[Nut-upsuser] battery not installed, but battery still 100% and NUT 2.7.2-4 does not catch this and report a error
Jon Bendtsen
jon.bendtsen at jonix.dk
Mon Apr 3 21:52:44 UTC 2017
On 03/04/17 22.11, Gene Heskett wrote:
> On Monday 03 April 2017 14:13:08 Stuart D. Gathman wrote:
>
> Back on the mailing list, where such belongs.
>
[cuuut]
>> We want the ALARM that the nut driver is
>> generating, and upsd is passing on - to be acted on in some way by
>> upsmon. Which NOTIFYCMD is run when there is an ALARM?
[cuuut]
I dont think any NOTIFYCMD is run when there is an ALARM Stuart.
> I've not read the docs in ages, but if there isn't something mentioned in
> a man upsmon, I would be unpleasantly surprised.
>
> According to my copy, it does a -wall (warn all) by default, and it looks
> like REPLBATT is one such message, and the default time for a repeat is
> 12 hours. The -wall type message shows on every open terminal on the
> system's network, so someone should see it. From the upsmon.conf file:
[cuuuut]
> Possible values for type:
>
> ONLINE
> UPS is back online
>
> ONBATT
> UPS is on battery
>
> LOWBATT
> UPS is on battery and has a low battery (is critical)
>
> FSD
> UPS is being shutdown by the master (FSD = "Forced
> Shutdown")
>
> COMMOK
> Communications established with the UPS
>
> COMMBAD
> Communications lost to the UPS
>
> SHUTDOWN
> The system is being shutdown
>
> REPLBATT
> The UPS battery is bad and needs to be replaced
>
> NOCOMM
> A UPS is unavailable (can’t be contacted for monitoring)
ALARM is not mentioned, so I suppose NUT only reacts to the Online message it gets?
JonB
More information about the Nut-upsuser
mailing list