ff 09 5d 85 87 75 20
27 ff ff ff 7f 66 01
1.001018 10 b1 82 09 5e 85 8a b1 82 c0 05 84 09 20 a1 83 09 57
85 8e 15 ff b1 82 09
1.001035 56 85 91 b1 82 09 1f 85 80 75 08 15 00 26 ff 00 65 00
b1 03 09 21 b1 03 09
1.001051 02 a1 02 09 6c 85 81 b1 03 09 6b 85 82 b1 83 09 6b 81
83 c0 06 ff ff 09 5d
1.001068 85 88 75 20 27 ff ff ff 7f 66 01 10 b1 82 09 5e 85 8b
b1 82 c0 06 ff ff 09
1.001085 c0 85 c0 75 08 26 ff 00 65 00 b1 82 05 84 09 19 85 80
b1 03 c0 09 16 a1 00
1.001101 06 ff ff 09 41 85 4a b1 03 05 84 09 1a a1 81 06 ff ff
09 43 85 73 b1 82 09
1.001118 94 85 c1 b1 82 05 84 09 1f 85 30 b1 03 09 32 85 31 75
10 27 ff ff 00 00 66
1.001135 01 f0 55 0f b1 83 09 1b 85 30 75 08 26 ff 00 65 00 55
00 b1 03 09 02 a1 02
1.001151 09 6e 85 2d b1 83 09 6e 81 83 09 6f b1 83 09 6f 81 83
09 64 85 32 b1 83 09
1.001168 64 81 83 09 63 b1 83 09 63 81 83 06 ff ff 09 78 b1 83
09 78 81 83 c0 05 84
1.001184 09 30 85 31 75 10 27 ff ff 00 00 67 21 d1 f0 00 55 07
b1 83 c0 05 84 09 1a
1.001201 a1 83 06 ff ff 09 46 85 39 75 08 26 ff 00 65 00 55 00
b1 82 05 84 09 1f 85
1.001218 30 b1 03 09 1b b1 03 09 02 a1 02 09 6d 85 3b b1 83 09
6d 81 83 c0 06 ff ff
1.001235 09 47 85 3a b1 82 c0 09 14 a1 00 09 15 85 40 b1 03 05
84 09 02 a1 02 09 6d
1.001251 85 41 b1 83 09 6d 81 83 06 ff ff 09 74 85 3e b1 83 09
74 81 83 09 75 b1 83
1.001268 09 75 81 83 c0 c0 05 84 09 1c a1 00 09 34 85 42 75 10
27 ff ff 00 00 66 21
1.001284 d1 55 07 b1 83 09 33 66 21 d1 b1 83 09 1f 85 40 75 08
26 ff 00 65 00 55 00
1.001301 b1 03 05 84 09 32 85 42 75 10 27 ff ff 00 00 66 01 f0
55 0f b1 83 06 ff ff
1.001318 09 53 85 4d 67 21 d1 f0 00 55 07 b1 82 05 84 09 54 85
48 b1 82 06 ff ff 09
1.001334 50 85 4e b1 82 05 84 09 53 85 47 b1 82 09 1d 85 40 75
08 26 ff 00 65 00 55
1.001351 00 b1 03 05 84 09 02 a1 02 06 ff ff 09 4a 85 49 65 00
b1 83 09 4a 81 83 c0
1.001368 05 84 09 30 85 42 75 10 27 ff ff 00 00 67 21 d1 f0 00
55 07 b1 83 c0 09 17
1.001384 85 40 75 08 26 ff 00 65 00 55 00 b1 03 c0 09 24 a1 00
09 5a 85 13 b1 82 05
1.001401 85 09 8d 85 0c b1 03 09 2c b1 03 05 84 09 40 85 0d 67
21 d1 f0 00 55 07 b1
1.001418 03 06 ff ff 09 95 85 0b 65 00 55 00 b1 03 05 84 09 57
85 09 75 20 15 ff 27
1.001435 ff ff ff 7f 66 01 10 b1 82 09 56 85 0a b1 82 05 85 09
83 85 0c 75 08 15 00
1.001579 26 ff 00 65 00 b1 03 05 84 09 1f 85 0b 65 00 b1 03 05
85 09 67 85 0c 65 00
1.001604 b1 03 09 89 85 10 65 00 b1 03 05 84 09 fd b1 03 06 ff
ff 09 f0 b1 03 05 84
1.001622 09 fe b1 03 05 84 09 ff b1 03 06 ff ff 09 f1 b1 03 09
f2 b1 03 09 e2 85 e2
1.001639 b1 83 05 84 09 35 85 07 65 00 b1 83 09 25 85 0b 65 00
b1 03 06 ff ff 09 94
1.001655 85 e1 65 00 b1 83 05 84 09 02 a1 02 05 85 09 d0 85 01
b1 83 09 42 b1 83 09
1.001672 44 b1 83 09 45 85 01 b1 83 06 ff ff 85 03 09 77 b1 83
09 77 81 83 05 84 09
1.001689 61 85 01 b1 83 09 62 85 02 b1 83 09 62 81 83 05 85 09
4b b1 83 09 4b 81 83
1.001706 05 84 09 65 b1 83 09 65 81 83 09 67 85 03 b1 83 09 67
81 83 c0 05 85 09 66
1.001722 85 06 65 00 b1 83 05 85 09 68 85 06 75 20 27 ff ff ff
7f 66 01 10 b1 83 05
1.001739 84 09 36 85 07 75 10 27 ff ff 00 00 67 01 00 01 00 55
0f b1 83 09 30 67 21
1.001756 d1 f0 00 55 06 b1 83 c0 06 ff ff 09 10 a1 81 09 f0 85
f0 75 08 95 27 15 00
1.001772 26 ff 00 65 00 55 00 b1 82 09 f1 85 f1 95 04 b1 82 09
ff 85 ff 95 01 b1 82
1.001780 c0 c0
1.001971 Using subdriver: Liebert HID 0.3
1.030501 Report[get]: (4 bytes) => 20 01 01 01
1.031181 Path: UPS.BatterySystem.Battery.BatteryID, Type:
Feature, ReportID: 0x20, Offset: 0, Size: 8, Value: 1
1.131175 Report[get]: (2 bytes) => 21 06
1.131795 Path: UPS.BatterySystem.Battery.ffff0090, Type:
Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 6
1.230941 Report[get]: (6 bytes) => 27 01 00 00 00 01
1.231500 Path: UPS.BatterySystem.Battery.PresentStatus.Present,
Type: Feature, ReportID: 0x27, Offset: 0, Size: 8, Value: 1
1.232184 Report[buf]: (6 bytes) => 27 01 00 00 00 01
1.232674 Path: UPS.BatterySystem.Battery.PresentStatus.Present,
Type: Input, ReportID: 0x27, Offset: 0, Size: 8, Value: 1
