[Nut-upsuser] Debian 10 nut 2.7.4-8 and APC Back UPS 600i on 940-0020B

tovis r-visor tovis at r-visor.hu
Sun Sep 8 20:17:48 BST 2019


> On Wed, 28 Aug 2019, tovis r-visor wrote:
>> I was switch to battery, after 2-3 second it show that is on battery OB
and after it shutdown because of low battery LO.
> I wondered how old is your battery ?
> Roger
> I have change it 2019.03.08. 12V/10Ah YUASA.
> I was checked not only battery voltage (13.6V without load), but
charging > voltage and output voltage using true rms dmm.
> It is working well with Debian 6
>
> tovis

After long struggling, check every parts of UPS and cable, I have realized
that is after boot I reload the driver the system work well:
# systemctl restart nut-driver.service
I was checked up to real "battery low" and shutdown, switch off the UPS
every thing goes well.
I was activated /etc/rc.local but it is starting before that Netwrok UPS
Tools starting - nothing to restart.
What can I do now?
Any suggestion?

  tovis