[Nut-upsuser] AVR750U Low Power not Triggering Shutdown
Manuel Wolfshant
wolfy at nobugconsulting.ro
Sun Jun 28 03:17:17 BST 2020
On 6/28/20 4:25 AM, Scott Colby wrote:
> Hello,
>
> I am having difficulty using NUT to shut down my Netgate SG-1100
> (a pfSense router) when the power level of the UPS gets critically
> low.
>
> Here is some relevant information:
> - OS: pfSense 2.4.5-RELEASE-p1 (FreeBSD 11.3-STABLE)
> - NUT version: 2.7.4
> - Installed from: pfSense package 2.7.4_7
> - UPS: AVR750U (Device release number 2)
> - I have included my config files, output from `upsc`, and output
> from running the driver in debug mode at the bottom of this message.
>
> To get this UPS to work with NUT, I had to create a custom devd
> rule:
> # cat /usr/local/etc/devd/nut-usb-custom.conf
> notify 100 {
> match "system" "USB";
> match "subsystem" "DEVICE";
> match "type" "ATTACH";
> match "vendor" "0x09ae";
> match "product" "0x3024"; # difference from default config here
> action "chgrp uucp /dev/$cdev; chmod g+rw /dev/$cdev";
> };
> It seems like my particular AVR750U has a different product id than
> the one that came in the package at /usr/local/etc/nut-usb.conf,
> which has a similar rule entry but with product id 0x1007. I'm not
> sure if this is a package maintainer issue or a NUT isue.
Manufacturers change product IDs over time. Both nut as product and the
various packages shipped by unix distributions need to adjust according
to those changes
>
> I unplugged the UPS from the mains power and let it run down. The
> battery level and time remaining numbers seemed to update correctly
> during this, but when the battery got down to 1% and showed less
> than one minute of time remaining, NUT still hadn't shut down the
> device--I chickened out and plugged it back in. Following the advice
> from usbhid-ups(8), I ran `upsmon -c fsd` which properly brought
> the system down but did not power cycle the UPS.
>
> I am a little unclear on what actually causes NUT to issue the
> shutdown command. I've read something about the "low power flag:"
> is that something that the UPS decides on?
Indeed, the UPS sends a specific flag ( LB == low battery ) when it
believes that the battery is depleted below a specific level. How nut
behaves depends on the actual configuration, as a few other variables
are also taken into account.
>
> Have I made a configuration error?
yes, I think that you did a small error. see below
> Do I need to set some configuration
> on the UPS with `upsrw` or something? Do I need to use Tripp Lite's
> Windows software to configure something before using it with NUT?
> Is this a new version of the AVR750U that's not compatible yet with
> NUT?
no, no and no.
>
> Thank you for your attention to my questions,
> Scott
>
>
> # cat nut.conf
> MODE=none
According to the documentation included in the nut.conf file ( at least
in linux.. ), you should change this line to
MODE=standalone
because "none" means nut is not yet configured and prohibits it from
even starting . You can of course use "netserver" instead if you plan to
power down more servers that will talk with the one which is actually
connected to the UPS. Do not forget to start the services after
modifying the config file
Here is a quote from the content of that file from a linux box:
# The values of MODE can be:
# - none: NUT is not configured, or use the Integrated Power Management,
or use
# some external system to startup NUT components. So nothing is to be
started.
