> On Oct 20, 2016, at 8:25 AM, jfmxl at sdf.org wrote:
>
> Using protocol: Q1 0.02
> Can't autodetect number of battery packs [-1/13.50]
> Battery runtime will not be calculated (runtimecal not set)
>
> ... looks like it's connected to something, although maybe the driver is not quite right?
That looks reasonable. Not all UPSes provide enough information to calculate runtime, but you can improve it slightly:
http://networkupstools.org/docs/man/nutdrv_qx.html#_battery_charge
What does "upsc easton" say? (make sure that upsd is running)