[Nut-upsuser] No run cmd /usbhid-ups -k !
icingaj at gmail.com
icingaj at gmail.com
Tue Jul 3 14:24:08 BST 2018
> On Jul 2, 2018, at 9:02 AM, icingaj at gmail.com wrote:
> >
> > ioctl(12, USBDEVFS_CLAIMINTERFACE, 0xbecf910c) = -1 EBUSY (Resource
> > busy) ioctl(12, USBDEVFS_GETDRIVER, 0xbecf9024) = 0 writev(2, [{"Can't
> > claim USB device [0463:fff"..., 62}, {NULL, 0}], 2Can't claim USB
> > device [0463:ffff]: No such file or directory
> > ) = 62
> > exit_group(1) = ?
> > +++ exited with 1 +++
> >
> > Why?
>
> did you see this reply?
>
>
https://alioth-lists.debian.net/pipermail/nut-upsuser/2018-July/011147.html
>
> if that does not change the strace output, how is your OS launching the
NUT
> driver? Are the startup scripts in a repository somewhere?
>
> (if you aren't getting replies, you can check if you are subscribed here:
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser )
I have UPS Eaton 5SC 500.
I tested three solutions:
1. swap usbhid-ups -a qnapups with usbhid-ups -a qnapups -k
Result: server shutdown UPS not.
2. run upsmon -c fsd
Result: server shutdown UPS not.
3. run upscmd -u admin -p 123456 qnapups shutdown.return and next shutdown
Result: server shutdown UPS shutdown. After starting the UPS, immediately
the UPS is switched on.
The UPS was supposed to wait ups.delay.start time and then turned on.
I set in rc.local this parameters for UPS:
Set with upsrw: ups.delay.shutdown=60
Set with upsrw: ups.delay.start=90
Set with upsrw: ups.start.auto=no
Set with upsrw: ups.start.auto=no
Set with upsrw: ups.start.battery=no
Set with upsrw: ups.start.reboot=no
Please do not know how to write some parameters permanently to UPS?
Sorry but I'm not working with Mailing lists!
Thx Jan.
More information about the Nut-upsuser