1.233188 Report[buf]: (6 bytes) => 27 01 00 00 00 01
1.233675 Path: UPS.BatterySystem.Battery.PresentStatus.ffff0074,
Type: Feature, ReportID: 0x27, Offset: 8, Size: 8, Value: 0
1.234186 Report[buf]: (6 bytes) => 27 01 00 00 00 01
1.234594 Path: UPS.BatterySystem.Battery.PresentStatus.ffff0074,
Type: Input, ReportID: 0x27, Offset: 8, Size: 8, Value: 0
1.531614 Report[get]: (2 bytes) => 24 01
1.532688 Path: UPS.BatterySystem.Battery.Test, Type: Feature,
ReportID: 0x24, Offset: 0, Size: 8, Value: 1
1.630323 Report[get]: (2 bytes) => e3 01
1.630858 Path: UPS.BatterySystem.Battery.ffff00e3, Type:
Feature, ReportID: 0xe3, Offset: 0, Size: 8, Value: 1
1.730337 Report[get]: (5 bytes) => 25 00 ea 24 00
1.731043 Path: UPS.BatterySystem.Battery.ffff0045, Type:
Feature, ReportID: 0x25, Offset: 0, Size: 32, Value: 2.4192e+06
1.731723 Report[buf]: (4 bytes) => 20 01 01 01
1.732152 Path: UPS.BatterySystem.BatterySystemID, Type: Feature,
ReportID: 0x20, Offset: 8, Size: 8, Value: 1
1.732591 Report[buf]: (4 bytes) => 20 01 01 01
1.733217 Path: UPS.BatterySystem.Charger.ChargerID, Type:
Feature, ReportID: 0x20, Offset: 16, Size: 8, Value: 1
1.830397 Report[get]: (2 bytes) => 26 04
1.830884 Path: UPS.BatterySystem.Charger.ffff0094, Type:
Feature, ReportID: 0x26, Offset: 0, Size: 8, Value: 4
1.831327 Report[buf]: (6 bytes) => 27 01 00 00 00 01
1.831639 Path: UPS.BatterySystem.Charger.PresentStatus.ffff0079,
Type: Feature, ReportID: 0x27, Offset: 16, Size: 8, Value: 0
1.831893 Report[buf]: (6 bytes) => 27 01 00 00 00 01
1.832134 Path: UPS.BatterySystem.Charger.PresentStatus.ffff0079,
Type: Input, ReportID: 0x27, Offset: 16, Size: 8, Value: 0
1.832284 Report[buf]: (6 bytes) => 27 01 00 00 00 01
1.832423 Path:
UPS.BatterySystem.Charger.PresentStatus.InternalFailure, Type: Feature,
ReportID: 0x27, Offset: 24, Size: 8, Value: 0
1.832664 Report[buf]: (6 bytes) => 27 01 00 00 00 01
1.832982 Path:
UPS.BatterySystem.Charger.PresentStatus.InternalFailure, Type: Input,
ReportID: 0x27, Offset: 24, Size: 8, Value: 0
1.833135 Report[buf]: (6 bytes) => 27 01 00 00 00 01
1.833271 Path: UPS.BatterySystem.Charger.PresentStatus.Used,
Type: Feature, ReportID: 0x27, Offset: 32, Size: 8, Value: 1
1.833521 Report[buf]: (6 bytes) => 27 01 00 00 00 01
1.833794 Path: UPS.BatterySystem.Charger.PresentStatus.Used,
Type: Input, ReportID: 0x27, Offset: 32, Size: 8, Value: 1
1.930273 Report[get]: (2 bytes) => 14 32
1.930683 Path: UPS.Flow.[1].ConfigFrequency, Type: Feature,
ReportID: 0x14, Offset: 0, Size: 8, Value: 50
2.131290 Report[get]: (2 bytes) => 15 dc
2.131867 Path: UPS.Flow.[1].ConfigVoltage, Type: Feature,
ReportID: 0x15, Offset: 0, Size: 8, Value: 220
2.230866 Report[get]: (6 bytes) => 0b 01 04 00 04 01
2.231140 Path: UPS.Flow.[1].FlowID, Type: Feature, ReportID:
0x0b, Offset: 0, Size: 8, Value: 1
2.331089 Report[get]: (5 bytes) => 74 8c 0a b8 0b
2.331355 Path: UPS.Flow.[4].ConfigActivePower, Type: Feature,
ReportID: 0x74, Offset: 0, Size: 16, Value: 2700
2.331528 Report[buf]: (5 bytes) => 74 8c 0a b8 0b
2.331686 Path: UPS.Flow.[4].ConfigApparentPower, Type: Feature,
ReportID: 0x74, Offset: 16, Size: 16, Value: 3000
2.430415 Report[get]: (2 bytes) => 36 32
2.430989 Path: UPS.Flow.[4].ConfigFrequency, Type: Feature,
ReportID: 0x36, Offset: 0, Size: 8, Value: 50
2.530421 Report[get]: (2 bytes) => 16 6e
2.530909 Path: UPS.Flow.[4].ConfigPercentLoad, Type: Feature,
ReportID: 0x16, Offset: 0, Size: 8, Value: 110
2.631091 Report[get]: (2 bytes) => 72 dc
2.631870 Path: UPS.Flow.[4].ConfigVoltage, Type: Feature,
ReportID: 0x72, Offset: 0, Size: 8, Value: 220
2.632624 Report[buf]: (6 bytes) => 0b 01 04 00 04 01
2.632834 Path: UPS.Flow.[4].FlowID, Type: Feature, ReportID:
0x0b, Offset: 8, Size: 8, Value: 4
2.830735 Report[get]: (8 bytes) => 80 04 00 04 01 04 02 01
2.831045 Path: UPS.OutletSystem.Outlet.[1].FlowID, Type:
Feature, ReportID: 0x80, Offset: 0, Size: 8, Value: 4
2.831151 Report[buf]: (8 bytes) => 80 04 00 04 01 04 02 01
