[Nut-upsuser] AVR750U Low Power not Triggering Shutdown
Scott Colby
scott at scolby.com
Sun Jun 28 03:54:03 BST 2020
Thanks for the quick response!
On Sat, Jun 27, 2020, at 22:17, Manuel Wolfshant wrote:
> On 6/28/20 4:25 AM, Scott Colby wrote:
> > Hello,
> >
> > I am having difficulty using NUT to shut down my Netgate SG-1100
> > (a pfSense router) when the power level of the UPS gets critically
> > low.
> >
> > Here is some relevant information:
> > - OS: pfSense 2.4.5-RELEASE-p1 (FreeBSD 11.3-STABLE)
> > - NUT version: 2.7.4
> > - Installed from: pfSense package 2.7.4_7
> > - UPS: AVR750U (Device release number 2)
> > - I have included my config files, output from `upsc`, and output
> > from running the driver in debug mode at the bottom of this message.
> >
> > To get this UPS to work with NUT, I had to create a custom devd
> > rule:
> > # cat /usr/local/etc/devd/nut-usb-custom.conf
> > notify 100 {
> > match "system" "USB";
> > match "subsystem" "DEVICE";
> > match "type" "ATTACH";
> > match "vendor" "0x09ae";
> > match "product" "0x3024"; # difference from default config here
> > action "chgrp uucp /dev/$cdev; chmod g+rw /dev/$cdev";
> > };
> > It seems like my particular AVR750U has a different product id than
> > the one that came in the package at /usr/local/etc/nut-usb.conf,
> > which has a similar rule entry but with product id 0x1007. I'm not
> > sure if this is a package maintainer issue or a NUT isue.
>
> Manufacturers change product IDs over time. Both nut as product and the
> various packages shipped by unix distributions need to adjust according
> to those changes
>
>
>
> >
> > I unplugged the UPS from the mains power and let it run down. The
> > battery level and time remaining numbers seemed to update correctly
> > during this, but when the battery got down to 1% and showed less
> > than one minute of time remaining, NUT still hadn't shut down the
> > device--I chickened out and plugged it back in. Following the advice
> > from usbhid-ups(8), I ran `upsmon -c fsd` which properly brought
> > the system down but did not power cycle the UPS.
> >
> > I am a little unclear on what actually causes NUT to issue the
> > shutdown command. I've read something about the "low power flag:"
> > is that something that the UPS decides on?
>
> Indeed, the UPS sends a specific flag ( LB == low battery ) when it
> believes that the battery is depleted below a specific level. How nut
> behaves depends on the actual configuration, as a few other variables
> are also taken into account.
>
>
> >
> > Have I made a configuration error?
>
> yes, I think that you did a small error. see below
>
>
> > Do I need to set some configuration
> > on the UPS with `upsrw` or something? Do I need to use Tripp Lite's
> > Windows software to configure something before using it with NUT?
> > Is this a new version of the AVR750U that's not compatible yet with
> > NUT?
>
> no, no and no.
>
>
> >
> > Thank you for your attention to my questions,
> > Scott
> >
> >
> > # cat nut.conf
> > MODE=none
>
> According to the documentation included in the nut.conf file ( at least
> in linux.. ), you should change this line to
>
> MODE=standalone
>
> because "none" means nut is not yet configured and prohibits it from
> even starting . You can of course use "netserver" instead if you plan to
> power down more servers that will talk with the one which is actually
> connected to the UPS. Do not forget to start the services after
> modifying the config file
>
> Here is a quote from the content of that file from a linux box:
>
> # The values of MODE can be:
> # - none: NUT is not configured, or use the Integrated Power Management,
> or use
> # some external system to startup NUT components. So nothing is to be
> started.
> # - standalone: This mode address a local only configuration, with 1 UPS
> # protecting the local system. This implies to start the 3 NUT layers
> (driver,
> # upsd and upsmon) and the matching configuration files. This mode can
> also
> # address UPS redundancy.
