[Nut-upsuser] UPS Socomec is unavailable appears in the logs
Charles Lepple
clepple at gmail.com
Fri Feb 12 13:53:53 UTC 2016
On Feb 8, 2016, at 8:46 AM, Henning Fehrmann <henning.fehrmann at aei.mpg.de> wrote:
>
> Hello,
>
> we have two UPSes - one Galaxy and one from Socomec, both monitored by the NUT server.
>
> The NUT server runs the version 2.7.2.
>
> We have roughly 3500 clients running upsmon, reading the status of both
> UPSes. They run mainly the version 2.6.4 and some 2.7.2.
>
> We observed the following on both client versions, regardless whether
> we run upsmon in the daemon or debug mode:
>
> Running
> upsc socomec at ip_socomec
> returns a list of all required values.
>
> OTOH, we find on all clients the folloging logs:
> upsmon[1608]: UPS socomec at ip_socomec is unavailable
I think this error message comes from this check:
https://github.com/networkupstools/nut/blob/1993c39866b4625c0218fda1dfa9b037934c4c47/clients/upsmon.c#L1458
"empty response is the same as a dead ups"
Corresponds to these lines from strace:
4275 14:08:05.693306 write(6, "GET VAR socomec ups.status\n", 27) = 27
4275 14:08:05.693373 select(7, [6], NULL, NULL, {5, 0}) = 1 (in [6], left {4, 997653})
4275 14:08:05.695899 read(6, "VAR socomec ups.status \"\"\n", 64) = 26
If you run "upsc socomec at ip_socomec ups.status", it should return (at a minimum) "ups.status: OL", "ups.status: OB" or "ups.status: OB LB".
The Galaxy seems to be working (from a few lines earlier):
4275 14:08:05.689595 write(4, "GET VAR galaxy ups.status\n", 26) = 26
4275 14:08:05.689721 select(5, [4], NULL, NULL, {5, 0}) = 1 (in [4], left {4, 996929})
4275 14:08:05.692927 read(4, "VAR galaxy ups.status \"OL\"\n", 64) = 27
There was a change to the Netvision MIB file (included in NUT 2.7.3) that might fix the empty ups.status:
https://github.com/networkupstools/nut/commit/4552d14162086a280445efc5331a8e6ad7b1c3a4
It should not be necessary to update the clients to NUT 2.7.3, only the Socomec NUT server.
>
> This appears regularly each little bit more than 300s and corresponds to
> the NOCOMMWARNTIME in the upsmon.conf.
>
> The log entry appears only for the Socomec UPS, not for the Galaxy.
>
> The process list shows that /sbin/upsmon is forking occasionally, generating a child in the Z state
>
> root 3294 0.0 0.0 10448 704 ? Ss 14:02 0:00 /sbin/upsmon
> nut 3295 0.0 0.0 10448 580 ? S 14:02 0:00 /sbin/upsmon
> nut 3497 0.0 0.0 0 0 ? Z 14:02 0:00 [upsmon] <defunct>
It is unclear to me why this process is a zombie (defunct). I would expect upsmon to fork every 300s to run the NOTIFYCMD (upssched, in your case) due to the empty ups.status, but since the wait4 syscall (the waitpid() library function in the code) is being called, it should reap the zombie process. Maybe you are just seeing the window of time between the fork() and the waitpid()?
> On the client side the ups.conf is
> [galaxy]
> driver = galaxy
> port = ip_NUTserver
> desc = "GALAXY 6000"
>
> [socomec]
> driver = socomec
> port = ip_NUTserver
> desc = "SOCOMEC"
Actually, the clients don't need ups.conf - they get the description from the server's ups.conf over the NUT network protocol.
> The upsmon.conf reads:
>
> MONITOR galaxy at 172.28.22.40 1 monuser XXX master
> MONITOR socomec at 172.28.22.40 1 monuser XXX master
>
>
> MINSUPPLIES 1
> SHUTDOWNCMD "/sbin/shutdown -h now"
> NOTIFYCMD "/sbin/upssched"
>
I don't use upssched - maybe someone else can shed some light on this?
> _______________________________________________
> Nut-upsuser mailing list
> Nut-upsuser at lists.alioth.debian.org
> http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
--
Charles Lepple
clepple at gmail
More information about the Nut-upsuser
mailing list