2.831247 Path: UPS.OutletSystem.Outlet.[1].OutletID, Type:
Feature, ReportID: 0x80, Offset: 8, Size: 8, Value: 0
2.930398 Report[get]: (4 bytes) => 81 00 01 01
2.930651 Path:
UPS.OutletSystem.Outlet.[1].PresentStatus.Switchable, Type: Feature,
ReportID: 0x81, Offset: 0, Size: 8, Value: 0
3.031205 Report[get]: (5 bytes) => 8d ff ff ff ff
3.031638 Path: UPS.OutletSystem.Outlet.[2].DelayBeforeShutdown,
Type: Feature, ReportID: 0x8d, Offset: 0, Size: 32, Value: 0
3.130460 Report[get]: (5 bytes) => 90 ff ff ff ff
3.131092 Path: UPS.OutletSystem.Outlet.[2].DelayBeforeStartup,
Type: Feature, ReportID: 0x90, Offset: 0, Size: 32, Value: 0
3.131535 Report[buf]: (8 bytes) => 80 04 00 04 01 04 02 01
3.132270 Path: UPS.OutletSystem.Outlet.[2].FlowID, Type:
Feature, ReportID: 0x80, Offset: 16, Size: 8, Value: 4
3.132771 Report[buf]: (8 bytes) => 80 04 00 04 01 04 02 01
3.132973 Path: UPS.OutletSystem.Outlet.[2].OutletID, Type:
Feature, ReportID: 0x80, Offset: 24, Size: 8, Value: 1
3.133138 Report[buf]: (4 bytes) => 81 00 01 01
3.133391 Path:
UPS.OutletSystem.Outlet.[2].PresentStatus.Switchable, Type: Feature,
ReportID: 0x81, Offset: 8, Size: 8, Value: 1
3.230608 Report[get]: (3 bytes) => 82 01 01
3.231123 Path:
UPS.OutletSystem.Outlet.[2].PresentStatus.SwitchOn/Off, Type: Feature,
ReportID: 0x82, Offset: 0, Size: 8, Value: 1
3.231862 Report[buf]: (3 bytes) => 82 01 01
3.232091 Path:
UPS.OutletSystem.Outlet.[2].PresentStatus.SwitchOn/Off, Type: Input,
ReportID: 0x82, Offset: 0, Size: 8, Value: 1
3.330450 Report[get]: (5 bytes) => 87 ff ff 00 00
3.330727 Path: UPS.OutletSystem.Outlet.[2].ffff005d, Type:
Feature, ReportID: 0x87, Offset: 0, Size: 32, Value: 65535
3.431196 Report[get]: (5 bytes) => 8a 01 00 00 00
3.431399 Path: UPS.OutletSystem.Outlet.[2].ffff005e, Type:
Feature, ReportID: 0x8a, Offset: 0, Size: 32, Value: 1
3.530305 Report[get]: (5 bytes) => 8e ff ff ff ff
3.530617 Path: UPS.OutletSystem.Outlet.[3].DelayBeforeShutdown,
Type: Feature, ReportID: 0x8e, Offset: 0, Size: 32, Value: 0
3.631051 Report[get]: (5 bytes) => 91 ff ff ff ff
3.631851 Path: UPS.OutletSystem.Outlet.[3].DelayBeforeStartup,
Type: Feature, ReportID: 0x91, Offset: 0, Size: 32, Value: 0
3.632372 Report[buf]: (8 bytes) => 80 04 00 04 01 04 02 01
3.632672 Path: UPS.OutletSystem.Outlet.[3].FlowID, Type:
Feature, ReportID: 0x80, Offset: 32, Size: 8, Value: 4
3.633109 Report[buf]: (8 bytes) => 80 04 00 04 01 04 02 01
3.633506 Path: UPS.OutletSystem.Outlet.[3].OutletID, Type:
Feature, ReportID: 0x80, Offset: 40, Size: 8, Value: 2
3.633751 Report[buf]: (4 bytes) => 81 00 01 01
3.633945 Path:
UPS.OutletSystem.Outlet.[3].PresentStatus.Switchable, Type: Feature,
ReportID: 0x81, Offset: 16, Size: 8, Value: 1
3.634412 Report[buf]: (3 bytes) => 82 01 01
3.634624 Path:
UPS.OutletSystem.Outlet.[3].PresentStatus.SwitchOn/Off, Type: Feature,
ReportID: 0x82, Offset: 8, Size: 8, Value: 1
3.634942 Report[buf]: (3 bytes) => 82 01 01
3.635139 Path:
UPS.OutletSystem.Outlet.[3].PresentStatus.SwitchOn/Off, Type: Input,
ReportID: 0x82, Offset: 8, Size: 8, Value: 1
3.731298 Report[get]: (5 bytes) => 88 ff ff 00 00
3.731747 Path: UPS.OutletSystem.Outlet.[3].ffff005d, Type:
Feature, ReportID: 0x88, Offset: 0, Size: 32, Value: 65535
3.830802 Report[get]: (5 bytes) => 8b 03 00 00 00
3.831517 Path: UPS.OutletSystem.Outlet.[3].ffff005e, Type:
Feature, ReportID: 0x8b, Offset: 0, Size: 32, Value: 3
3.930921 Report[get]: (2 bytes) => c0 02
3.931449 Path: UPS.OutletSystem.ffff00c0, Type: Feature,
ReportID: 0xc0, Offset: 0, Size: 8, Value: 2
3.931939 Report[buf]: (8 bytes) => 80 04 00 04 01 04 02 01
3.932184 Path: UPS.OutletSystem.OutletSystemID, Type: Feature,
ReportID: 0x80, Offset: 48, Size: 8, Value: 1
4.030661 Report[get]: (2 bytes) => 4a 01
4.031178 Path: UPS.PowerConverter.ffff0041, Type: Feature,
ReportID: 0x4a, Offset: 0, Size: 8, Value: 1
4.130639 Report[get]: (2 bytes) => 73 01
4.131135 Path: UPS.PowerConverter.Input.[1].ffff0043, Type:
Feature, ReportID: 0x73, Offset: 0, Size: 8, Value: 1
