[Nut-upsuser] cannot get APC ups status change via usb cable	from RaspberryPi
    Charles Lepple 
    clepple at gmail.com
       
    Wed Jun  1 02:48:28 UTC 2016
    
    
  
On May 31, 2016, at 1:11 AM, Tomas Tang <myhnet at gmail.com> wrote:
> 
> Hi All,
> 
>  
> 
>                 I get very strange UPS problem from RspberryPI mode B (both version 2 and 3).
> 
>  
> 
>                 Here is our environment:
> 
>  
> 
>                 OS:                         Raspbian 8.0, Ubuntu 16.04 and Ubuntu 14.04
> 
>                 Platform:             RaspberryPi Mode B version 2 and version 3
> 
>                 NUT:                      tested version 2.6.3, 2.7.1 and 2.7.2 (from ports.ubuntu.com)
> 
>                 UPS:                       APC Smart-UPS 3000 RM and APC Smart-UPS 1500 RM
> 
>                 Cable:                    USB
> 
>  
> 
>                 Problem detail:
> 
>                 NUT can read all the information after installed, but once you unplug the input power, the status didn’t get changed and there is no log related to NUT from syslog.
Please check the mailing lists to see if there are any other reports for these particular models over USB. The only full dump I could find was with the apcsmart driver: http://networkupstools.org/ddl/APC/Smart-UPS_3000_RM.html
There is a "pollonly" flag that might help, but it is supposed to be selected automatically. What does 'lsusb -vvv -d 051d:' return when run as root?
-- 
Charles Lepple
clepple at gmail
    
    
More information about the Nut-upsuser
mailing list