On 06/12/2017 12:56 PM, Andrea de Lutti wrote:
>
>
> > I have also successfully tested the battery...
> >
> > upscmd -uadmin -pups Elit at artu test.battery.start.quick
>
> I would also recommend testing the shutdown procedure and making sure
> that everything works as expected on power failures.
> Please, let us know the results of these tests, so that we can add a
> more informed report about your device to our library
> (http://networkupstools.org/ddl/ <http://networkupstools.org/ddl/>).
>
>
> Nice, I would like to test it, but if I don't have battery runtime
> value and / or battery charge, how may I test it correctly?
> I have seen also some strange values for battery.voltage.high and
> battery.voltage.low....are they correct?
run with a test load ( at least twice, for 50% and 100% load for
instance ) and write down the periods between full charge and shutdown.
Then you can use runtimecal in ups.conf to obtain guestimations during
normal usage