[Nut-upsuser] System with MGE UPS shuts down too early

Manuel Wolfshant wolfy at nobugconsulting.ro
Sat Jan 11 12:24:22 GMT 2020


On January 11, 2020 1:18:27 PM GMT+02:00, "Georgi D. Sotirov" <gdsotirov at gmail.com> wrote:
>Hello,
>
>I'm experiencing a strange early shutdown behavior with the following 
>system:
>
>  * */OS/*: Slackware Linux 14.2 x86_64
>  * */NUT/*: 2.7.4 (from my own package
>    <https://sotirov-bg.net/slackpack/pack.cgi?id=4083>)
>  * */UPS/*: MGE Ellipse PRO 1600
><powerquality.eaton.com/Products-services/Backup-Power-UPS/Ellipse-PRO.aspx>
>    (bought in September 2017)
>
>*/Problem description/*: An hour ago there was a power outage for about
>
>3-4 minutes. However, the system was forcefully shut down just after a 
>minute (!) and I'm not sure I understand why. This is what I found into
>
>the logs:
>
>  * /var/log/messages (only relevant):
>
>Jan 11 11:49:15 sotirov-bg upsmon[2677]: UPS mgeups at localhost on
>battery
>Jan 11 11:49:15 sotirov-bg upssched[29746]: Executing command: 
>ups-on-battery
>Jan 11 11:49:15 sotirov-bg upssched-cmd: Unrecognized command: 
>ups-on-battery
>Jan 11 11:50:20 sotirov-bg upsmon[2677]: UPS mgeups at localhost battery
>is low
>Jan 11 11:50:20 sotirov-bg upsd[2672]: Client monuser at 127.0.0.1 set FSD
>
>on UPS [mgeups]
>Jan 11 11:50:20 sotirov-bg upsmon[2677]: Auto logout and shutdown
>proceeding
>Jan 11 11:50:20 sotirov-bg upssched[30461]: Executing command:
>ups-low-batt
>Jan 11 11:50:20 sotirov-bg upssched-cmd: Unrecognized command:
>ups-low-batt
>Jan 11 11:50:20 sotirov-bg upssched[30466]: Executing command:
>ups-shutdown
>Jan 11 11:50:20 sotirov-bg upssched-cmd: Unrecognized command:
>ups-shutdown
>Jan 11 11:50:25 sotirov-bg shutdown[30471]: shutting down for system
>halt
>Jan 11 11:50:25 sotirov-bg init: Switching to runlevel: 0
>
>  * /var/log/ups (snippet of consecutive messages):
>
>20200111 114901 100 221.0 17 [OL] NA 50.0
>20200111 114906 100 221.0 17 [OL] NA 50.0
>20200111 114911 100 221.0 17 [OL] NA 50.0
>20200111 114916 99 0.0 19 [OB] NA 0.0
>20200111 114921 99 0.0 19 [OB] NA 0.0
>20200111 114926 99 0.0 19 [OB] NA 0.0
>20200111 114931 99 0.0 19 [OB] NA 0.0
>20200111 114936 99 0.0 19 [OB] NA 0.0
>20200111 114941 99 0.0 19 [OB] NA 0.0
>20200111 114946 98 0.0 16 [OB] NA 0.0
>20200111 114951 98 0.0 16 [OB] NA 0.0
>20200111 114956 98 0.0 16 [OB] NA 0.0
>20200111 115001 98 0.0 16 [OB] NA 0.0
>20200111 115006 98 0.0 16 [OB] NA 0.0
>20200111 115011 98 0.0 16 [OB] NA 0.0
>20200111 115016 98 0.0 16 [OB] NA 0.0
>20200111 115021 96 0.0 18 [FSD ALARM OB LB] NA 0.0
>20200111 115026 96 0.0 18 [FSD ALARM OB LB] NA 0.0
>20200111 115031 96 0.0 18 [FSD ALARM OB LB] NA 0.0
>20200111 115036 96 0.0 18 [FSD ALARM OB LB] NA 0.0
>20200111 115041 96 0.0 18 [FSD ALARM OB LB] NA 0.0
>20200111 115044 96 0.0 18 [FSD ALARM OB LB] NA 0.0
>20200111 120209 NA NA NA [WAIT] NA NA
>20200111 120214 84 217.0 16 [OL] NA 50.0
>20200111 120219 84 217.0 16 [OL] NA 50.0
>20200111 120224 84 217.0 16 [OL] NA 50.0
>
>What bugs me is that for just over a minute on battery power the status
>
>changes to FSD ALARM OB LB (see in red above), while at this moment the
>
>battery charge is 96 % (!?). After the power was restored the system 
>didn't come up, so I had to power it up manually. Checking the battery 
>charge afterwards it was still 85 %, so I'm really not sure why NUT 
>shutdown the system so early. I have tested the shutdown sequence in 
>September 2017 after I installed the UPS by manually removing the
>online 
>power and the system was shutdown properly after about 30 minutes. In 
>several previous occasions I didn't notice such problem and the system 
>was shutdown after the battery reached the critical charge level of 20% or managed to discharge the battery until online power restored.
>
>Any suggestions what could be the problem? What does this "ALARM" in 
>status mean? I checked older ups monitor logs and I did not find such 
>status.
>
>
"Jan 11 11:50:20 sotirov-bg upsmon[2677]: UPS mgeups at localhost battery is low"
indicates that the UPS thought that battery was close to depleted and decided to shutdown. I suggest to fully retest your battery ( doing a full charge/discharge cycle with a dummy load ), I suspect it is not any more as good as you believe it to be.


wolfy



More information about the Nut-upsuser mailing list