On Jun 10, 2019, at 2:32 PM, Marc Finns wrote:
> 
> Hello, I read all FAQ and other sources but I could not find this situation, so I thought of asking the experts.
> I successfully configured a Raspberry NUT server to control my UPS that powers several devices (NUC with ESXI VMs, Synology NAS etc).
> All works well in principle, but I have the following behaviours that I could not find described anywhere.
> 	• When power returns after the system has shuts down because of battery flat, all restarts immediately. However, as soon as NUT server reboots, it switches the UPS to battery till it dies – even if line is present

This is FAQ #49: https://networkupstools.org/docs/FAQ.html#_my_ups_powers_up_immediately_after_a_power_failure_instead_of_waiting_for_the_batteries_to_recharge

> 	• If power returns after the system has started the shutdown sequence, the UPS does not return to AC mode and stays on battery till it dies.

This is FAQ #51:

https://networkupstools.org/docs/FAQ.html#_the_power_came_back_during_the_shutdown_but_before_the_ups_power_off_now_the_ups_does_not_reboot_and_my_computer_stays_off_how_can_i_fix_that

These are subtle edge cases, but apparently a lot of entry-level UPS models omit the interface to control these two situations. As mentioned in both of the FAQ explanations, you can work around this in software, or you can sell the UPS to someone who annoys you, and look for one that provides the "battery.charge.restart" NUT variable (Minimum battery level for UPS restart after power-off) and the "shutdown.return" instant command.

In both cases, we have tried to collect NUT variable dumps and command listings from NUT users here: https://networkupstools.org/ddl/

Note that this information is best-effort, and sometimes vendors change the underlying firmware without changing the model name. There is no substitute for testing when it comes to shutdown procedures, unfortunately. 

(If you get an error from the mailing list about the message size, please try turning off HTML posting, and gzip any log files.)

>  
> Therefore, behaviour (1) creates a dangerous endless loop where power returns, all boots, after 30 sec power is brutally cut, and so on. The net result is that I already killed a disk.
> Please note: I never had this behaviour when I used the Synology as network UPS server.
> Is anyone having the same / having a suggestion?
> Thanks a million. Marc.
>  
> Hardware: Raspberry PI
> OS name and version: Raspbian (Linux raspberrypi 4.19.42-v7+ #1219 SMP Tue May 14 21:20:58 BST 2019 armv7l GNU/Linux)
> NUT version 2.7.4 installed from repo
> UPS: APS Back-UPS RS 550G 
> Driver configuration:
> [ups]
>         driver = usbhid-ups
>         port = auto
>         desc = "Back-UPS RS 550G"
>        ignorelb
>        override.battery.charge.low = 20
>        override.battery.runtime.low = 200
>        pollfreq = 15
>  
> Output of  /lib/nut/usbhid-ups -DD -a ups
> Network UPS Tools - Generic HID driver 0.41 (2.7.4)
> USB communication driver 0.33
>    0.000000   debug level is '2'
>    0.004536   upsdrv_initups...
