[Nut-upsuser] AVR750U Low Power not Triggering Shutdown

Manuel Wolfshant wolfy at nobugconsulting.ro
Sun Jun 28 03:17:17 BST 2020


On 6/28/20 4:25 AM, Scott Colby wrote:
> Hello,
>
> I am having difficulty using NUT to shut down my Netgate SG-1100
> (a pfSense router) when the power level of the UPS gets critically
> low.
>
> Here is some relevant information:
> - OS: pfSense 2.4.5-RELEASE-p1 (FreeBSD 11.3-STABLE)
> - NUT version: 2.7.4
> - Installed from: pfSense package 2.7.4_7
> - UPS: AVR750U (Device release number 2)
> - I have included my config files, output from `upsc`, and output
> from running the driver in debug mode at the bottom of this message.
>
> To get this UPS to work with NUT, I had to create a custom devd
> rule:
> # cat /usr/local/etc/devd/nut-usb-custom.conf
> notify 100 {
>          match "system"          "USB";
>          match "subsystem"       "DEVICE";
>          match "type"            "ATTACH";
>          match "vendor"          "0x09ae";
>          match "product"         "0x3024";  # difference from default config here
>          action "chgrp uucp /dev/$cdev; chmod g+rw /dev/$cdev";
> };
> It seems like my particular AVR750U has a different product id than
> the one that came in the package at /usr/local/etc/nut-usb.conf,
> which has a similar rule entry but with product id 0x1007. I'm not
> sure if this is a package maintainer issue or a NUT isue.

Manufacturers change product IDs over time. Both nut as product and the 
various packages shipped by unix distributions need to adjust according 
to those changes



>
> I unplugged the UPS from the mains power and let it run down. The
> battery level and time remaining numbers seemed to update correctly
> during this, but when the battery got down to 1% and showed less
> than one minute of time remaining, NUT still hadn't shut down the
> device--I chickened out and plugged it back in. Following the advice
> from usbhid-ups(8), I ran `upsmon -c fsd` which properly brought
> the system down but did not power cycle the UPS.
>
> I am a little unclear on what actually causes NUT to issue the
> shutdown command. I've read something about the "low power flag:"
> is that something that the UPS decides on?

Indeed, the UPS sends a specific flag ( LB == low battery ) when it 
believes that the battery is depleted below a specific level. How nut 
behaves depends on the actual configuration, as a few other variables 
are also taken into account.


>
> Have I made a configuration error?

yes, I think that you did a small error. see below


> Do I need to set some configuration
> on the UPS with `upsrw` or something? Do I need to use Tripp Lite's
> Windows software to configure something before using it with NUT?
> Is this a new version of the AVR750U that's not compatible yet with
> NUT?

no, no and no.


>
> Thank you for your attention to my questions,
> Scott
>
>
> # cat nut.conf
> MODE=none

According to the documentation included in the nut.conf file ( at least 
in linux.. ), you should change this line to

      MODE=standalone

because "none" means nut is not yet configured and prohibits it from 
even starting . You can of course use "netserver" instead if you plan to 
power down more servers that will talk with the one which is actually 
connected to the UPS. Do not forget to start the services after 
modifying the config file

Here is a quote from the content of that file from a linux box:

# The values of MODE can be:
# - none: NUT is not configured, or use the Integrated Power Management, 
or use
#   some external system to startup NUT components. So nothing is to be 
started.
# - standalone: This mode address a local only configuration, with 1 UPS
#   protecting the local system. This implies to start the 3 NUT layers 
(driver,
#   upsd and upsmon) and the matching configuration files. This mode can 
also
#   address UPS redundancy.
# - netserver: same as for the standalone configuration, but also need
#   some more network access controls (firewall, tcp-wrappers) and 
possibly a
#   specific LISTEN directive in upsd.conf.
#   Since this MODE is opened to the network, a special care should be 
applied
#   to security concerns.
# - netclient: this mode only requires upsmon