> # - netserver: same as for the standalone configuration, but also need
> # some more network access controls (firewall, tcp-wrappers) and
> possibly a
> # specific LISTEN directive in upsd.conf.
> # Since this MODE is opened to the network, a special care should be
> applied
> # to security concerns.
> # - netclient: this mode only requires upsmon
>
>
I'm not convinced this is the problem; I think that pfSense has
an alternative way of running the NUT components:
# ps aux | grep ups
root 45456 0.0 0.1 6796 884 - Is 02:22 0:00.01 /usr/local/sbin/upsmon
uucp 45751 0.0 0.1 6796 772 - S 02:22 0:00.10 /usr/local/sbin/upsmon
uucp 46796 0.0 0.1 6888 888 - Ss 02:22 0:00.45 /usr/local/libexec/nut/usbhid-ups -a AVR750U
root 56752 0.0 0.1 6788 832 - Ss 02:22 0:00.13 /usr/local/sbin/upsd -u root
root 39437 0.0 0.2 6828 2464 0 S+ 02:46 0:00.01 grep ups
Is there anything else that should be running?
Would you expect `upsmon -c fsd` to not work as I described above
(system halting but UPS not power cycling) if MODE was set to none
but upsmon, the driver, and upsd were running?
>
> >
> > # cat ups.conf
> > [AVR750U]
> > driver=usbhid-ups
> > port=auto
> > productid=3024
> >
> > # cat upsmon.conf
> > MONITOR AVR750U 1 local-monitor <password> master
> > SHUTDOWNCMD "/sbin/shutdown -p +0"
> > POWERDOWNFLAG /etc/killpower
> > NOTIFYCMD /usr/local/pkg/nut/nut_email.php
> > NOTIFYFLAG ONLINE SYSLOG+WALL+EXEC
> > NOTIFYFLAG ONBATT SYSLOG+WALL+EXEC
> > NOTIFYFLAG LOWBATT SYSLOG+WALL+EXEC
> > NOTIFYFLAG FSD SYSLOG+WALL+EXEC
> > NOTIFYFLAG COMMOK SYSLOG+WALL+EXEC
> > NOTIFYFLAG COMMBAD SYSLOG+WALL+EXEC
> > NOTIFYFLAG SHUTDOWN SYSLOG+WALL+EXEC
> > NOTIFYFLAG REPLBATT SYSLOG+WALL+EXEC
> > NOTIFYFLAG NOCOMM SYSLOG+WALL+EXEC
> > NOTIFYFLAG NOPARENT SYSLOG+WALL+EXEC
> >
> > # upsc AVR750U
> > battery.charge: 100
> > battery.charge.warning: 30
> > battery.runtime: 3649
> > battery.type: PbAc
> > battery.voltage: 0.0
> > battery.voltage.nominal: 12.0
> > device.mfr: Tripp Lite
> > device.model: AVR750U
> > device.serial: 2945CVLOM87C901526
> > device.type: ups
> > driver.name: usbhid-ups
> > driver.parameter.pollfreq: 30
> > driver.parameter.pollinterval: 2
> > driver.parameter.port: auto
> > driver.parameter.productid: 3024
> > driver.parameter.synchronous: no
> > driver.version: 2.7.4
> > driver.version.data: TrippLite HID 0.82
> > driver.version.internal: 0.41
> > input.frequency: 5990.0
>
> This value is definitely incorrectly reported. Based on the voltages
> below I assume you are in USA and the displayed value could be an
> incorrectly scaled 59.9 Hz
>
>
You are correct about my location and expected voltage. Is there
somewhere that I can change the scaling factor used by NUT?