>    0.006506   Checking device (051D/0002) (001/004)
>    0.009744   - VendorID: 051d
>    0.009826   - ProductID: 0002
>    0.010240   - Manufacturer: American Power Conversion
>    0.010866   - Product: Back-UPS RS 550G FW:857.L5 .I USB FW:L5  
>    0.011214   - Serial Number: 3B1547X04970  
>    0.011271   - Bus: 001
>    0.011768   - Device release number: 0090
>    0.011822   Trying to match device
>    0.012248   Device matches
>    0.013822   HID descriptor length 1134
>    0.016761   Report Descriptor size = 1134
>    0.019750   Using subdriver: APC HID 0.96
>    0.019824   112 HID objects found
>    0.020801   Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 2
>    0.021529   Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 3
>    0.022404   Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x03, Offset: 0, Size: 8, Value: 4
>    0.023913   Path: UPS.PowerSummary.iOEMInformation, Type: Feature, ReportID: 0x04, Offset: 0, Size: 8, Value: 1
>    0.025154   Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID: 0x05, Offset: 0, Size: 8, Value: 1
>    0.026405   Path: UPS.PowerSummary.Charging, Type: Input, ReportID: 0x06, Offset: 0, Size: 8, Value: 1
>    0.027244   Path: UPS.PowerSummary.Charging, Type: Feature, ReportID: 0x06, Offset: 0, Size: 8, Value: 1
>    0.028082   Path: UPS.PowerSummary.Discharging, Type: Input, ReportID: 0x06, Offset: 8, Size: 8, Value: 0
>    0.028965   Path: UPS.PowerSummary.Discharging, Type: Feature, ReportID: 0x06, Offset: 8, Size: 8, Value: 0
>    0.029785   Path: UPS.PowerSummary.APCStatusFlag, Type: Input, ReportID: 0x06, Offset: 16, Size: 8, Value: 8
>    0.030618   Path: UPS.PowerSummary.APCStatusFlag, Type: Feature, ReportID: 0x06, Offset: 16, Size: 8, Value: 8
>    0.031914   Path: UPS.PowerSummary.ManufacturerDate, Type: Feature, ReportID: 0x07, Offset: 0, Size: 16, Value: 18290
>    0.033288   Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, ReportID: 0x08, Offset: 0, Size: 16, Value: 12
>    0.034536   Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x09, Offset: 0, Size: 16, Value: 12.59
>    0.035776   Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 8, Value: 1
>    0.037025   Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x0b, Offset: 0, Size: 8, Value: 2
>    0.038282   Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x0c, Offset: 0, Size: 8, Value: 18
>    0.039169   Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 18
>    0.040008   Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x0c, Offset: 8, Size: 16, Value: 262
>    0.040842   Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x0c, Offset: 8, Size: 16, Value: 262
>    0.042150   Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 0x0d, Offset: 0, Size: 8, Value: 100
>    0.043790   Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, ReportID: 0x0e, Offset: 0, Size: 8, Value: 100
>    0.045030   Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 8, Value: 50
>    0.046289   Path: UPS.PowerSummary.CapacityGranularity2, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 1
>    0.047658   Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 10
>    0.048905   Path: UPS.PowerSummary.CapacityGranularity1, Type: Feature, ReportID: 0x12, Offset: 0, Size: 8, Value: 1
>    0.050153   Path: UPS.PowerSummary.ACPresent, Type: Input, ReportID: 0x13, Offset: 0, Size: 8, Value: 1
>    0.050693   Path: UPS.PowerSummary.ACPresent, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 1
>    0.051529   Path: UPS.PowerSummary.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x14, Offset: 0, Size: 8, Value: 0
>    0.051760   Path: UPS.PowerSummary.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 0
