[Nut-upsuser] System with MGE UPS shuts down too early
    Georgi D. Sotirov 
    gdsotirov at gmail.com
       
    Sat Jan 11 13:02:59 GMT 2020
    
    
  
OK. I'll try it, but it really puzzles me how the battery could have 
gone bad for just 15 months. The online power is pretty stable, so the 
battery hasn't gone through many charge/discharge cycles...
Regards,
--
Georgi
On 11.1.2020 at 14:24, Manuel Wolfshant wrote:
>
> indicates that the UPS thought that battery was close to depleted and decided to shutdown. I suggest to fully retest your battery ( doing a full charge/discharge cycle with a dummy load ), I suspect it is not any more as good as you believe it to be.
>
>
> wolfy
    
    