On Sun, 5 Feb 2017, Tim Richards wrote:
> Setup: Active/Passive Two Node Cluster. Two UPSes (APC Smart-UPS 1500 C)
> with USB communication cables cross connected (ie UPS-webserver1
> monitored by webserver2, and vice versa) to allow for stonith/fencing
>
> OS OpenSuse Leap 42.2
> NUT version 2.7.1-2.41-x86_64
> Fencing agent: external/nut
>
> Problem: When power fails to a single UPS, both nodes are shutdown. The
> node with the still powered UPS comes back up, but requires manual
> intervention to keep it providing services. I would like only the node
> with the “On Battery” UPS to shutdown.
I think your title hints at the solution. What is the advantage of the
cross-connection of the UPS units? Wouldn't it be simpler to have each
node connected to the UPS which supplies the power? This is easier to set
up, extends easily to n servers, and is independent of the stonith/fencing
which I assume you use for other purposes.
> The resupply of services problem seems to be that NUT on the node that
> comes back up will not restart until the other node restarts.
With a simpler setup, this problem should go away.
Roger