>    0.052150   Path: UPS.PowerSummary.ShutdownImminent, Type: Input, ReportID: 0x14, Offset: 8, Size: 8, Value: 0
>    0.052536   Path: UPS.PowerSummary.ShutdownImminent, Type: Feature, ReportID: 0x14, Offset: 8, Size: 8, Value: 0
>    0.053409   Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
>    0.054039   Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x16, Offset: 0, Size: 1, Value: 1
>    0.054279   Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x16, Offset: 0, Size: 1, Value: 1
>    0.054497   Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x16, Offset: 1, Size: 1, Value: 0
>    0.054959   Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x16, Offset: 1, Size: 1, Value: 0
>    0.055360   Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x16, Offset: 2, Size: 1, Value: 1
>    0.055752   Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x16, Offset: 2, Size: 1, Value: 1
>    0.056148   Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: Input, ReportID: 0x16, Offset: 3, Size: 1, Value: 1
>    0.056541   Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: Feature, ReportID: 0x16, Offset: 3, Size: 1, Value: 1
>    0.056957   Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x16, Offset: 4, Size: 1, Value: 0
>    0.057713   Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x16, Offset: 4, Size: 1, Value: 0
>    0.059206   Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x16, Offset: 5, Size: 1, Value: 0
>    0.059435   Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x16, Offset: 5, Size: 1, Value: 0
>    0.059909   Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input, ReportID: 0x16, Offset: 6, Size: 1, Value: 0
>    0.060331   Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Feature, ReportID: 0x16, Offset: 6, Size: 1, Value: 0
>    0.060733   Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Input, ReportID: 0x16, Offset: 7, Size: 1, Value: 0
>    0.060957   Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Feature, ReportID: 0x16, Offset: 7, Size: 1, Value: 0
>    0.061353   Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x16, Offset: 8, Size: 1, Value: 0
>    0.061752   Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x16, Offset: 8, Size: 1, Value: 0
>    0.062147   Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, ReportID: 0x16, Offset: 9, Size: 1, Value: 0
>    0.062550   Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature, ReportID: 0x16, Offset: 9, Size: 1, Value: 0
>    0.063188   Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, Type: Input, ReportID: 0x16, Offset: 10, Size: 1, Value: 0
>    0.063408   Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, Type: Feature, ReportID: 0x16, Offset: 10, Size: 1, Value: 0
>    0.064299   Path: UPS.PowerSummary.RemainingTimeLimit, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 120
>    0.065154   Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x18, Offset: 0, Size: 8, Value: 1
>    0.065791   Path: UPS.Battery.APCBattReplaceDate, Type: Feature, ReportID: 0x1c, Offset: 0, Size: 24, Value: 599297
>    0.066410   Path: UPS.Battery.ManufacturerDate, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 19752
>    0.067027   Path: UPS.Battery.Test, Type: Input, ReportID: 0x21, Offset: 0, Size: 8, Value: 6
>    0.067247   Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 6
>    0.067906   Path: UPS.Battery.RemainingCapacity, Type: Feature, ReportID: 0x22, Offset: 0, Size: 8, Value: 18
>    0.068533   Path: UPS.Battery.RunTimeToEmpty, Type: Feature, ReportID: 0x23, Offset: 0, Size: 16, Value: 262
>    0.069157   Path: UPS.Battery.RemainingTimeLimit, Type: Feature, ReportID: 0x24, Offset: 0, Size: 16, Value: 120
>    0.069783   Path: UPS.Battery.ConfigVoltage, Type: Feature, ReportID: 0x25, Offset: 0, Size: 16, Value: 12
