[Nut-upsuser] Problem installing NUT on 16.04

Jack McGee jack at greendesk.net
Sat Dec 3 17:57:34 UTC 2016


On 12/03/2016 11:46 AM, Charles Lepple wrote:
>
> If you don't mind sending the full output of "upsc" and "upsrw", we can update the DDL page (it only has "upsc" output for an older version of NUT). This UPS provides some sort of serial number (doesn't match the label) in the device.model (and mirrored at ups.model) variables, so if you want to mask off a few digits from the end, that's fine. (CyberPower seems to have swapped the model name and serial number strings in the USB descriptor.)
mythuser at amethi:/etc/nut$ upsc CyberUPS1 at 192.168.0.105
Init SSL without certificate database
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 3840
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 24.0
battery.voltage.nominal: 24
device.mfr: CPS
device.model: CP1500PFCLCD
device.serial: 000000000000
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.synchronous: no
driver.parameter.vendorid: 0764
driver.version: 2.7.4.1
driver.version.data: CyberPower HID 0.4
driver.version.internal: 0.42
driver.version.usb: libusb-1.0 (API: 0x1000104)
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 126.0
input.voltage.nominal: 120
output.voltage: 142.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 13
ups.mfr: CPS
ups.model: CP1500PFCLCD
ups.productid: 0501
ups.realpower.nominal: 900
ups.serial: 000000000000
ups.status: OL
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764



mythuser at amethi:/etc/nut$ upsrw CyberUPS1 at 192.168.0.105
[battery.charge.low]
Remaining battery level when UPS switches to LB (percent)
Type: STRING
Maximum length: 10
Value: 10

[battery.runtime.low]
Remaining battery runtime when UPS switches to LB (seconds)
Type: STRING
Maximum length: 10
Value: 300

[input.transfer.high]
High voltage transfer point (V)
Type: STRING
Maximum length: 10
Value: 139

[input.transfer.low]
Low voltage transfer point (V)
Type: STRING
Maximum length: 10
Value: 88

[ups.delay.shutdown]
Interval to wait after shutdown with delay command (seconds)
Type: STRING
Maximum length: 10
Value: 20

[ups.delay.start]
Interval to wait before (re)starting the load (seconds)
Type: STRING
Maximum length: 10
Value: 30





More information about the Nut-upsuser mailing list