[Nut-upsuser] Contact-closure UPS
Charles Lepple
clepple at gmail.com
Mon Nov 16 14:20:17 UTC 2015
[please use reply-all when responding - the list does not modify the reply-to header.]
> On Nov 16, 2015, at 8:24 AM, Róbert SZAKSZ <robert at szaksz.eu> wrote:
>
> Hello,
>
> I have one UPS Infosec XP Pro 2500 RM and it works with windows sw RUPS2000.
> Now I want to install this UPS as virtual server on vmware ESXi vMA - (SUSE SLES 11SP2 linux).
> On this linux I have NUT 2.6.0 and I stopped now with configuration of genericups driver.
>
> Working cable (direct cable pin1-pin1 ... pin9-pin9) connection on Windows:
>
> PIN | PC | UPS
> __________________________________________________________________________________
> Pin1 | DCD | described as DTR (must keep Hi)
> Pin2 | RxD | AC Power fail (NO, connected to pin4 UPS ground in case of AC failure)
The genericups driver does not have a setting to use the PC RxD line as a contact-closure input. It seems to be possible if the other software is using it, but genericups can only send a BREAK signal (rather than receiving it).
> Pin3 | TxD | N/A
> Pin4 | DTR | UPS ground
> Pin5 | GND | Battery low (NO, connected to pin4 UPS ground in case of LB)
> Pin6 | DSR | 1. described as UPS RxD and 2. 3 seconds Hi (UPS shutdown)
> Pin7 | RTS | UPS ground
> Pin8 | CTS | N/A
> Pin9 | RI | described as UPS TxD
>
> And the question is, how to configure CP[???], OL[???], LB[???], SD[???]?
> No one from predefined 21 types worked for me.
>
The RUPS 2000 cable type in genericups seems to correspond to a crossed cable as shown in 5.2.1 below:
http://web.archive.org/web/20100106160328/http://ups.miem.edu.ru/ups_faq5.html
You might also be able to connect up the TxD and RxD lines, and use the nutdrv_qx (not available until after v2.6.5), megatec or blazer_ser drivers:
PC UPS Description
== === ===========
2 9 TxD
3 6 RxD
5 7 Ground
--
Charles Lepple
clepple at gmail