>
> # cat ups.conf
> [AVR750U]
> driver=usbhid-ups
> port=auto
> productid=3024
>
> # cat upsmon.conf
> MONITOR AVR750U 1 local-monitor <password> master
> SHUTDOWNCMD "/sbin/shutdown -p +0"
> POWERDOWNFLAG /etc/killpower
> NOTIFYCMD /usr/local/pkg/nut/nut_email.php
> NOTIFYFLAG ONLINE   SYSLOG+WALL+EXEC
> NOTIFYFLAG ONBATT   SYSLOG+WALL+EXEC
> NOTIFYFLAG LOWBATT  SYSLOG+WALL+EXEC
> NOTIFYFLAG FSD    SYSLOG+WALL+EXEC
> NOTIFYFLAG COMMOK   SYSLOG+WALL+EXEC
> NOTIFYFLAG COMMBAD  SYSLOG+WALL+EXEC
> NOTIFYFLAG SHUTDOWN SYSLOG+WALL+EXEC
> NOTIFYFLAG REPLBATT SYSLOG+WALL+EXEC
> NOTIFYFLAG NOCOMM   SYSLOG+WALL+EXEC
> NOTIFYFLAG NOPARENT SYSLOG+WALL+EXEC
>
> # upsc AVR750U
> battery.charge: 100
> battery.charge.warning: 30
> battery.runtime: 3649
> battery.type: PbAc
> battery.voltage: 0.0
> battery.voltage.nominal: 12.0
> device.mfr: Tripp Lite
> device.model: AVR750U
> device.serial: 2945CVLOM87C901526
> device.type: ups
> driver.name: usbhid-ups
> driver.parameter.pollfreq: 30
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.parameter.productid: 3024
> driver.parameter.synchronous: no
> driver.version: 2.7.4
> driver.version.data: TrippLite HID 0.82
> driver.version.internal: 0.41
> input.frequency: 5990.0

This value is definitely incorrectly reported. Based on the voltages 
below I assume you are in USA and the displayed value could be an 
incorrectly scaled 59.9 Hz



> input.transfer.high: 145.0
> input.transfer.low: 89.0
> input.voltage: 0.0
> input.voltage.nominal: 120
> output.current: 0.0
> output.frequency: 5990.0

As above, I guess this should actually be 59.9 Hz


> output.frequency.nominal: 60
> output.voltage: 0.0
> output.voltage.nominal: 120
> ups.beeper.status: muted
> ups.delay.shutdown: 20
> ups.delay.start: 30
> ups.load: 0
> ups.mfr: Tripp Lite
> ups.model: AVR750U
> ups.power: 0.0
> ups.power.nominal: 750
> ups.productid: 3024
> ups.serial: 2945CVLOM87C901526
> ups.status: OL
> ups.timer.reboot: 65535
> ups.timer.shutdown: 65535
> ups.timer.start: 65535
> ups.vendorid: 09ae
> ups.watchdog.status: 0
>
> # /usr/local/libexec/nut/usbhid-ups -DD -a AVR750U
> Network UPS Tools - Generic HID driver 0.41 (2.7.4)
> USB communication driver 0.33
>     0.000000     debug level is '2'
>     0.001637     upsdrv_initups...
>     0.002374     Checking device (09AE/3024) (/dev/usb//dev/ugen1.2)
>     0.014968     - VendorID: 09ae
>     0.015020     - ProductID: 3024
>     0.015031     - Manufacturer: Tripp Lite
>     0.015041     - Product: AVR750U
>     0.015052     - Serial Number: 2945CVLOM87C901526
>     0.015061     - Bus: /dev/usb
>     0.015071     - Device release number: 0002
>     0.015084     Trying to match device
>     0.015265     Device matches
>     0.016003     HID descriptor length 885
>     0.020119     Report Descriptor size = 885
>     0.021057     Using subdriver: TrippLite HID 0.82
>     0.021116     87 HID objects found
>     0.022059     Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x28, Offset: 0, Size: 8, Value: 1
>     0.023013     Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 5
>     0.024007     Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: 0x2b, Offset: 0, Size: 8, Value: 3
>     0.025006     Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 120
>     0.025997     Path: UPS.PowerSummary.Input.Voltage, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 0.001233
>     0.027006     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 3
>     0.027995     Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
>     0.028034     Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
>     0.028059     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
>     0.028084     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
>     0.028138     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x32, Offset: 16, Size: 1, Value: 1
>     0.028164     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 16, Size: 1, Value: 1
>     0.028188     Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x32, Offset: 18, Size: 1, Value: 0
>     0.028212     Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
>     0.028237     Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x32, Offset: 20, Size: 1, Value: 0
>     0.028262     Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
>     0.028286     Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
>     0.028310     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
>     0.028333     Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 18, Size: 1, Value: 0
>     0.028357     Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
>     0.028383     Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 20, Size: 1, Value: 0
>     0.028407     Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
>     0.028430     Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
>     0.028454     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
>     0.029017     Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x2a, Offset: 0, Size: 8, Value: 4
>     0.030035     Path: UPS.PowerSummary.iOEMInformation, Type: Feature, ReportID: 0x62, Offset: 0, Size: 8, Value: 2
>     0.030999     Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x33, Offset: 0, Size: 8, Value: 2
>     0.031992     Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x34, Offset: 0, Size: 8, Value: 100
>     0.032029     Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x34, Offset: 0, Size: 8, Value: 100
>     0.033026     Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, ReportID: 0x37, Offset: 0, Size: 8, Value: 100
>     0.034014     Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 0x36, Offset: 0, Size: 8, Value: 100
>     0.035013     Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, ReportID: 0x38, Offset: 0, Size: 8, Value: 30
>     0.035995     Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID: 0x2c, Offset: 0, Size: 8, Value: 1
>     0.037002     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x35, Offset: 0, Size: 16, Value: 3650
>     0.037045     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x35, Offset: 0, Size: 16, Value: 3650
>     0.038032     Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature, ReportID: 0x04, Offset: 0, Size: 16, Value: 12
>     0.038999     Path: UPS.BatterySystem.Battery.Voltage, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 0.000137
>     0.040012     Path: UPS.BatterySystem.Battery.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x23, Offset: 2, Size: 1, Value: 0
>     0.040243     Path: UPS.BatterySystem.Battery.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x23, Offset: 3, Size: 1, Value: 1
>     0.040273     Path: UPS.BatterySystem.Battery.PresentStatus.Charging, Type: Feature, ReportID: 0x23, Offset: 4, Size: 1, Value: 0
>     0.040298     Path: UPS.BatterySystem.Battery.PresentStatus.Discharging, Type: Feature, ReportID: 0x23, Offset: 5, Size: 1, Value: 0
>     0.040321     Path: UPS.BatterySystem.Battery.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x23, Offset: 6, Size: 1, Value: 0
>     0.040345     Path: UPS.BatterySystem.Battery.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x23, Offset: 7, Size: 1, Value: 0
>     0.041012     Path: UPS.BatterySystem.Battery.RemainingCapacity, Type: Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 100
>     0.042012     Path: UPS.BatterySystem.Battery.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 6
>     0.043020     Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 120
>     0.044002     Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 60
>     0.045016     Path: UPS.Flow.ffff0097, Type: Feature, ReportID: 0x55, Offset: 0, Size: 8, Value: 2
>     0.046012     Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID: 0x03, Offset: 0, Size: 16, Value: 750
>     0.047000     Path: UPS.PowerConverter.Input.Voltage, Type: Feature, ReportID: 0x18, Offset: 0, Size: 16, Value: 0.001233
>     0.048042     Path: UPS.PowerConverter.Input.Frequency, Type: Feature, ReportID: 0x19, Offset: 0, Size: 16, Value: 5990

