[Nut-upsuser] NUT Client shuts down when performing runtime calibration on APC UPS

Merk - Oliver oliver.merk at pecon.biz
Mon Jan 9 14:46:42 UTC 2017


Here are the results from the output of upsc under different conditions from my Debian Test system with NUT 2.7.2 :

Normal: ups.status: OL
No wall power: ups.status: OB
Runtime calibration (started from AP9630 web interface): ups.status: OB CAL

So at this stage there is a difference!

 I then connected to my QNAP and set the UPS settings on the web interface to "Shutdown server if power loss is 5 min", the UPS is configured to an SNMP-Connection with its IP-address.  Started runtime calibration and after 5min. the QNAP NAS has shut down. But before that I connected via SSH on it and also checked the output of upsc during runtime calibration: ups.status: OB CAL.

Currently I don't understand how Nut works in detail, but at least the information that it is on calibration is there. Why the NAS still shuts down after 5min. I cannot understand, but maybe you can help me. I give here the settings in the QNAP nut configuration files. I hope I've got the correct files, since they are not located at the normal place:

[/mnt/HDA_ROOT/.config] # more ups_snmptrapd.conf
#
# use fully qualified prefix... just to be safe
#
traphandle .1.3.6.1.4.1.318.0.5 /sbin/ups_snmptrap_handler POWER_LOST
traphandle .1.3.6.1.4.1.318.0.9 /sbin/ups_snmptrap_handler POWER_RESTORED
traphandle .1.3.6.1.4.1.318.0.7 /sbin/ups_snmptrap_handler BATTERY_LOW
traphandle .1.3.6.1.4.1.318.0.1 /sbin/ups_snmptrap_handler COMM_LOST
traphandle .1.3.6.1.4.1.318.0.8 /sbin/ups_snmptrap_handler COMM_RESTORED


-----------------------------------------------------------------------------------------------------------
[/mnt/HDA_ROOT/.config/ups] # more ups.conf
[qnapups]
driver = snmp-ups
        port = /dev/ttyS1
        desc = "Workstation"
        pollinterval=1


-----------------------------------------------------------------------------------------------------------
[/mnt/HDA_ROOT/.config/ups] # more upsd.conf
# Network UPS Tools: example upsd configuration file
#
# This file contains access control data, you should keep it secure.
#
# It should only be readable by the user that upsd becomes.  See the FAQ.

# =======================================================================
# Access Control Lists (ACLs)
#
# ACL <name> <ipblock>
# ACL myhost 10.0.0.1/32
#
# ACCEPT <aclname> [<aclname>...]
# REJECT <aclname> [<aclname>...]
#
# Define lists of hosts or networks with ACL definitions.
#
# ACCEPT and REJECT use ACL definitions to control whether a host is
# allowed to connect to upsd.
#
# This default configuration only gives access to localhost.  To allow
# other hosts or networks to connect, see the documentation and change
# these lines.

ACL all 0.0.0.0/0
ACL localhost 127.0.0.1/32

ACCEPT localhost
REJECT all

MAXAGE          20

# =======================================================================
# MAXAGE <seconds>
# MAXAGE 15
#
# This defaults to 15 seconds.  After a UPS driver has stopped updating
# the data for this many seconds, upsd marks it stale and stops making
# that information available to clients.  After all, the only thing worse
# than no data is bad data.
#
# You should only use this if your driver has difficulties keeping
# the data fresh within the normal 15 second interval.  Watch the syslog
# for notifications from upsd about staleness.


-----------------------------------------------------------------------------------------------------------
[/mnt/HDA_ROOT/.config/ups] # more upsd.users
# Network UPS Tools: Example upsd.users
#
# This file sets the permissions for upsd - the UPS network daemon.
# Users are defined here, are given passwords, and their privileges are
# controlled here too.  Since this file will contain passwords, keep it
# secure, with only enough permissions for upsd to read it.

# --------------------------------------------------------------------------

# Each user gets a section.  To start a section, put the username in
# brackets on a line by itself.  To set something for that user, specify
# it under that section heading.  The username is case-sensitive, so
# admin and AdMiN are two different users.
#
# Possible settings:
#
# password: The user's password.  This is case-sensitive.
#
# --------------------------------------------------------------------------
#
# allowfrom: ACL names that this user may connect from.  ACLs are
#            defined in upsd.conf.
#
# --------------------------------------------------------------------------
#
# actions: Let the user do certain things with upsd.
#
# Valid actions are:
#
# SET   - change the value of certain variables in the UPS
# FSD   - set the "forced shutdown" flag in the UPS
#
# --------------------------------------------------------------------------
#
# instcmds: Let the user initiate specific instant commands.  Use "ALL"
# to grant all commands automatically.  There are many possible
# commands, so use 'upscmd -l' to see what your hardware supports.  Here
# are a few examples:
#
# test.panel.start      - Start a front panel test
# test.battery.start    - Start battery test
# test.battery.stop     - Stop battery test
# calibrate.start       - Start calibration
# calibrate.stop        - Stop calibration
#
# --------------------------------------------------------------------------
#
# Example:
#
#       [admin]
#               password = mypass
#               allowfrom = admworkstation admhome
#               actions = SET
#               instcmds = ALL
#