4.230445 Report[get]: (2 bytes) => c1 00
4.230930 Path: UPS.PowerConverter.Input.[1].ffff0094, Type:
Feature, ReportID: 0xc1, Offset: 0, Size: 8, Value: 0
4.330787 Report[get]: (5 bytes) => 30 01 01 03 03
4.331293 Path: UPS.PowerConverter.Input.[1].FlowID, Type:
Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 1
4.430448 Report[get]: (5 bytes) => 31 f3 01 e4 00
4.430934 Path: UPS.PowerConverter.Input.[1].Frequency, Type:
Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 49.9
4.431102 Report[buf]: (5 bytes) => 30 01 01 03 03
4.431316 Path: UPS.PowerConverter.Input.[1].InputID, Type:
Feature, ReportID: 0x30, Offset: 8, Size: 8, Value: 1
4.530740 Report[get]: (3 bytes) => 2d 00 00
4.531001 Path: UPS.PowerConverter.Input.[1].PresentStatus.Boost,
Type: Feature, ReportID: 0x2d, Offset: 0, Size: 8, Value: 0
4.531131 Report[buf]: (3 bytes) => 2d 00 00
4.531210 Path: UPS.PowerConverter.Input.[1].PresentStatus.Boost,
Type: Input, ReportID: 0x2d, Offset: 0, Size: 8, Value: 0
4.531332 Report[buf]: (3 bytes) => 2d 00 00
4.531409 Path: UPS.PowerConverter.Input.[1].PresentStatus.Buck,
Type: Feature, ReportID: 0x2d, Offset: 8, Size: 8, Value: 0
4.531529 Report[buf]: (3 bytes) => 2d 00 00
4.531606 Path: UPS.PowerConverter.Input.[1].PresentStatus.Buck,
Type: Input, ReportID: 0x2d, Offset: 8, Size: 8, Value: 0
4.630485 Report[get]: (4 bytes) => 32 00 00 00
4.631051 Path:
UPS.PowerConverter.Input.[1].PresentStatus.FrequencyOutOfRange, Type:
Feature, ReportID: 0x32, Offset: 0, Size: 8, Value: 0
4.631263 Report[buf]: (4 bytes) => 32 00 00 00
4.631569 Path:
UPS.PowerConverter.Input.[1].PresentStatus.FrequencyOutOfRange, Type:
Input, ReportID: 0x32, Offset: 0, Size: 8, Value: 0
4.631761 Report[buf]: (4 bytes) => 32 00 00 00
4.631830 Path:
UPS.PowerConverter.Input.[1].PresentStatus.VoltageOutOfRange, Type:
Feature, ReportID: 0x32, Offset: 8, Size: 8, Value: 0
4.631894 Report[buf]: (4 bytes) => 32 00 00 00
4.632403 Path:
UPS.PowerConverter.Input.[1].PresentStatus.VoltageOutOfRange, Type:
Input, ReportID: 0x32, Offset: 8, Size: 8, Value: 0
4.632475 Report[buf]: (4 bytes) => 32 00 00 00
4.632542 Path:
UPS.PowerConverter.Input.[1].PresentStatus.ffff0078, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 8, Value: 0
4.632617 Report[buf]: (4 bytes) => 32 00 00 00
4.632682 Path:
UPS.PowerConverter.Input.[1].PresentStatus.ffff0078, Type: Input,
ReportID: 0x32, Offset: 16, Size: 8, Value: 0
4.632743 Report[buf]: (5 bytes) => 31 f3 01 e4 00
4.632810 Path: UPS.PowerConverter.Input.[1].Voltage, Type:
Feature, ReportID: 0x31, Offset: 16, Size: 16, Value: 228
4.731148 Report[get]: (2 bytes) => 39 00
4.731346 Path: UPS.PowerConverter.Input.[3].ffff0046, Type:
Feature, ReportID: 0x39, Offset: 0, Size: 8, Value: 0
4.731460 Report[buf]: (5 bytes) => 30 01 01 03 03
4.731528 Path: UPS.PowerConverter.Input.[3].FlowID, Type:
Feature, ReportID: 0x30, Offset: 16, Size: 8, Value: 3
4.731589 Report[buf]: (5 bytes) => 30 01 01 03 03
4.731652 Path: UPS.PowerConverter.Input.[3].InputID, Type:
Feature, ReportID: 0x30, Offset: 24, Size: 8, Value: 3
4.830307 Report[get]: (2 bytes) => 3b 01
4.830440 Path: UPS.PowerConverter.Input.[3].PresentStatus.Used,
Type: Feature, ReportID: 0x3b, Offset: 0, Size: 8, Value: 1
4.830501 Report[buf]: (2 bytes) => 3b 01
4.830567 Path: UPS.PowerConverter.Input.[3].PresentStatus.Used,
Type: Input, ReportID: 0x3b, Offset: 0, Size: 8, Value: 1
5.131046 Report[get]: (2 bytes) => 3a 01
5.131202 Path: UPS.PowerConverter.Input.[3].ffff0047, Type:
Feature, ReportID: 0x3a, Offset: 0, Size: 8, Value: 1
5.230660 Report[get]: (5 bytes) => 40 01 04 01 01
5.231096 Path: UPS.PowerConverter.ffff0014.ffff0015, Type:
Feature, ReportID: 0x40, Offset: 0, Size: 8, Value: 1
5.330530 Report[get]: (2 bytes) => 41 00
5.331054 Path: UPS.PowerConverter.ffff0014.PresentStatus.Used,
Type: Feature, ReportID: 0x41, Offset: 0, Size: 8, Value: 0
5.331220 Report[buf]: (2 bytes) => 41 00
5.331545 Path: UPS.PowerConverter.ffff0014.PresentStatus.Used,
