[Nut-upsuser] Turn on UPS via USB

Stuart D. Gathman stuart at gathman.org
Wed Jan 2 16:32:45 GMT 2019


Here is another XS model:

[root at sampson log]# upsrw apc at localhost
[input.sensitivity]
Input power sensitivity
Type: STRING
Value: medium

[input.transfer.high]
High voltage transfer point (V)
Type: STRING
Value: 139

[input.transfer.low]
Low voltage transfer point (V)
Type: STRING
Value: 88

[ups.delay.shutdown]
Interval to wait after shutdown with delay command (seconds)
Type: STRING
Value: 20

[root at sampson log]# upsc apc at localhost
battery.charge: 100
battery.charge.low: 15
battery.charge.warning: 50
battery.date: 2001/09/25
battery.mfr.date: 2017/04/26
battery.runtime: 2154
battery.runtime.low: 300
battery.type: PbAc
battery.voltage: 27.2
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Back-UPS XS 1300G
device.serial: 4B1717P20965
device.type: ups
driver.flag.ignorelb: enabled
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.serial: 4B1717P20965
driver.parameter.vendorid: 051d
driver.version: 2.6.5
driver.version.data: APC HID 0.95
driver.version.internal: 0.37
input.sensitivity: medium
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 116.0
input.voltage.nominal: 120
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.firmware: 864.L9 .D
ups.firmware.aux: L9
ups.load: 16
ups.mfr: American Power Conversion
ups.mfr.date: 2017/04/26
ups.model: Back-UPS XS 1300G
ups.productid: 0002
ups.realpower.nominal: 780
ups.serial: 4B1717P20965
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: 0
ups.timer.shutdown: -1
ups.vendorid: 051d


On Wed, Jan 2, 2019 at 9:08 AM, Charles Lepple <clepple at gmail.com> 
wrote:
> 
> 
> Given that we don't have a Back-UPS NS in the compatibility list, and 
> that you have two of the three categories of information on the list 
> already, would you mind if we added this to the DDL? The output of 
> upsrw would be useful for completeness. Also, if you know any of the 
> values from upsc are incorrect, we can note that. For instance, I'm 
> assuming that "battery.date" is incorrect, and the real dates are 
> under "battery.mfr.date" and "ups.mfr.date". Other reports: 
> http://new.networkupstools.org/ddl/APC/
> 
> 
> _______________________________________________
> Nut-upsuser mailing list
> Nut-upsuser at alioth-lists.debian.net
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20190102/76f24292/attachment.html>


More information about the Nut-upsuser mailing list