>    0.070424   Path: UPS.Battery.Voltage, Type: Feature, ReportID: 0x26, Offset: 0, Size: 16, Value: 12.59
>    0.071043   Path: UPS.Battery.ff860024, Type: Feature, ReportID: 0x27, Offset: 0, Size: 16, Value: 247
>    0.071667   Path: UPS.Battery.ff860018, Type: Feature, ReportID: 0x28, Offset: 0, Size: 32, Value: -1.34135e+09
>    0.072280   Path: UPS.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 230
>    0.072912   Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 235
>    0.073536   Path: UPS.Input.LowVoltageTransfer, Type: Feature, ReportID: 0x32, Offset: 0, Size: 16, Value: 176
>    0.074160   Path: UPS.Input.HighVoltageTransfer, Type: Feature, ReportID: 0x33, Offset: 0, Size: 16, Value: 282
>    0.074783   Path: UPS.Input.ff860024, Type: Feature, ReportID: 0x34, Offset: 0, Size: 16, Value: 128
>    0.075399   Path: UPS.Input.APCSensitivity, Type: Feature, ReportID: 0x35, Offset: 0, Size: 8, Value: 1
>    0.076023   Path: UPS.Input.APCLineFailCause, Type: Feature, ReportID: 0x36, Offset: 0, Size: 8, Value: 0
>    0.076649   Path: UPS.APCGeneralCollection.APCDelayBeforeReboot, Type: Feature, ReportID: 0x40, Offset: 0, Size: 8, Value: 0
>    0.077279   Path: UPS.APCGeneralCollection.APCDelayBeforeShutdown, Type: Feature, ReportID: 0x41, Offset: 0, Size: 16, Value: -1
>    0.077902   Path: UPS.APCGeneralCollection.DelayBeforeShutdown, Type: Feature, ReportID: 0x42, Offset: 0, Size: 16, Value: -1
>    0.078529   Path: UPS.PowerConverter.PercentLoad, Type: Feature, ReportID: 0x50, Offset: 0, Size: 8, Value: 26
>    0.079478   Path: UPS.PowerConverter.ff860024, Type: Feature, ReportID: 0x51, Offset: 0, Size: 8, Value: 226
>    0.080454   Path: UPS.PowerConverter.ConfigActivePower, Type: Feature, ReportID: 0x52, Offset: 0, Size: 16, Value: 330
>    0.081163   Path: UPS.ff860001.ff860023, Type: Feature, ReportID: 0x60, Offset: 0, Size: 16, Value: 0
>    0.081788   Path: UPS.ff860001.ff860026, Type: Feature, ReportID: 0x61, Offset: 0, Size: 8, Value: 138
>    0.082900   Path: UPS.ff860001.ff860025, Type: Feature, ReportID: 0x62, Offset: 0, Size: 32, Value: 5.0463e+07
>    0.083531   Path: UPS.iProduct, Type: Feature, ReportID: 0x7f, Offset: 0, Size: 8, Value: 5
>    0.084150   Path: UPS.APC_UPS_FirmwareRevision, Type: Feature, ReportID: 0x7e, Offset: 0, Size: 8, Value: 7
>    0.084774   Path: UPS.iSerialNumber, Type: Feature, ReportID: 0x7d, Offset: 0, Size: 8, Value: 3
>    0.085397   Path: UPS.iManufacturer, Type: Feature, ReportID: 0x7c, Offset: 0, Size: 8, Value: 1
>    0.086029   Path: UPS.ManufacturerDate, Type: Feature, ReportID: 0x7b, Offset: 0, Size: 16, Value: 18290
>    0.086659   Path: UPS.PresentStatus.Charging, Type: Feature, ReportID: 0x7a, Offset: 0, Size: 1, Value: 1
>    0.086916   Path: UPS.PresentStatus.Discharging, Type: Feature, ReportID: 0x7a, Offset: 1, Size: 1, Value: 0
>    0.087155   Path: UPS.PresentStatus.ACPresent, Type: Feature, ReportID: 0x7a, Offset: 2, Size: 1, Value: 1
>    0.087368   Path: UPS.PresentStatus.BatteryPresent, Type: Feature, ReportID: 0x7a, Offset: 3, Size: 1, Value: 1
>    0.087585   Path: UPS.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x7a, Offset: 4, Size: 1, Value: 0
>    0.087804   Path: UPS.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x7a, Offset: 5, Size: 1, Value: 0
>    0.088017   Path: UPS.PresentStatus.RemainingTimeLimitExpired, Type: Feature, ReportID: 0x7a, Offset: 6, Size: 1, Value: 0
>    0.088231   Path: UPS.PresentStatus.CommunicationLost, Type: Feature, ReportID: 0x7a, Offset: 7, Size: 1, Value: 0
>    0.088447   Path: UPS.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x7a, Offset: 8, Size: 1, Value: 0