[admin]
                password = <secret>
                allowfrom = localhost
                actions = SET
                instcmds = ALL
                upsmon master           # or upsmon slave

#
# --- Configuring for upsmon
#
# To add a user for your upsmon, use this example:
#
#       [monuser]
#               password  = pass
#               allowfrom = bigserver
#
#               upsmon master                   (or upsmon slave)
#
# The matching MONITOR line in your upsmon.conf would look like this:
#
# MONITOR myups at myhost 1 monuser pass master    (or slave)


-----------------------------------------------------------------------------------------------------------
[/mnt/HDA_ROOT/.config/ups] # more upsdrv.map
version=1
0x51d,,usbhid-ups
0x463,,usbhid-ups
0x764,,usbhid-ups
0x9ae,,usbhid-ups
0x50d,,usbhid-ups
0x665,0x5161,blazer_usb
0x1d6b,0x2,NOT_UPS
0x1d6b,0x3,NOT_UPS
0x1d6b,0x1,NOT_UPS
0x1005,0xb155,NOT_UPS
0x051d,0x0002,usbhid-ups
0x051d,0x0002,usbhid-ups
0x051d,0x0002,usbhid-ups
0x051d,0x0002,usbhid-ups


-----------------------------------------------------------------------------------------------------------
[/mnt/HDA_ROOT/.config/ups] # more upsmon.conf
# Network UPS Tools: example upsmon configuration
#
# This file contains passwords, so keep it secure.

# --------------------------------------------------------------------------
# RUN_AS_USER <userid>
#
# By default, upsmon splits into two processes.  One stays as root and
# waits to run the SHUTDOWNCMD.  The other one switches to another userid
# and does everything else.
#
# The default nonprivileged user is set at compile-time with
#       'configure --with-user=...'.
#
# You can override it with '-u <user>' when starting upsmon, or just
# define it here for convenience.
#
# Note: if you plan to use the reload feature, this file (upsmon.conf)
# must be readable by this user!  Since it contains passwords, DO NOT
# make it world-readable.  Also, do not make it writable by the upsmon
# user, since it creates an opportunity for an attack by changing the
# SHUTDOWNCMD to something malicious.
#
# For best results, you should create a new normal user like "nutmon",
# and make it a member of a "nut" group or similar.  Then specify it
# here and grant read access to the upsmon.conf for that group.
#
# This user should not have write access to upsmon.conf.
#
# RUN_AS_USER nutmon

RUN_AS_USER admin

# --------------------------------------------------------------------------
# MONITOR <system> <powervalue> <username> <password> ("master"|"slave")
#
# List systems you want to monitor.  Not all of these may supply power
# to the system running upsmon, but if you want to watch it, it has to
# be in this section.
#
# You must have at least one of these declared.
#
# <system> is a UPS identifier in the form <upsname>@<hostname>[:<port>]
# like ups at localhost, su700 at mybox, etc.
#
# Examples:
#
#  - "su700 at mybox" means a UPS called "su700" on a system called "mybox"
#
#  - "fenton at bigbox:5678" is a UPS called "fenton" on a system called
#    "bigbox" which runs upsd on port "5678".
#
# The UPS names like "su700" and "fenton" are set in your ups.conf
# in [brackets] which identify a section for a particular driver.
#
# If the ups.conf on host "doghouse" has a section called "snoopy", the
# identifier for it would be "snoopy at doghouse".
#
# <powervalue> is an integer - the number of power supplies that this UPS
# feeds on this system.  Most computers only have one power supply, so this
# is normally set to 1.  You need a pretty big or special box to have any
# other value here.
#
# You can also set this to 0 for a system that doesn't supply any power,
# but you still want to monitor.  Use this when you want to hear about
# changes for a given UPS without shutting down when it goes critical,
# unless <powervalue> is 0.
#
# <username> and <password> must match an entry in that system's
# upsd.users.  If your username is "monmaster" and your password is
# "blah", the upsd.users would look like this:
#
#       [monmaster]
#               password  = blah
#               allowfrom =     (whatever applies to this host)
#               upsmon master   (or slave)
#
# "master" means this system will shutdown last, allowing the slaves
# time to shutdown first.
#
# "slave" means this system shuts down immediately when power goes critical.
#
# Examples:
#
# MONITOR myups at bigserver 1 monmaster blah master
# MONITOR su700 at server.example.com 1 upsmon secretpass slave