# - standalone: This mode address a local only configuration, with 1 UPS
# protecting the local system. This implies to start the 3 NUT layers
(driver,
# upsd and upsmon) and the matching configuration files. This mode can
also
# address UPS redundancy.
# - netserver: same as for the standalone configuration, but also need
# some more network access controls (firewall, tcp-wrappers) and
possibly a
# specific LISTEN directive in upsd.conf.
# Since this MODE is opened to the network, a special care should be
applied
# to security concerns.
# - netclient: this mode only requires upsmon
>
> # cat ups.conf
> [AVR750U]
> driver=usbhid-ups
> port=auto
> productid=3024
>
> # cat upsmon.conf
> MONITOR AVR750U 1 local-monitor <password> master
> SHUTDOWNCMD "/sbin/shutdown -p +0"
> POWERDOWNFLAG /etc/killpower
> NOTIFYCMD /usr/local/pkg/nut/nut_email.php
> NOTIFYFLAG ONLINE SYSLOG+WALL+EXEC
> NOTIFYFLAG ONBATT SYSLOG+WALL+EXEC
> NOTIFYFLAG LOWBATT SYSLOG+WALL+EXEC
> NOTIFYFLAG FSD SYSLOG+WALL+EXEC
> NOTIFYFLAG COMMOK SYSLOG+WALL+EXEC
> NOTIFYFLAG COMMBAD SYSLOG+WALL+EXEC
> NOTIFYFLAG SHUTDOWN SYSLOG+WALL+EXEC
> NOTIFYFLAG REPLBATT SYSLOG+WALL+EXEC
> NOTIFYFLAG NOCOMM SYSLOG+WALL+EXEC
> NOTIFYFLAG NOPARENT SYSLOG+WALL+EXEC
>
> # upsc AVR750U
> battery.charge: 100
> battery.charge.warning: 30
> battery.runtime: 3649
> battery.type: PbAc
> battery.voltage: 0.0
> battery.voltage.nominal: 12.0
> device.mfr: Tripp Lite
> device.model: AVR750U
> device.serial: 2945CVLOM87C901526
> device.type: ups
> driver.name: usbhid-ups
> driver.parameter.pollfreq: 30
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.parameter.productid: 3024
> driver.parameter.synchronous: no
> driver.version: 2.7.4
> driver.version.data: TrippLite HID 0.82
> driver.version.internal: 0.41
> input.frequency: 5990.0
This value is definitely incorrectly reported. Based on the voltages
below I assume you are in USA and the displayed value could be an
incorrectly scaled 59.9 Hz
> input.transfer.high: 145.0
> input.transfer.low: 89.0
> input.voltage: 0.0
> input.voltage.nominal: 120
> output.current: 0.0
> output.frequency: 5990.0
As above, I guess this should actually be 59.9 Hz
> output.frequency.nominal: 60
> output.voltage: 0.0
> output.voltage.nominal: 120
> ups.beeper.status: muted
> ups.delay.shutdown: 20
> ups.delay.start: 30
> ups.load: 0
> ups.mfr: Tripp Lite
> ups.model: AVR750U
> ups.power: 0.0
> ups.power.nominal: 750
> ups.productid: 3024
> ups.serial: 2945CVLOM87C901526
> ups.status: OL
> ups.timer.reboot: 65535
> ups.timer.shutdown: 65535
> ups.timer.start: 65535
> ups.vendorid: 09ae
> ups.watchdog.status: 0
>
> # /usr/local/libexec/nut/usbhid-ups -DD -a AVR750U
> Network UPS Tools - Generic HID driver 0.41 (2.7.4)
> USB communication driver 0.33
> 0.000000 debug level is '2'
> 0.001637 upsdrv_initups...
> 0.002374 Checking device (09AE/3024) (/dev/usb//dev/ugen1.2)
> 0.014968 - VendorID: 09ae
> 0.015020 - ProductID: 3024
> 0.015031 - Manufacturer: Tripp Lite
> 0.015041 - Product: AVR750U
> 0.015052 - Serial Number: 2945CVLOM87C901526
> 0.015061 - Bus: /dev/usb
> 0.015071 - Device release number: 0002
> 0.015084 Trying to match device
> 0.015265 Device matches
> 0.016003 HID descriptor length 885
> 0.020119 Report Descriptor size = 885
> 0.021057 Using subdriver: TrippLite HID 0.82
> 0.021116 87 HID objects found
> 0.022059 Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x28, Offset: 0, Size: 8, Value: 1
> 0.023013 Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 5
> 0.024007 Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: 0x2b, Offset: 0, Size: 8, Value: 3
> 0.025006 Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 120
> 0.025997 Path: UPS.PowerSummary.Input.Voltage, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 0.001233
> 0.027006 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 3
> 0.027995 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
> 0.028034 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
> 0.028059 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
> 0.028084 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
> 0.028138 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x32, Offset: 16, Size: 1, Value: 1
> 0.028164 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 16, Size: 1, Value: 1
> 0.028188 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x32, Offset: 18, Size: 1, Value: 0
> 0.028212 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
> 0.028237 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x32, Offset: 20, Size: 1, Value: 0
> 0.028262 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
> 0.028286 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
> 0.028310 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
> 0.028333 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 18, Size: 1, Value: 0