>    0.088668   Path: UPS.PresentStatus.Overload, Type: Feature, ReportID: 0x7a, Offset: 9, Size: 1, Value: 0
>    0.088887   Path: UPS.PresentStatus.VoltageNotRegulated, Type: Feature, ReportID: 0x7a, Offset: 10, Size: 1, Value: 0
>    0.089537   Path: UPS.APCPanelTest, Type: Feature, ReportID: 0x79, Offset: 0, Size: 8, Value: 0
>    0.090152   Path: UPS.AudibleAlarmControl, Type: Feature, ReportID: 0x78, Offset: 0, Size: 8, Value: 1
>    0.090785   Path: UPS.ff860029, Type: Feature, ReportID: 0x75, Offset: 0, Size: 16, Value: 98
>    0.092051   Path: UPS.ff86002a, Type: Feature, ReportID: 0x74, Offset: 0, Size: 32, Value: 3.0318e+08
>    0.092948   Path: UPS.ff860090.ff860091, Type: Feature, ReportID: 0x8c, Offset: 0, Size: 8, Value: 1
>    0.093576   Path: UPS.ff860090.ff860092, Type: Feature, ReportID: 0x8d, Offset: 0, Size: 8, Value: 25
>    0.094305   Path: UPS.ff860090.ff860093, Type: Feature, ReportID: 0x8e, Offset: 0, Size: 8, Value: 36
>    0.094758   Path: UPS.ff860090.ff860094, Type: Feature, ReportID: 0x8f, Offset: 0, Size: 8, Value: 0
>    0.095293   Path: UPS.ff860090.ff860095, Type: Feature, ReportID: 0x90, Offset: 0, Size: 8, Value: 1
>    0.095763   Path: UPS.ff860090.ff860096, Type: Feature, ReportID: 0x91, Offset: 0, Size: 16, Value: 4
>    0.096259   Path: UPS.ff860090.ff860097, Type: Feature, ReportID: 0x92, Offset: 0, Size: 16, Value: 4
>    0.096757   Path: UPS.00000000.ff000055, Type: Feature, ReportID: 0x80, Offset: 0, Size: 8, Value: 0
>    0.096884   Report descriptor retrieved (Reportlen = 1134)
>    0.096919   Found HID device
>    0.096954   Detected a UPS: American Power Conversion/Back-UPS RS 550G FW:857.L5 .I USB FW:L5  
>    0.097057   Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 18
>    0.097169   Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 8, Value: 50
>    0.097273   Path: UPS.Battery.RunTimeToEmpty, Type: Feature, ReportID: 0x23, Offset: 0, Size: 16, Value: 262
>    0.097423   Path: UPS.Battery.Voltage, Type: Feature, ReportID: 0x26, Offset: 0, Size: 16, Value: 12.59
>    0.097553   Path: UPS.Battery.ConfigVoltage, Type: Feature, ReportID: 0x25, Offset: 0, Size: 16, Value: 12
>    0.097676   Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x03, Offset: 0, Size: 8, Value: 4
>    0.098542   Path: UPS.Battery.ManufacturerDate, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 19752
>    0.098659   Path: UPS.Battery.APCBattReplaceDate, Type: Feature, ReportID: 0x1c, Offset: 0, Size: 24, Value: 599297
>    0.098762   Path: UPS.PowerConverter.PercentLoad, Type: Feature, ReportID: 0x50, Offset: 0, Size: 8, Value: 26
>    0.098951   Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
>    0.099201   Path: UPS.APCGeneralCollection.APCDelayBeforeReboot, Type: Feature, ReportID: 0x40, Offset: 0, Size: 8, Value: 0
>    0.099280   Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 6
>    0.099361   Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x18, Offset: 0, Size: 8, Value: 1
>    0.099448   Path: UPS.ManufacturerDate, Type: Feature, ReportID: 0x7b, Offset: 0, Size: 16, Value: 18290
>    0.099551   Path: UPS.PowerConverter.ConfigActivePower, Type: Feature, ReportID: 0x52, Offset: 0, Size: 16, Value: 330
>    0.099663   Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x16, Offset: 2, Size: 1, Value: 1
>    0.099740   Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x16, Offset: 1, Size: 1, Value: 0
>    0.099817   Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x16, Offset: 0, Size: 1, Value: 1
>    0.099889   Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x16, Offset: 5, Size: 1, Value: 0
>    0.099964   Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x16, Offset: 4, Size: 1, Value: 0
>    0.100036   Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature, ReportID: 0x16, Offset: 9, Size: 1, Value: 0