MONITOR qnapups at 0.0.0.0 1 admin <secret> slave

# --------------------------------------------------------------------------
# MINSUPPLIES <num>
#
# Give the number of power supplies that must be receiving power to keep
# this system running.  Most systems have one power supply, so you would
# put "1" in this field.
#
# Large/expensive server type systems usually have more, and can run with
# a few missing.  The HP NetServer LH4 can run with 2 out of 4, for example,
# so you'd set that to 2.  The idea is to keep the box running as long
# as possible, right?
#
# Obviously you have to put the redundant supplies on different UPS circuits
# for this to make sense!  See big-servers.txt in the docs subdirectory
# for more information and ideas on how to use this feature.

MINSUPPLIES 1

# --------------------------------------------------------------------------
# SHUTDOWNCMD "<command>"
#
# upsmon runs this command when the system needs to be brought down.
#
# This should work just about everywhere ... if it doesn't, well, change it.

SHUTDOWNCMD "/sbin/shutdown -h +0"

# --------------------------------------------------------------------------
# NOTIFYCMD <command>
#
#
# upsmon calls this to send messages when things happen
#
# This command is called with the full text of the message as one argument.
# The environment string NOTIFYTYPE will contain the type string of
# whatever caused this event to happen.
#
# Note that this is only called for NOTIFY events that have EXEC set with
# NOTIFYFLAG.  See NOTIFYFLAG below for more details.
#
# Making this some sort of shell script might not be a bad idea.  For more
# information and ideas, see pager.txt in the docs directory.
#
# Example:
# NOTIFYCMD /usr/local/ups/bin/notifyme

# --------------------------------------------------------------------------
# POLLFREQ <n>
#
# Polling frequency for normal activities, measured in seconds.
#
# Adjust this to keep upsmon from flooding your network, but don't make
# it too high or it may miss certain short-lived power events.

POLLFREQ 5

# --------------------------------------------------------------------------
# POLLFREQALERT <n>
#
# Polling frequency in seconds while UPS on battery.
#
# You can make this number lower than POLLFREQ, which will make updates
# faster when any UPS is running on battery.  This is a good way to tune
# network load if you have a lot of these things running.
#
# The default is 5 seconds for both this and POLLFREQ.

POLLFREQALERT 5

# --------------------------------------------------------------------------
# HOSTSYNC - How long upsmon will wait before giving up on another upsmon
#
# The master upsmon process uses this number when waiting for slaves to
# disconnect once it has set the forced shutdown (FSD) flag.  If they
# don't disconnect after this many seconds, it goes on without them.
#
# Similarly, upsmon slave processes wait up to this interval for the
# master upsmon to set FSD when a UPS they are monitoring goes critical -
# that is, on battery and low battery.  If the master doesn't do its job,
# the slaves will shut down anyway to avoid damage to the file systems.
#
# This "wait for FSD" is done to avoid races where the status changes
# to critical and back between polls by the master.

HOSTSYNC 15

# --------------------------------------------------------------------------
# DEADTIME - Interval to wait before declaring a stale ups "dead"
#
# upsmon requires a UPS to provide status information every few seconds
# (see POLLFREQ and POLLFREQALERT) to keep things updated.  If the status
# fetch fails, the UPS is marked stale.  If it stays stale for more than
# DEADTIME seconds, the UPS is marked dead.
#
# A dead UPS that was last known to be on battery is assumed to have gone
# to a low battery condition.  This may force a shutdown if it is providing
# a critical amount of power to your system.
#
# Note: DEADTIME should be a multiple of POLLFREQ and POLLFREQALERT.
# Otherwise you'll have "dead" UPSes simply because upsmon isn't polling
# them quickly enough.  Rule of thumb: take the larger of the two
# POLLFREQ values, and multiply by 3.

DEADTIME 15

# --------------------------------------------------------------------------
# POWERDOWNFLAG - Flag file for forcing UPS shutdown on the master system
#
# upsmon will create a file with this name in master mode when it's time
# to shut down the load.  You should check for this file's existence in
# your shutdown scripts and run 'upsdrvctl shutdown' if it exists.
#
# See the shutdown.txt file in the docs subdirectory for more information.

