[Nut-upsuser] SNMP shutdown timing out

Lee Damon nomad at ee.washington.edu
Wed Apr 29 23:00:16 BST 2020


I'm in the process of trying to get NUT to manage an APC SmartUPS.

Monitoring of the UPS is working fine:
$ upsc nutdev1 at localhost
Init SSL without certificate database
ambient.1.humidity.alarm.high: 60.00
ambient.1.humidity.alarm.low: 30.00
ambient.1.temperature.alarm.high: 40.00
ambient.1.temperature.alarm.low: 10.00
battery.charge: 94.00
battery.charge.restart: 0
battery.current: 0.00
battery.date: 03/14/20
battery.packs: 0.00
battery.packs.bad: -1.00
battery.runtime: 5160.00
battery.runtime.low: 120
battery.voltage: 27.00
battery.voltage.nominal: -1.00
device.mfr: APC
device.model: SMART-UPS 1400
device.serial: WS9831004667
device.type: ups
driver.name: snmp-ups
driver.parameter.authProtocol: MD5
driver.parameter.mibs: apcc
driver.parameter.pollinterval: 2
driver.parameter.port: 192.5.37.191
driver.parameter.privProtocol: DES
driver.parameter.secLevel: authPriv
driver.parameter.synchronous: no
driver.version: 2.7.4
driver.version.data: apcc MIB 1.2
driver.version.internal: 0.97
input.frequency: 60.00
input.sensitivity: high
input.transfer.high: 132
input.transfer.low: 103
input.transfer.reason: selfTest
input.voltage: 120.90
input.voltage.maximum: 122.20
input.voltage.minimum: 120.20
output.current: 0.00
output.frequency: 60.00
output.voltage: 120.90
output.voltage.nominal: 115
ups.delay.shutdown: 20
ups.delay.start: 0
ups.firmware: 70.11.D
ups.id: apcups
ups.load: 14.00
ups.mfr: APC
ups.mfr.date: 07/28/98
ups.model: SMART-UPS 1400
ups.serial: WS9831004667
ups.status: OL
ups.temperature: 24.70
ups.test.date: 04/29/2020
ups.test.result: Ok

I can use snmpset to halt the UPS.
  snmpset -v 3 -a MD5 -A NutScan at Password43LongerWord -l authPriv -u nut -x
DES -X NutScan at Password43LongerWord apcups
SNMPv2-SMI::enterprises.318.1.1.1.6.1.1.0 i 2

(Passwords are temporary, I don't care if they leak.)

I am aware of the note in the MIB that states "Setting this variable to
turnUpsOffToConserveBattery(2) causes a UPS on battery to be put into
'sleep' mode.  The UPS will turn back on when utility power is restored.
Attempting to turn off a UPS that is not on battery will result in a
badValue error." so tests are being done with the UPS on battery.

However, when I try to tell it to shut down the UPS it fails with a timeout.

$ sudo snmp-ups -DDDDDDD -a nutdev1 -k
Network UPS Tools - Generic SNMP UPS driver 0.97 (2.7.4)
   0.000000     send_to_all: SETINFO driver.parameter.port "192.5.37.191"
   0.000027     send_to_all: SETINFO driver.parameter.mibs "apcc"
   0.000044     send_to_all: SETINFO driver.parameter.secLevel "authPriv"
   0.000049     send_to_all: SETINFO driver.parameter.authProtocol "MD5"
   0.000067     send_to_all: SETINFO driver.parameter.privProtocol "DES"
   0.000071     debug level is '7'
   0.001365     SNMP UPS driver: entering upsdrv_initups()
   0.001371     SNMP UPS driver: entering nut_snmp_init(snmp-ups)
   0.008570     Setting SNMP retries to 5
   0.008575     Setting SNMP timeout to 1 second(s)
   0.008605     SNMP UPS driver: entering load_mib2nut(apcc)
   0.008610     load_mib2nut: trying classic method with 'apcc' mib
   0.008613     su_find_info: "ups.model" found
   0.008615     Testing ups.model using OID .1.3.6.1.4.1.318.1.1.1.1.1.1.0
   0.008617     Entering nut_snmp_get_str()
   0.008619     nut_snmp_get(.1.3.6.1.4.1.318.1.1.1.1.1.1.0)
   0.008637     nut_snmp_walk(.1.3.6.1.4.1.318.1.1.1.1.1.1.0)
   0.008640     nut_snmp_walk: max. iteration = 1
   0.027623     load_mib2nut: testOID provided and matches MIB 'apcc'!
   0.027636     load_mib2nut: using apcc mib
   0.027639     su_find_info: "ups.model" found
   0.027641     Entering nut_snmp_get_str()
   0.027642     nut_snmp_get(.1.3.6.1.4.1.318.1.1.1.1.1.1.0)
   0.027644     nut_snmp_walk(.1.3.6.1.4.1.318.1.1.1.1.1.1.0)
   0.027646     nut_snmp_walk: max. iteration = 1
   0.051176     Detected SMART-UPS 1400 on host 192.5.37.191 (mib: apcc 1.2)
   0.051192     su_find_info: unknown info type (load.off.delay)
   0.051195     su_find_info: unknown info type (load.on.delay)
   0.051197     su_find_info: unknown info type (load.off.delay)
   0.051199     Initiating UPS shutdown
   0.051201     upsdrv_shutdown...
   0.051203     Unknown template type: shutdown.return
   0.051204     entering su_instcmd(shutdown.return, (null))
   0.051207     su_find_info: "shutdown.return" found
   0.051209     entering nut_snmp_set(.1.3.6.1.4.1.318.1.1.1.6.1.1.0, i, 2)
   6.059576     [nutdev1] nut_snmp_set: can't set
.1.3.6.1.4.1.318.1.1.1.6.1.1.0: Timeout
   6.059591     su_instcmd: cannot set value for shutdown.return
   6.059593     Unknown template type: shutdown.reboot
   6.059595     entering su_instcmd(shutdown.reboot, (null))
   6.059599     su_find_info: unknown info type (shutdown.reboot)
   6.059601     su_instcmd: shutdown.reboot unavailable
   6.059602     Unknown template type: load.off.delay
   6.059603     entering su_instcmd(load.off.delay, (null))
   6.059606     su_find_info: unknown info type (load.off.delay)
   6.059608     su_instcmd: load.off.delay unavailable
   6.059609     Shutdown failed!

This *might* be related to the question I asked yesterday about nut-scanner
but given the difference in error reported (nut-scanner was complaining
about auth) I don't think so.

I'm using nut packages from EPEL 8 for all of this.

I've set SELinux to permissive (even tried 'disabled') and it doesn't
appear to be blocking anything.

Anyone have any suggestions for what I can try next?