>
> > input.transfer.high: 145.0
> > input.transfer.low: 89.0
> > input.voltage: 0.0
> > input.voltage.nominal: 120
> > output.current: 0.0
> > output.frequency: 5990.0
>
> As above, I guess this should actually be 59.9 Hz
>
>
> > output.frequency.nominal: 60
> > output.voltage: 0.0
> > output.voltage.nominal: 120
> > ups.beeper.status: muted
> > ups.delay.shutdown: 20
> > ups.delay.start: 30
> > ups.load: 0
> > ups.mfr: Tripp Lite
> > ups.model: AVR750U
> > ups.power: 0.0
> > ups.power.nominal: 750
> > ups.productid: 3024
> > ups.serial: 2945CVLOM87C901526
> > ups.status: OL
> > ups.timer.reboot: 65535
> > ups.timer.shutdown: 65535
> > ups.timer.start: 65535
> > ups.vendorid: 09ae
> > ups.watchdog.status: 0
> >
> > # /usr/local/libexec/nut/usbhid-ups -DD -a AVR750U
> > Network UPS Tools - Generic HID driver 0.41 (2.7.4)
> > USB communication driver 0.33
> > 0.000000 debug level is '2'
> > 0.001637 upsdrv_initups...
> > 0.002374 Checking device (09AE/3024) (/dev/usb//dev/ugen1.2)
> > 0.014968 - VendorID: 09ae
> > 0.015020 - ProductID: 3024
> > 0.015031 - Manufacturer: Tripp Lite
> > 0.015041 - Product: AVR750U
> > 0.015052 - Serial Number: 2945CVLOM87C901526
> > 0.015061 - Bus: /dev/usb
> > 0.015071 - Device release number: 0002
> > 0.015084 Trying to match device
> > 0.015265 Device matches
> > 0.016003 HID descriptor length 885
> > 0.020119 Report Descriptor size = 885
> > 0.021057 Using subdriver: TrippLite HID 0.82
> > 0.021116 87 HID objects found
> > 0.022059 Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x28, Offset: 0, Size: 8, Value: 1
> > 0.023013 Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 5
> > 0.024007 Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: 0x2b, Offset: 0, Size: 8, Value: 3
> > 0.025006 Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 120
> > 0.025997 Path: UPS.PowerSummary.Input.Voltage, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 0.001233
> > 0.027006 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 3
> > 0.027995 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
> > 0.028034 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
> > 0.028059 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
> > 0.028084 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
> > 0.028138 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x32, Offset: 16, Size: 1, Value: 1
> > 0.028164 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 16, Size: 1, Value: 1
> > 0.028188 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x32, Offset: 18, Size: 1, Value: 0
> > 0.028212 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
> > 0.028237 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x32, Offset: 20, Size: 1, Value: 0
> > 0.028262 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
> > 0.028286 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
> > 0.028310 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
> > 0.028333 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 18, Size: 1, Value: 0
> > 0.028357 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
> > 0.028383 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 20, Size: 1, Value: 0
> > 0.028407 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
> > 0.028430 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
> > 0.028454 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
> > 0.029017 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x2a, Offset: 0, Size: 8, Value: 4
> > 0.030035 Path: UPS.PowerSummary.iOEMInformation, Type: Feature, ReportID: 0x62, Offset: 0, Size: 8, Value: 2
> > 0.030999 Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x33, Offset: 0, Size: 8, Value: 2
> > 0.031992 Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x34, Offset: 0, Size: 8, Value: 100
> > 0.032029 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x34, Offset: 0, Size: 8, Value: 100
> > 0.033026 Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, ReportID: 0x37, Offset: 0, Size: 8, Value: 100