Type: Input, ReportID: 0x41, Offset: 0, Size: 8, Value: 0
5.430677 Report[get]: (3 bytes) => 3e 00 00
5.430801 Path:
UPS.PowerConverter.ffff0014.PresentStatus.ffff0074, Type: Feature,
ReportID: 0x3e, Offset: 0, Size: 8, Value: 0
5.430857 Report[buf]: (3 bytes) => 3e 00 00
5.430916 Path:
UPS.PowerConverter.ffff0014.PresentStatus.ffff0074, Type: Input,
ReportID: 0x3e, Offset: 0, Size: 8, Value: 0
5.430970 Report[buf]: (3 bytes) => 3e 00 00
5.431028 Path:
UPS.PowerConverter.ffff0014.PresentStatus.ffff0075, Type: Feature,
ReportID: 0x3e, Offset: 8, Size: 8, Value: 0
5.431841 Report[buf]: (3 bytes) => 3e 00 00
5.431930 Path:
UPS.PowerConverter.ffff0014.PresentStatus.ffff0075, Type: Input,
ReportID: 0x3e, Offset: 8, Size: 8, Value: 0
5.532263 Report[get]: (9 bytes) => 42 e5 00 1e 01 f3 01 e3 00
5.532393 Path: UPS.PowerConverter.Output.ActivePower, Type:
Feature, ReportID: 0x42, Offset: 0, Size: 16, Value: 229
5.532515 Report[buf]: (9 bytes) => 42 e5 00 1e 01 f3 01 e3 00
5.532586 Path: UPS.PowerConverter.Output.ApparentPower, Type:
Feature, ReportID: 0x42, Offset: 16, Size: 16, Value: 286
5.532822 Report[buf]: (5 bytes) => 40 01 04 01 01
5.533057 Path: UPS.PowerConverter.Output.FlowID, Type: Feature,
ReportID: 0x40, Offset: 8, Size: 8, Value: 4
5.533489 Report[buf]: (9 bytes) => 42 e5 00 1e 01 f3 01 e3 00
5.533761 Path: UPS.PowerConverter.Output.Frequency, Type:
Feature, ReportID: 0x42, Offset: 32, Size: 16, Value: 49.9
5.839206 Report[get]: (3 bytes) => 4d e9 00
5.839332 Path: UPS.PowerConverter.Output.ffff0053, Type:
Feature, ReportID: 0x4d, Offset: 0, Size: 16, Value: 233
5.930151 Report[get]: (3 bytes) => 48 08 01
5.930232 Path: UPS.PowerConverter.Output.HighVoltageTransfer,
Type: Feature, ReportID: 0x48, Offset: 0, Size: 16, Value: 264
6.031184 Report[get]: (3 bytes) => 4e c6 00
6.031741 Path: UPS.PowerConverter.Output.ffff0050, Type:
Feature, ReportID: 0x4e, Offset: 0, Size: 16, Value: 198
6.130606 Report[get]: (3 bytes) => 47 b0 00
6.130747 Path: UPS.PowerConverter.Output.LowVoltageTransfer,
Type: Feature, ReportID: 0x47, Offset: 0, Size: 16, Value: 176
6.130812 Report[buf]: (5 bytes) => 40 01 04 01 01
6.130879 Path: UPS.PowerConverter.Output.OutputID, Type:
Feature, ReportID: 0x40, Offset: 16, Size: 8, Value: 1
6.231055 Report[get]: (2 bytes) => 49 00
6.231557 Path: UPS.PowerConverter.Output.PresentStatus.ffff004a,
Type: Feature, ReportID: 0x49, Offset: 0, Size: 8, Value: 0
6.231641 Report[buf]: (2 bytes) => 49 00
6.231731 Path: UPS.PowerConverter.Output.PresentStatus.ffff004a,
Type: Input, ReportID: 0x49, Offset: 0, Size: 8, Value: 0
6.232688 Report[buf]: (9 bytes) => 42 e5 00 1e 01 f3 01 e3 00
6.233234 Path: UPS.PowerConverter.Output.Voltage, Type: Feature,
ReportID: 0x42, Offset: 48, Size: 16, Value: 227
6.233561 Report[buf]: (5 bytes) => 40 01 04 01 01
6.233917 Path: UPS.PowerConverter.PowerConverterID, Type:
Feature, ReportID: 0x40, Offset: 24, Size: 8, Value: 1
6.530351 Report[get]: (2 bytes) => 13 02
6.530812 Path: UPS.PowerSummary.AudibleAlarmControl, Type:
Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 2
6.631077 Report[get]: (5 bytes) => 0c 01 02 64 64
6.631538 Path: UPS.PowerSummary.CapacityGranularity1, Type:
Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 1
6.631714 Report[buf]: (5 bytes) => 0c 01 02 64 64
6.632060 Path: UPS.PowerSummary.CapacityMode, Type: Feature,
ReportID: 0x0c, Offset: 8, Size: 8, Value: 2
6.730422 Report[get]: (2 bytes) => 0d 48
6.730923 Path: UPS.PowerSummary.ConfigVoltage, Type: Feature,
ReportID: 0x0d, Offset: 0, Size: 8, Value: 72
6.830997 Report[get]: (6 bytes) => 0b 01 04 00 04 01
6.831486 Path: UPS.PowerSummary.ffff0095, Type: Feature,
ReportID: 0x0b, Offset: 16, Size: 8, Value: 0
6.930501 Report[get]: (5 bytes) => 09 ff ff ff ff
6.931536 Path: UPS.PowerSummary.DelayBeforeShutdown, Type:
Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
7.030611 Report[get]: (5 bytes) => 0a ff ff ff ff
7.030862 Path: UPS.PowerSummary.DelayBeforeStartup, Type:
Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
7.031017 Report[buf]: (5 bytes) => 0c 01 02 64 64
7.031154 Path: UPS.PowerSummary.DesignCapacity, Type: Feature,
ReportID: 0x0c, Offset: 16, Size: 8, Value: 100
7.031211 Report[buf]: (6 bytes) => 0b 01 04 00 04 01
7.031481 Path: UPS.PowerSummary.FlowID, Type: Feature, ReportID:
0x0b, Offset: 24, Size: 8, Value: 4
7.031669 Report[buf]: (5 bytes) => 0c 01 02 64 64
7.031805 Path: UPS.PowerSummary.FullChargeCapacity, Type:
Feature, ReportID: 0x0c, Offset: 24, Size: 8, Value: 100
7.131020 Report[get]: (8 bytes) => 10 05 01 03 02 04 06 08
7.131474 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature,
ReportID: 0x10, Offset: 0, Size: 8, Value: 5
7.131663 Report[buf]: (8 bytes) => 10 05 01 03 02 04 06 08
7.131910 Path: UPS.PowerSummary.iManufacturer, Type: Feature,
ReportID: 0x10, Offset: 8, Size: 8, Value: 1
7.132372 Report[buf]: (8 bytes) => 10 05 01 03 02 04 06 08
7.132719 Path: UPS.PowerSummary.ffff00f0, Type: Feature,
ReportID: 0x10, Offset: 16, Size: 8, Value: 3
7.132933 Report[buf]: (8 bytes) => 10 05 01 03 02 04 06 08
7.133176 Path: UPS.PowerSummary.iProduct, Type: Feature,
ReportID: 0x10, Offset: 24, Size: 8, Value: 2
7.133239 Report[buf]: (8 bytes) => 10 05 01 03 02 04 06 08
7.133426 Path: UPS.PowerSummary.iSerialNumber, Type: Feature,
ReportID: 0x10, Offset: 32, Size: 8, Value: 4
7.133578 Report[buf]: (8 bytes) => 10 05 01 03 02 04 06 08
7.133643 Path: UPS.PowerSummary.ffff00f1, Type: Feature,
ReportID: 0x10, Offset: 40, Size: 8, Value: 6
7.133709 Report[buf]: (8 bytes) => 10 05 01 03 02 04 06 08
7.134126 Path: UPS.PowerSummary.ffff00f2, Type: Feature,
ReportID: 0x10, Offset: 48, Size: 8, Value: 8
7.231265 Report[get]: (2 bytes) => e2 0c
7.231779 Path: UPS.PowerSummary.ffff00e2, Type: Feature,
ReportID: 0xe2, Offset: 0, Size: 8, Value: 12
7.330739 Report[get]: (6 bytes) => 07 09 b8 0b 31 03
7.331204 Path: UPS.PowerSummary.PercentLoad, Type: Feature,
ReportID: 0x07, Offset: 0, Size: 8, Value: 9
7.331332 Report[buf]: (6 bytes) => 0b 01 04 00 04 01
7.331733 Path: UPS.PowerSummary.PowerSummaryID, Type: Feature,
ReportID: 0x0b, Offset: 32, Size: 8, Value: 1
7.430670 Report[get]: (2 bytes) => e1 03
7.430941 Path: UPS.PowerSummary.ffff0094, Type: Feature,
ReportID: 0xe1, Offset: 0, Size: 8, Value: 3
7.530374 Report[get]: (6 bytes) => 01 01 00 01 00 01
7.530639 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type:
Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
7.530810 Report[buf]: (6 bytes) => 01 01 00 01 00 01
7.530962 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
7.531025 Report[buf]: (6 bytes) => 01 01 00 01 00 01
7.531343 Path: UPS.PowerSummary.PresentStatus.Charging, Type:
Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
7.531406 Report[buf]: (6 bytes) => 01 01 00 01 00 01
7.531469 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
7.630383 Report[get]: (3 bytes) => 03 00 00
7.630522 Path: UPS.PowerSummary.PresentStatus.ffff0077, Type:
Feature, ReportID: 0x03, Offset: 0, Size: 8, Value: 0
7.630593 Report[buf]: (3 bytes) => 03 00 00
7.630665 Path: UPS.PowerSummary.PresentStatus.ffff0077, Type:
Input, ReportID: 0x03, Offset: 0, Size: 8, Value: 0
7.630735 Report[buf]: (6 bytes) => 01 01 00 01 00 01
7.631040 Path: UPS.PowerSummary.PresentStatus.Good, Type:
Feature, ReportID: 0x01, Offset: 32, Size: 8, Value: 1
7.730654 Report[get]: (4 bytes) => 02 00 00 00
7.730953 Path: UPS.PowerSummary.PresentStatus.InternalFailure,
Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 0
7.731457 Report[buf]: (4 bytes) => 02 00 00 00
7.731538 Path: UPS.PowerSummary.PresentStatus.InternalFailure,
Type: Input, ReportID: 0x02, Offset: 0, Size: 8, Value: 0
7.731719 Report[buf]: (4 bytes) => 02 00 00 00
7.731794 Path: UPS.PowerSummary.PresentStatus.NeedReplacement,
Type: Feature, ReportID: 0x02, Offset: 8, Size: 8, Value: 0
7.731860 Report[buf]: (4 bytes) => 02 00 00 00
7.731930 Path: UPS.PowerSummary.PresentStatus.NeedReplacement,