POWERDOWNFLAG /etc/killpower

# --------------------------------------------------------------------------
# NOTIFYMSG - change messages sent by upsmon when certain events occur
#
# You can change the default messages to something else if you like.
#
# NOTIFYMSG <notify type> "message"
#
# NOTIFYMSG ONLINE      "UPS %s on line power"
# NOTIFYMSG ONBATT      "UPS %s on battery"
# NOTIFYMSG LOWBATT     "UPS %s battery is low"
# NOTIFYMSG FSD         "UPS %s: forced shutdown in progress"
# NOTIFYMSG COMMOK      "Communications with UPS %s established"
# NOTIFYMSG COMMBAD     "Communications with UPS %s lost"
# NOTIFYMSG SHUTDOWN    "Auto logout and shutdown proceeding"
# NOTIFYMSG REPLBATT    "UPS %s battery needs to be replaced"
# NOTIFYMSG NOCOMM      "UPS %s is unavailable"
# NOTIFYMSG NOPARENT    "upsmon parent process died - shutdown impossible"
#
# Note that %s is replaced with the identifier of the UPS in question.
#
# Possible values for <notify type>:
#
# ONLINE   : UPS is back online
# ONBATT   : UPS is on battery
# LOWBATT  : UPS has a low battery (if also on battery, it's "critical")
# FSD      : UPS is being shutdown by the master (FSD = "Forced Shutdown")
# COMMOK   : Communications established with the UPS
# COMMBAD  : Communications lost to the UPS
# SHUTDOWN : The system is being shutdown
# REPLBATT : The UPS battery is bad and needs to be replaced
# NOCOMM   : A UPS is unavailable (can't be contacted for monitoring)
# NOPARENT : The process that shuts down the system has died (shutdown impossible)

# --------------------------------------------------------------------------
# NOTIFYFLAG - change behavior of upsmon when NOTIFY events occur
#
# By default, upsmon sends walls (global messages to all logged in users)
# and writes to the syslog when things happen.  You can change this.
#
# NOTIFYFLAG <notify type> <flag>[+<flag>][+<flag>] ...
#
# NOTIFYFLAG ONLINE     SYSLOG+WALL
# NOTIFYFLAG ONBATT     SYSLOG+WALL
# NOTIFYFLAG LOWBATT    SYSLOG+WALL
# NOTIFYFLAG FSD        SYSLOG+WALL
# NOTIFYFLAG COMMOK     SYSLOG+WALL
# NOTIFYFLAG COMMBAD    SYSLOG+WALL
# NOTIFYFLAG SHUTDOWN   SYSLOG+WALL
# NOTIFYFLAG REPLBATT   SYSLOG+WALL
# NOTIFYFLAG NOCOMM     SYSLOG+WALL
# NOTIFYFLAG NOPARENT   SYSLOG+WALL
#
# Possible values for the flags:
#
# SYSLOG - Write the message in the syslog
# WALL   - Write the message to all users on the system
# EXEC   - Execute NOTIFYCMD (see above) with the message
# IGNORE - Don't do anything
#
# If you use IGNORE, don't use any other flags on the same line.

# --------------------------------------------------------------------------
# RBWARNTIME - replace battery warning time in seconds
#
# upsmon will normally warn you about a battery that needs to be replaced
# every 43200 seconds, which is 12 hours.  It does this by triggering a
# NOTIFY_REPLBATT which is then handled by the usual notify structure
# you've defined above.
#
# If this number is not to your liking, override it here.

RBWARNTIME 43200

# --------------------------------------------------------------------------
# NOCOMMWARNTIME - no communications warning time in seconds
#
# upsmon will let you know through the usual notify system if it can't
# talk to any of the UPS entries that are defined in this file.  It will
# trigger a NOTIFY_NOCOMM by default every 300 seconds unless you
# change the interval with this directive.

NOCOMMWARNTIME 300

# --------------------------------------------------------------------------
# FINALDELAY - last sleep interval before shutting down the system
#
# On a master, upsmon will wait this long after sending the NOTIFY_SHUTDOWN
# before executing your SHUTDOWNCMD.  If you need to do something in between
# those events, increase this number.  Remember, at this point your UPS is
# almost depleted, so don't make this too high.
#
# Alternatively, you can set this very low so you don't wait around when
# it's time to shut down.  Some UPSes don't give much warning for low
# battery and will require a value of 0 here for a safe shutdown.
#
# Note: If FINALDELAY on the slave is greater than HOSTSYNC on the master,
# the master will give up waiting for the slave to disconnect.

FINALDELAY 5

________________________