[Nut-upsuser] Turn on UPS via USB

Stuart D. Gathman stuart at gathman.org
Wed Jan 2 16:41:36 GMT 2019


# upscmd -l apc at localhost
Instant commands supported on UPS [apc]:

beeper.disable - Disable the UPS beeper
beeper.enable - Enable the UPS beeper
beeper.mute - Temporarily mute the UPS beeper
beeper.off - Obsolete (use beeper.disable or beeper.mute)
beeper.on - Obsolete (use beeper.enable)
load.off - Turn off the load immediately
load.off.delay - Turn off the load with a delay (seconds)
shutdown.reboot - Shut down the load briefly while rebooting the UPS
shutdown.stop - Stop a shutdown in progress
test.battery.start.deep - Start a deep battery test
test.battery.start.quick - Start a quick battery test
test.battery.stop - Stop the battery test
test.panel.start - Start testing the UPS panel
test.panel.stop - Stop a UPS panel test


On Wed, Jan 2, 2019 at 11:32 AM, Stuart D. Gathman <stuart at gathman.org> 
wrote:
> Here is another XS model:
> 
> [root at sampson log]# upsrw apc at localhost
> [input.sensitivity]
> Input power sensitivity
> Type: STRING
> Value: medium
> 
> [input.transfer.high]
> High voltage transfer point (V)
> Type: STRING
> Value: 139
> 
> [input.transfer.low]
> Low voltage transfer point (V)
> Type: STRING
> Value: 88
> 
> [ups.delay.shutdown]
> Interval to wait after shutdown with delay command (seconds)
> Type: STRING
> Value: 20
> 
> [root at sampson log]# upsc apc at localhost
> battery.charge: 100
> battery.charge.low: 15
> battery.charge.warning: 50
> battery.date: 2001/09/25
> battery.mfr.date: 2017/04/26
> battery.runtime: 2154
> battery.runtime.low: 300
> battery! .type: PbAc
> battery.voltage: 27.2
> battery.voltage.nominal: 24.0
> device.mfr: American Power Conversion
> device.model: Back-UPS XS 1300G
> device.serial: 4B1717P20965
> device.type: ups
> driver.flag.ignorelb: enabled
> driver.name: usbhid-ups
> driver.parameter.pollfreq: 30
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.parameter.serial: 4B1717P20965
> driver.parameter.vendorid: 051d
> driver.version: 2.6.5
> driver.version.data: APC HID 0.95
> driver.version.internal: 0.37
> input.sensitivity: medium
> input.transfer.high: 139
> input.transfer.low: 88
> input.voltage: 116.0
> input.voltage.nominal: 120
> ups.beeper.status: enabled
> ups.delay.shutdown: 20
> ups.firmware: 864.L9 .D
> ups.firmware.aux: L9
> ups.load: 16
> !
> ups.mfr: American Power Conversion
> ups.mfr.date: 2017/04/26
> ups.model: Back-UPS XS 1300G
> ups.productid: 0002
> ups.realpower.nominal: 780
> ups.serial: 4B1717P20965
> ups.status: OL
> ups.test.result: No test initiated
> ups.timer.reboot: 0
> ups.timer.shutdown: -1
> ups.vendorid: 051d
> 
> 
> On Wed, Jan 2, 2019 at 9:08 AM, Charles Lepple <clepple at gmail.com> 
> wrote:
>> 
>> 
>> Given that we don't have a Back-UPS NS in the compatibility list, 
>> and that you have two of the three categories of information on the 
>> list already, would you mind if we added this to the DDL? The output 
>> of upsrw would be useful for completeness. Also, if you know any of 
>> the values from upsc are incorrect, we can note that. For instance, 
>> I'm assuming that "battery.date" is incorrect, and the real dates 
>> are under "battery.mfr.date" and "ups.mfr.date". Other reports: 
>> http://new.networkupstools.org/ddl/APC/
>> 
>> 
>> _______________________________________________
>> Nut-upsuser mailing list
>> Nut-upsuser at alioth-lists.debian.net
>> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20190102/e9d7eeda/attachment-0001.html>


More information about the Nut-upsuser mailing list