On 06/12/2017 12:56 PM, Andrea de Lutti wrote:
>
>
>     > I have also successfully tested the battery...
>     >
>     >  upscmd -uadmin -pups Elit at artu test.battery.start.quick
>
>     I would also recommend testing the shutdown procedure and making sure
>     that everything works as expected on power failures.
>     Please, let us know the results of these tests, so that we can add a
>     more informed report about your device to our library
>     (http://networkupstools.org/ddl/ <http://networkupstools.org/ddl/>).
>
>
> ​Nice, I would like to test it, but if I don't have battery runtime 
> value and / or battery charge, how may I test it correctly?
> I have seen also some strange values for battery.voltage.high and 
> battery.voltage.low....are they correct?
run with a test load   ( at least twice, for 50% and 100% load for 
instance ) and write down the periods between full charge and shutdown. 
Then you can use runtimecal in ups.conf to obtain guestimations during 
normal usage