Type: Input, ReportID: 0x02, Offset: 8, Size: 8, Value: 0
7.732145 Report[buf]: (4 bytes) => 02 00 00 00
7.732219 Path: UPS.PowerSummary.PresentStatus.Overload, Type:
Feature, ReportID: 0x02, Offset: 16, Size: 8, Value: 0
7.732286 Report[buf]: (4 bytes) => 02 00 00 00
7.732548 Path: UPS.PowerSummary.PresentStatus.Overload, Type:
Input, ReportID: 0x02, Offset: 16, Size: 8, Value: 0
7.732953 Report[buf]: (3 bytes) => 03 00 00
7.733034 Path: UPS.PowerSummary.PresentStatus.OverTemperature,
Type: Feature, ReportID: 0x03, Offset: 8, Size: 8, Value: 0
7.733101 Report[buf]: (3 bytes) => 03 00 00
7.733172 Path: UPS.PowerSummary.PresentStatus.OverTemperature,
Type: Input, ReportID: 0x03, Offset: 8, Size: 8, Value: 0
7.830110 Report[get]: (6 bytes) => 06 64 d1 14 00 00
7.830187 Path: UPS.PowerSummary.RemainingCapacity, Type:
Feature, ReportID: 0x06, Offset: 0, Size: 8, Value: 100
7.830219 Report[buf]: (6 bytes) => 06 64 d1 14 00 00
7.830252 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature,
ReportID: 0x06, Offset: 8, Size: 32, Value: 5329
7.830284 Report[buf]: (6 bytes) => 07 09 b8 0b 31 03
7.830316 Path: UPS.PowerSummary.Temperature, Type: Feature,
ReportID: 0x07, Offset: 8, Size: 16, Value: 300
7.830345 Report[buf]: (6 bytes) => 07 09 b8 0b 31 03
7.830377 Path: UPS.PowerSummary.Voltage, Type: Feature,
ReportID: 0x07, Offset: 24, Size: 16, Value: 81.7
7.934660 Report[get]: (33 bytes) => 06 64 d1 14 00 00 09 08 01
00 25 01 f4 01 e3 00
7.934817 09 64 d1 14 00 00 b8 0b 31 03 06 32 dc 8c 0a b8 0b
7.934935 Path: UPS.ffff0010.[1].ffff00f0, Type: Feature,
ReportID: 0xf0, Offset: 0, Size: 8, Value: 100
8.031185 Report[get]: (5 bytes) => 06 64 d1 14 00
8.031342 Path: UPS.ffff0010.[1].ffff00f1, Type: Feature,
ReportID: 0xf1, Offset: 0, Size: 8, Value: 100
8.130742 Report[get]: (2 bytes) => ff 00
8.130956 Path: UPS.ffff0010.[1].ffff00ff, Type: Feature,
ReportID: 0xff, Offset: 0, Size: 8, Value: 0
8.131057 Report descriptor retrieved (Reportlen = 1365)
8.131407 Found HID device
8.131463 Detected a UPS: PPC/HID UPS
8.132010 Report[buf]: (6 bytes) => 07 09 b8 0b 31 03
8.132247 Path: UPS.PowerSummary.Voltage, Type: Feature,
ReportID: 0x07, Offset: 24, Size: 16, Value: 81.7
8.132340 Report[buf]: (2 bytes) => 0d 48
8.132426 Path: UPS.PowerSummary.ConfigVoltage, Type: Feature,
ReportID: 0x0d, Offset: 0, Size: 8, Value: 72
8.132536 Report[buf]: (6 bytes) => 06 64 d1 14 00 00
8.132595 Path: UPS.PowerSummary.RemainingCapacity, Type:
Feature, ReportID: 0x06, Offset: 0, Size: 8, Value: 100
8.132685 Report[buf]: (6 bytes) => 06 64 d1 14 00 00
8.132751 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature,
ReportID: 0x06, Offset: 8, Size: 32, Value: 5329
8.132832 Report[buf]: (8 bytes) => 10 05 01 03 02 04 06 08
8.133335 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature,
ReportID: 0x10, Offset: 0, Size: 8, Value: 5
8.332226 Report[buf]: (6 bytes) => 07 09 b8 0b 31 03
8.332379 Path: UPS.PowerSummary.PercentLoad, Type: Feature,
ReportID: 0x07, Offset: 0, Size: 8, Value: 9
8.332548 Report[buf]: (6 bytes) => 01 01 00 01 00 01
8.333254 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type:
Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
8.333772 Report[buf]: (6 bytes) => 01 01 00 01 00 01
8.334178 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
8.334712 Report[buf]: (6 bytes) => 01 01 00 01 00 01
8.334883 Path: UPS.PowerSummary.PresentStatus.Charging, Type:
Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
8.335067 Report[buf]: (6 bytes) => 01 01 00 01 00 01
8.335310 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
8.335386 Report[buf]: (4 bytes) => 02 00 00 00
8.335633 Path: UPS.PowerSummary.PresentStatus.Overload, Type:
Feature, ReportID: 0x02, Offset: 16, Size: 8, Value: 0
8.335705 find_nut_info: unknown info type: load.off.delay
8.335865 find_nut_info: unknown info type: load.on.delay
8.336073 find_nut_info: unknown info type: load.off.delay
8.336152 upsdrv_initinfo...
