[Nut-upsuser] Are UPS shutdown commands automatically sent?
Rob Groner
rgroner at RTD.com
Wed May 27 14:31:08 UTC 2015
Roger,
Following your guide, it now works great, shutting down the UPS after the system has shutdown. I went with the bash script method.
I have noticed, however, that the command to the UPS to do the delayed shutdown comes RIGHT as openSUSE is shutting down. While that is a good thing as far as timing and the potential race is concerned, I have seen it once where the UPS received the command to do the delayed shutdown, but *not* the command to do the delayed restart. While that's not a critical failure, it would be if the UPS doesn't get the delayed shutdown command instead.
I'm wondering if the system (openSUSE ) died before that particular command could be sent over USB to the UPS.
Sincerely,
Robert G. Groner
Software Engineer
RTD Embedded Technologies, Inc.
ISO 9001 and AS9100 Certified
Ph: 814-234-8087
www.rtd.com
-----Original Message-----
From: Nut-upsuser [mailto:nut-upsuser-bounces+rgroner=rtd.com at lists.alioth.debian.org] On Behalf Of Roger Price
Sent: Saturday, May 23, 2015 6:02 AM
To: nut-upsuser Mailing List
Subject: Re: [Nut-upsuser] Are UPS shutdown commands automatically sent?
On Fri, 22 May 2015, Rob Groner wrote:
> So I'm pursuing the strategy of issuing the "upsdrvctl shutdown"
> command script when the OS (Porteus, in this case) is shutting down.
> I so far can't get it to do it, but I'm sure I'll overcome it, but I
> realized something else might be a problem.
>
> Won't that script execute every time Linux is shutting down, including
> rebooting? So, if I choose to reboot my system, I would most likely
> see the UPS shutoff and then turn back on, somewhere in the middle of
> my system booting back up.
Hello Robert, The command /sbin/shutdown -r used to reboot the box is incompatible with a UPS which receives a delayed shutdown order. If you have offdelay = 30 in /etc/ups/ups.conf, then 30 seconds after the upsdrvctl shutdown, when the box has now probably restarted, the UPS will shutdown with total loss of power to the box. Not good.
> I can think of a couple solutions: 1) Have the script verify that the
> UPS is actually in a OB state before giving the shutdown command.
> That should prevent unintended UPS power cycles when simply rebooting
> the system. 2) Have the UPS itself not respect any "load.off.delay" or
> similar commands when it is online.
This adds complexity, and in a critical system component simplicity is a virtue. To reboot my box, I turn off the wall power and wait until I hear the "clunk" as the shutdown relay operates in the UPS. I then turn the wall power back on.
> Looking over UPS documentation and various helps, it seems most people
> would expect their UPS to turn the load off and then back on, even if
> it has wall power the entire time. That would facilitate testing at a
> minimum. So I'm guessing option #2 isn't a good one.
If you have decided to use a UPS capable of shutting down and restarting when wall power comes back, then you have to respect the UPS cycle. You can't pretend it isn't there.
Best regards, Roger