So the UPS reports a frequency which nut should scale ...




>     0.049011     Path: UPS.PowerConverter.Output.Voltage, Type: Feature, ReportID: 0x1b, Offset: 0, Size: 16, Value: 0.001233
>     0.050013     Path: UPS.PowerConverter.Output.Frequency, Type: Feature, ReportID: 0x1c, Offset: 0, Size: 16, Value: 5990

Again , scaling error...



>     0.050996     Path: UPS.PowerConverter.Output.Current, Type: Feature, ReportID: 0x46, Offset: 0, Size: 16, Value: 0
> [...]
>     0.083217     Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 120
>     0.083281     Path: UPS.PowerSummary.Input.Voltage, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 0.001233
>     0.083375     Path: UPS.PowerConverter.Input.Frequency, Type: Feature, ReportID: 0x19, Offset: 0, Size: 16, Value: 5990

and again...


>     0.083451     Path: UPS.PowerConverter.Output.LowVoltageTransfer, Type: Feature, ReportID: 0x06, Offset: 0, Size: 16, Value: 89
>     0.083579     Path: UPS.PowerConverter.Output.HighVoltageTransfer, Type: Feature, ReportID: 0x09, Offset: 0, Size: 16, Value: 145
>     0.083698     Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 120
>     0.083761     Path: UPS.PowerConverter.Output.Voltage, Type: Feature, ReportID: 0x1b, Offset: 0, Size: 16, Value: 0.001233
>     0.083847     Path: UPS.PowerConverter.Output.Current, Type: Feature, ReportID: 0x46, Offset: 0, Size: 16, Value: 0
>     0.083909     Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 60
>     0.084153     Path: UPS.PowerConverter.Output.Frequency, Type: Feature, ReportID: 0x1c, Offset: 0, Size: 16, Value: 5990

and again


     wolfy