[Nut-upsuser] Compaq R3000h support
Charles Lepple
clepple at gmail.com
Wed Jul 26 13:23:14 UTC 2017
[please don't use HTML email unless needed.]
sorry for the delay.
> On Jul 22, 2017, at 11:33 AM, Tomas Larsson <tomas.larsson at enrad.se> wrote:
>
> Now I have some access problems.
> This is what ends up un messages
> Hosts.allow is set to accept anyone on the local net.
> Username and passwords are the same
> Upsc gives proper output.
> System is Centos 6.8
>
> Jul 22 17:20:06 BIFROST upscode2[10113]: Startup successful
> Jul 22 17:20:06 BIFROST upsd[10116]: listening on ::1 port 3493
> Jul 22 17:20:06 BIFROST upsd[10116]: listening on 192.168.0.1 port 3493
> Jul 22 17:20:06 BIFROST upsd[10116]: listening on 127.0.0.1 port 3493
> Jul 22 17:20:06 BIFROST upsd[10116]: Connected to UPS [R3000]: upscode2-R3000
> Jul 22 17:20:06 BIFROST upsd[10117]: Startup successful
> Jul 22 17:20:06 BIFROST upsmon[10121]: Startup successful
> Jul 22 17:20:06 BIFROST upsmon[10122]: Login on UPS [R3000 at localhost] failed - got [ERR ACCESS-DENIED]
>
for upsmon-to-upsd access issues, you should to check that upsmon.conf is using a NUT login/password that is listed in upsd.users as having either "upsmon master" or "upsmon slave" privileges, as appropriate. If you change upsd.users, reload or restart upsd.
http://networkupstools.org/docs/man/upsd.html
http://networkupstools.org/docs/man/upsd.users.html
More information about the Nut-upsuser
mailing list