8.336313 upsdrv_updateinfo...
8.587906 libusb_get_interrupt: Connection timed out
8.588490 Got 0 HID objects...
8.588658 Quick update...
8.588984 Report[buf]: (6 bytes) => 01 01 00 01 00 01
8.589247 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type:
Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
8.589321 Report[buf]: (6 bytes) => 01 01 00 01 00 01
8.589617 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
8.589701 Report[buf]: (6 bytes) => 01 01 00 01 00 01
8.589771 Path: UPS.PowerSummary.PresentStatus.Charging, Type:
Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
8.590150 Report[buf]: (6 bytes) => 01 01 00 01 00 01
8.590230 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
8.590642 dstate_init: sock /var/lib/nut/usbhid-ups-nutdev1 open
on fd 14
8.591460 upsdrv_updateinfo...
8.842714 libusb_get_interrupt: Connection timed out
8.843198 Got 0 HID objects...
8.843415 Quick update...
8.843622 Report[buf]: (6 bytes) => 01 01 00 01 00 01
8.843767 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type:
Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
8.844083 Report[buf]: (6 bytes) => 01 01 00 01 00 01
8.844315 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
8.844382 Report[buf]: (6 bytes) => 01 01 00 01 00 01
8.844438 Path: UPS.PowerSummary.PresentStatus.Charging, Type:
Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
8.844494 Report[buf]: (6 bytes) => 01 01 00 01 00 01
8.844849 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
10.593364 upsdrv_updateinfo...
10.844598 libusb_get_interrupt: Connection timed out
10.844974 Got 0 HID objects...
10.845061 Quick update...
10.931051 Report[get]: (6 bytes) => 01 01 00 01 00 01
10.931559 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type:
Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
10.931924 Report[buf]: (6 bytes) => 01 01 00 01 00 01
10.932126 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
10.932216 Report[buf]: (6 bytes) => 01 01 00 01 00 01
10.932360 Path: UPS.PowerSummary.PresentStatus.Charging, Type:
Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
10.932816 Report[buf]: (6 bytes) => 01 01 00 01 00 01
10.932895 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
^C
# upscmd -l nutdev1
Instant commands supported on UPS [nutdev1]:
2) RS-232 connection. I can't find any suitable driver. I've tried
blazer_ser, nutdrv_qx, liebert and some others - it didn't work.
The UPS sends the following binary data to the serial port every 3 or 4
seconds:
# od -t x1 < /dev/ttyS0
0000000 ab 01 35 81 01 01 00 ea 24 00 32 dc ff ff ff ff
0000020 ff ff ff ff ff ff 00 00 01 00 00 00 ff ff ff ff
0000040 ff ff ff ff ff ff 00 00 03 00 00 00 01 00 00 01
0000060 02 ff ff ff ff ff ff ff ff 94 ab 02 1d 81 29 00
0000100 00 29 00 00 00 00 00 00 29 00 00 00 00 00 00 04
0000120 00 23 23 00 00 23 00 03 23 00 23 84 ab 03 28 81
0000140 f4 01 e4 00 e5 00 1f 01 f4 01 e3 00 09 64 a2 14
0000160 00 00 b5 0b 31 03 06 32 dc 8c 0a b8 0b 6e e9 00
^C
# od -t x1 < /dev/ttyS0
0000000 ab 01 35 81 01 01 00 ea 24 00 32 dc ff ff ff ff
0000020 ff ff ff ff ff ff 00 00 01 00 00 00 ff ff ff ff
0000040 ff ff ff ff ff ff 00 00 03 00 00 00 01 00 00 01
0000060 02 ff ff ff ff ff ff ff ff 94 ab 02 1d 81 29 00
0000100 00 29 00 00 00 00 00 00 29 00 00 00 00 00 00 04
0000120 00 23 23 00 00 23 00 03 23 00 23 84 ab 03 28 81
0000140 f4 01 e5 00 e5 00 1f 01 f4 01 e3 00 09 64 e6 13
0000160 00 00 b5 0b 31 03 06 32 dc 8c 0a b8 0b 6e e9 00
^C
# od -t x1 < /dev/ttyS0
0000000 ab 01 35 81 01 01 00 ea 24 00 32 dc ff ff ff ff
0000020 ff ff ff ff ff ff 00 00 01 00 00 00 ff ff ff ff
0000040 ff ff ff ff ff ff 00 00 03 00 00 00 01 00 00 01
0000060 02 ff ff ff ff ff ff ff ff 94 ab 02 1d 81 29 00
0000100 00 29 00 00 00 00 00 00 29 00 00 00 00 00 00 04
0000120 00 23 23 00 00 23 00 03 23 00 23 84 ab 03 28 81
0000140 f4 01 e4 00 e6 00 20 01 f4 01 e4 00 09 64 dd 14
0000160 00 00 b5 0b 31 03 06 32 dc 8c 0a b8 0b 6e e9 00
^C
Which driver should I try to use?
More information about the Nut-upsuser