>    0.100118   Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x16, Offset: 8, Size: 1, Value: 0
>    0.100193   Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Feature, ReportID: 0x16, Offset: 6, Size: 1, Value: 0
>    0.100274   Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: Feature, ReportID: 0x16, Offset: 3, Size: 1, Value: 1
>    0.100346   Path: UPS.PowerSummary.Charging, Type: Feature, ReportID: 0x06, Offset: 0, Size: 8, Value: 1
>    0.100415   Path: UPS.PowerSummary.Discharging, Type: Feature, ReportID: 0x06, Offset: 8, Size: 8, Value: 0
>    0.100485   Path: UPS.PowerSummary.ACPresent, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 1
>    0.100555   Path: UPS.PowerSummary.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 0
>    0.100621   Path: UPS.PowerSummary.ShutdownImminent, Type: Feature, ReportID: 0x14, Offset: 8, Size: 8, Value: 0
>    0.100685   Path: UPS.PowerSummary.APCStatusFlag, Type: Feature, ReportID: 0x06, Offset: 16, Size: 8, Value: 8
>    0.100754   Path: UPS.Input.APCLineFailCause, Type: Feature, ReportID: 0x36, Offset: 0, Size: 8, Value: 0
>    0.100829   Path: UPS.Input.APCLineFailCause, Type: Feature, ReportID: 0x36, Offset: 0, Size: 8, Value: 0
>    0.100898   Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 235
>    0.100980   Path: UPS.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 230
>    0.101103   Path: UPS.Input.LowVoltageTransfer, Type: Feature, ReportID: 0x32, Offset: 0, Size: 16, Value: 176
>    0.101197   Path: UPS.Input.HighVoltageTransfer, Type: Feature, ReportID: 0x33, Offset: 0, Size: 16, Value: 282
>    0.101277   Path: UPS.Input.APCSensitivity, Type: Feature, ReportID: 0x35, Offset: 0, Size: 8, Value: 1
>    0.101492   Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 6
>    0.101581   Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 6
>    0.101668   Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 6
>    0.101735   Path: UPS.APCPanelTest, Type: Feature, ReportID: 0x79, Offset: 0, Size: 8, Value: 0
>    0.101803   Path: UPS.APCPanelTest, Type: Feature, ReportID: 0x79, Offset: 0, Size: 8, Value: 0
>    0.101914   Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
>    0.102004   Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
>    0.102169   Path: UPS.APCGeneralCollection.APCDelayBeforeShutdown, Type: Feature, ReportID: 0x41, Offset: 0, Size: 16, Value: -1
>    0.102249   Path: UPS.APCGeneralCollection.APCDelayBeforeShutdown, Type: Feature, ReportID: 0x41, Offset: 0, Size: 16, Value: -1
>    0.102311   Path: UPS.APCGeneralCollection.APCDelayBeforeReboot, Type: Feature, ReportID: 0x40, Offset: 0, Size: 8, Value: 0
>    0.102403   Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x18, Offset: 0, Size: 8, Value: 1
>    0.102478   Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x18, Offset: 0, Size: 8, Value: 1
>    0.102556   Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x18, Offset: 0, Size: 8, Value: 1
>    0.102625   Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x18, Offset: 0, Size: 8, Value: 1
>    0.102696   Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x18, Offset: 0, Size: 8, Value: 1
>    0.102831   find_nut_info: unknown info type: load.on.delay
>    0.102880   find_nut_info: unknown info type: load.on.delay
>    0.102946   upsdrv_initinfo...
>    0.102995   upsdrv_updateinfo...
>    0.103404   Got 2 HID objects...
>    0.103475   Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x0c, Offset: 0, Size: 8, Value: 18
>    0.103552   Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x0c, Offset: 8, Size: 16, Value: 262
>    0.103596   Quick update...




More information about the Nut-upsuser mailing list