> 0.028357 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
> 0.028383 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 20, Size: 1, Value: 0
> 0.028407 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
> 0.028430 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
> 0.028454 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
> 0.029017 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x2a, Offset: 0, Size: 8, Value: 4
> 0.030035 Path: UPS.PowerSummary.iOEMInformation, Type: Feature, ReportID: 0x62, Offset: 0, Size: 8, Value: 2
> 0.030999 Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x33, Offset: 0, Size: 8, Value: 2
> 0.031992 Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x34, Offset: 0, Size: 8, Value: 100
> 0.032029 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x34, Offset: 0, Size: 8, Value: 100
> 0.033026 Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, ReportID: 0x37, Offset: 0, Size: 8, Value: 100
> 0.034014 Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 0x36, Offset: 0, Size: 8, Value: 100
> 0.035013 Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, ReportID: 0x38, Offset: 0, Size: 8, Value: 30
> 0.035995 Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID: 0x2c, Offset: 0, Size: 8, Value: 1
> 0.037002 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x35, Offset: 0, Size: 16, Value: 3650
> 0.037045 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x35, Offset: 0, Size: 16, Value: 3650
> 0.038032 Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature, ReportID: 0x04, Offset: 0, Size: 16, Value: 12
> 0.038999 Path: UPS.BatterySystem.Battery.Voltage, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 0.000137
> 0.040012 Path: UPS.BatterySystem.Battery.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x23, Offset: 2, Size: 1, Value: 0
> 0.040243 Path: UPS.BatterySystem.Battery.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x23, Offset: 3, Size: 1, Value: 1
> 0.040273 Path: UPS.BatterySystem.Battery.PresentStatus.Charging, Type: Feature, ReportID: 0x23, Offset: 4, Size: 1, Value: 0
> 0.040298 Path: UPS.BatterySystem.Battery.PresentStatus.Discharging, Type: Feature, ReportID: 0x23, Offset: 5, Size: 1, Value: 0
> 0.040321 Path: UPS.BatterySystem.Battery.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x23, Offset: 6, Size: 1, Value: 0
> 0.040345 Path: UPS.BatterySystem.Battery.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x23, Offset: 7, Size: 1, Value: 0
> 0.041012 Path: UPS.BatterySystem.Battery.RemainingCapacity, Type: Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 100
> 0.042012 Path: UPS.BatterySystem.Battery.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 6
> 0.043020 Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 120
> 0.044002 Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 60
> 0.045016 Path: UPS.Flow.ffff0097, Type: Feature, ReportID: 0x55, Offset: 0, Size: 8, Value: 2
> 0.046012 Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID: 0x03, Offset: 0, Size: 16, Value: 750
> 0.047000 Path: UPS.PowerConverter.Input.Voltage, Type: Feature, ReportID: 0x18, Offset: 0, Size: 16, Value: 0.001233
> 0.048042 Path: UPS.PowerConverter.Input.Frequency, Type: Feature, ReportID: 0x19, Offset: 0, Size: 16, Value: 5990
So the UPS reports a frequency which nut should scale ...
> 0.049011 Path: UPS.PowerConverter.Output.Voltage, Type: Feature, ReportID: 0x1b, Offset: 0, Size: 16, Value: 0.001233
> 0.050013 Path: UPS.PowerConverter.Output.Frequency, Type: Feature, ReportID: 0x1c, Offset: 0, Size: 16, Value: 5990
Again , scaling error...
> 0.050996 Path: UPS.PowerConverter.Output.Current, Type: Feature, ReportID: 0x46, Offset: 0, Size: 16, Value: 0
> [...]
> 0.083217 Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 120
> 0.083281 Path: UPS.PowerSummary.Input.Voltage, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 0.001233
> 0.083375 Path: UPS.PowerConverter.Input.Frequency, Type: Feature, ReportID: 0x19, Offset: 0, Size: 16, Value: 5990
and again...
> 0.083451 Path: UPS.PowerConverter.Output.LowVoltageTransfer, Type: Feature, ReportID: 0x06, Offset: 0, Size: 16, Value: 89
> 0.083579 Path: UPS.PowerConverter.Output.HighVoltageTransfer, Type: Feature, ReportID: 0x09, Offset: 0, Size: 16, Value: 145
> 0.083698 Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 120
> 0.083761 Path: UPS.PowerConverter.Output.Voltage, Type: Feature, ReportID: 0x1b, Offset: 0, Size: 16, Value: 0.001233
> 0.083847 Path: UPS.PowerConverter.Output.Current, Type: Feature, ReportID: 0x46, Offset: 0, Size: 16, Value: 0
> 0.083909 Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 60
> 0.084153 Path: UPS.PowerConverter.Output.Frequency, Type: Feature, ReportID: 0x1c, Offset: 0, Size: 16, Value: 5990
and again
wolfy