[Nut-upsuser] System with MGE UPS shuts down too early
Georgi D. Sotirov
gdsotirov at gmail.com
Mon Jan 27 09:27:01 GMT 2020
Hello Manuel,
> that looks perfectly fine
That one yes, but as I wrote, LB and FSD are happening on much higher
battery charge values - 90% or more, which is not fine.
> That's... surprisingly well, assuming your multimeter indicates
> correct values. I would have expected values well below 12V
My multimeter hasn't gone inspection recently, but I do not have reasons
to believe that the readings are wrong :-)
> Can you please show us all the configuration files ? I can only
> suspect that there is something wrong there because (from a hardware
> point of view) the UPS behaves very very well, according to your tests
> and logs.
Which configuration files you'd like to see exactly? I haven't made many
configuration changes anyway. Isn't the UPS that reports LB (Low
Battery) and FSB (forcing shutdown of the machine)? I mean if this is a
configuration issue, then why I did not have this problem before? Why
the shutdown happens on different battery charge levels?
Regards,
--
Georgi
On 27.1.2020 at 2:53, Manuel Wolfshant wrote:
> On 1/25/20 10:53 AM, Georgi D. Sotirov wrote:
>> OK, so yesterday evening I done a real test cutting of the power to
>> the UPS. And it went good... the UPS supported my server for 28:50
>> minutes (i.e. the expected runtime with this load), before forcing
>> shutdown. The batteries could still hold as charge was 30 % with
>> about 15 minutes run time. And the UPS did hold for another full 10
>> minutes before powering off. These are the relevant lines from
>> /var/log/ups:
>>
>> 20200124 201318 32 0.0 12 [OB] NA 0.0
>> 20200124 201323 30 0.0 13 [ALARM OB LB] NA 0.0
>> 20200124 201328 30 0.0 13 [FSD ALARM OB LB] NA 0.0
>> 20200124 201333 30 0.0 13 [FSD ALARM OB LB] NA 0.0
>> 20200124 201338 30 0.0 13 [FSD ALARM OB LB] NA 0.0
>> 20200124 201340 30 0.0 13 [FSD ALARM OB LB] NA 0.0
>
> that looks perfectly fine
>
>
>>
>> The server was shutdown properly, but for some reason it did not
>> power off. I saw an error from umount about busy file system, but I'm
>> sure this doesn't always happen.
>
> the error is related to your linux system, not to nut
>
>
>>
>> With everything powered off, I extracted the original batteries to
>> check them and measure the voltage. The batteries are Leoch DJW12-9.0
>> with one of them at 12.57 V and the other at 12.64 V (measured
>> without load after the discharge).
>
> That's... surprisingly well, assuming your multimeter indicates
> correct values. I would have expected values well below 12V
>
>
>
>>
>> And this morning there was again a short power failure (not more than
>> 30 minutes, because the router connected to the battery power from
>> the UPS did hold up). With batteries charged up to 91% the UPS
>> supported the server for just 07:10 minutes and forced shutdown with
>> 69% battery charge and over 20 minutes of run time...
>>
>> 20200125 021123 70 0.0 16 [OB] NA 0.0
>> 20200125 021128 69 0.0 16 [FSD ALARM OB LB] NA 0.0
>> 20200125 021133 69 0.0 16 [FSD ALARM OB LB] NA 0.0
>> 20200125 021138 69 0.0 16 [FSD ALARM OB LB] NA 0.0
>> 20200125 021143 69 0.0 16 [FSD ALARM OB LB] NA 0.0
>> 20200125 021148 69 0.0 16 [FSD ALARM OB LB] NA 0.0
>> 20200125 021150 69 0.0 16 [FSD ALARM OB LB] NA 0.0
>>
>> So, it seems to me that my UPS forces shutdown pretty randomly. Why
>> the UPS is not waiting for the preset low battery charge value of
>> 15%? What is actually driving this FSD ALARM and LB signal when
>> batteries for sure could hold up more?
>
>
> Can you please show us all the configuration files ? I can only
> suspect that there is something wrong there because (from a hardware
> point of view) the UPS behaves very very well, according to your tests
> and logs.
>
>
>
> _______________________________________________
> Nut-upsuser mailing list
> Nut-upsuser at alioth-lists.debian.net
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20200127/a3ad9267/attachment-0001.html>
More information about the Nut-upsuser
mailing list