> > 0.034014 Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 0x36, Offset: 0, Size: 8, Value: 100
> > 0.035013 Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, ReportID: 0x38, Offset: 0, Size: 8, Value: 30
> > 0.035995 Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID: 0x2c, Offset: 0, Size: 8, Value: 1
> > 0.037002 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x35, Offset: 0, Size: 16, Value: 3650
> > 0.037045 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x35, Offset: 0, Size: 16, Value: 3650
> > 0.038032 Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature, ReportID: 0x04, Offset: 0, Size: 16, Value: 12
> > 0.038999 Path: UPS.BatterySystem.Battery.Voltage, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 0.000137
> > 0.040012 Path: UPS.BatterySystem.Battery.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x23, Offset: 2, Size: 1, Value: 0
> > 0.040243 Path: UPS.BatterySystem.Battery.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x23, Offset: 3, Size: 1, Value: 1
> > 0.040273 Path: UPS.BatterySystem.Battery.PresentStatus.Charging, Type: Feature, ReportID: 0x23, Offset: 4, Size: 1, Value: 0
> > 0.040298 Path: UPS.BatterySystem.Battery.PresentStatus.Discharging, Type: Feature, ReportID: 0x23, Offset: 5, Size: 1, Value: 0
> > 0.040321 Path: UPS.BatterySystem.Battery.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x23, Offset: 6, Size: 1, Value: 0
> > 0.040345 Path: UPS.BatterySystem.Battery.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x23, Offset: 7, Size: 1, Value: 0
> > 0.041012 Path: UPS.BatterySystem.Battery.RemainingCapacity, Type: Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 100
> > 0.042012 Path: UPS.BatterySystem.Battery.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 6
> > 0.043020 Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 120
> > 0.044002 Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 60
> > 0.045016 Path: UPS.Flow.ffff0097, Type: Feature, ReportID: 0x55, Offset: 0, Size: 8, Value: 2
> > 0.046012 Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID: 0x03, Offset: 0, Size: 16, Value: 750
> > 0.047000 Path: UPS.PowerConverter.Input.Voltage, Type: Feature, ReportID: 0x18, Offset: 0, Size: 16, Value: 0.001233
> > 0.048042 Path: UPS.PowerConverter.Input.Frequency, Type: Feature, ReportID: 0x19, Offset: 0, Size: 16, Value: 5990
>
> So the UPS reports a frequency which nut should scale ...
>
>
>
>
> > 0.049011 Path: UPS.PowerConverter.Output.Voltage, Type: Feature, ReportID: 0x1b, Offset: 0, Size: 16, Value: 0.001233
> > 0.050013 Path: UPS.PowerConverter.Output.Frequency, Type: Feature, ReportID: 0x1c, Offset: 0, Size: 16, Value: 5990
>
> Again , scaling error...
>
>
>
> > 0.050996 Path: UPS.PowerConverter.Output.Current, Type: Feature, ReportID: 0x46, Offset: 0, Size: 16, Value: 0
> > [...]
> > 0.083217 Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 120
> > 0.083281 Path: UPS.PowerSummary.Input.Voltage, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 0.001233
> > 0.083375 Path: UPS.PowerConverter.Input.Frequency, Type: Feature, ReportID: 0x19, Offset: 0, Size: 16, Value: 5990
>
> and again...
>
>
> > 0.083451 Path: UPS.PowerConverter.Output.LowVoltageTransfer, Type: Feature, ReportID: 0x06, Offset: 0, Size: 16, Value: 89
> > 0.083579 Path: UPS.PowerConverter.Output.HighVoltageTransfer, Type: Feature, ReportID: 0x09, Offset: 0, Size: 16, Value: 145
> > 0.083698 Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 120
> > 0.083761 Path: UPS.PowerConverter.Output.Voltage, Type: Feature, ReportID: 0x1b, Offset: 0, Size: 16, Value: 0.001233
> > 0.083847 Path: UPS.PowerConverter.Output.Current, Type: Feature, ReportID: 0x46, Offset: 0, Size: 16, Value: 0
> > 0.083909 Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 60
> > 0.084153 Path: UPS.PowerConverter.Output.Frequency, Type: Feature, ReportID: 0x1c, Offset: 0, Size: 16, Value: 5990
>
> and again
>
>
> wolfy
>
>
>
Thanks,
Scott