[Nut-upsuser] MGE EllipseMAX 1500 shuts down after a few hours

Charles Lepple clepple at gmail.com
Sun Dec 2 22:53:29 GMT 2018


On Dec 1, 2018, at 10:08 PM, raul <raulvior.bcn at gmail.com> wrote:
> 
>> Also, given that the load is only 12%, double-check that the UPS is not configured for any power saving features that might cause the shutdown ("ECO mode" or similar). NUT does not get a notification for that event the way that it gets a normal LB shutdown notification.
> 
> Are you referring to NUT (ups.conf) or to the UPS itself? I have checked the instruction manual and it says nothing about ECO modes. It talks only about disabling alarms or changing sensitivity to source voltage variations.
> 
I was referring to a setting on the UPS (which NUT can change). It would look like this in the upsc output, so I don't think you have it:

outlet.1.autoswitch.charge.low: 0


More information about the Nut-upsuser mailing list