[Nut-upsuser] [POSSIBLE FRAUD] Re: [EXTERNAL] Re: Help with Tripp Lite Internet600U
David Zomaya
David_Zomaya at tripplite.com
Thu May 21 01:03:06 BST 2020
No, it's not.
I'd defer to the list for tips on that one.
First thing I'd try if no one else has ideas is checking lsusb and restarting the service.
Thank you,
David Zomaya
Tripp Lite<http://www.tripplite.com/>
________________________________
From: Tom Cooper <tom at cooperfamily.xyz>
Sent: Wednesday, May 20, 2020 7:00 PM
To: David Zomaya
Cc: nut-upsuser
Subject: Re: [POSSIBLE FRAUD] Re: [Nut-upsuser] [EXTERNAL] Re: Help with Tripp Lite Internet600U
I'm not seeing this in the log. I'm guessing that's not great.
May 20 19:57:28 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:57:33 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:57:38 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:57:43 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:57:48 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:57:53 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:57:58 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:58:03 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:58:08 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:58:13 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:58:18 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:58:23 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:58:28 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:58:33 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:58:38 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:58:43 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:58:48 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:58:53 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:58:58 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
May 20 19:59:03 elmer upsmon[3828]: Poll UPS [tripplite at localhost] failed - Data stale
---- On Wed, 20 May 2020 19:49:27 -0400 David Zomaya <David_Zomaya at tripplite.com> wrote ----
Glad to hear it's working, thanks Tom.
Network UPS Tools team: is fixing this as simple as me telling you what new UPS protocols are HID-PDC compliant?
Thank you,
David Zomaya
Tripp Lite<http://www.tripplite.com/>
________________________________
From: Tom Cooper <tom at cooperfamily.xyz<mailto:tom at cooperfamily.xyz>>
Sent: Wednesday, May 20, 2020 2:42 PM
To: David Zomaya
Cc: nut-upsuser
Subject: Re: [POSSIBLE FRAUD] Re: [Nut-upsuser] [EXTERNAL] Re: Help with Tripp Lite Internet600U
The fix:
Was following a howto here: https://raymondjdouglas.com/blog/2018/ups-monitoring/<https://urldefense.proofpoint.com/v2/url?u=https-3A__raymondjdouglas.com_blog_2018_ups-2Dmonitoring_&d=DwMFaQ&c=f9s1WCuF-N6cmD_YaZ7gBg&r=lhr3k4au5dVQgHY_iS-v_t9g8PHVkn8Px_wyaupZGfQ&m=xxqnPehnxbPZyMn7Y4l3qE4tQqpQ88lYY6CCnQ2qVrU&s=nbzYFun_NHdb-5EB7VMlWNFsqwWbA2-VLKNlBKWFVUQ&e=>
Much thanks to David Zomaya for coming up with the recipe!
Nut.conf:
*
Just have
MODE=standalone
UPS.conf
*
[tripplite]
driver = usbhid-ups
port = auto
productid=3024
desc = "Tripp Lite Internet600U"
upsd.conf
*
LISTEN 127.0.0.1 3493
LISTEN ::1 3493
[tripplite]
driver = usbhid-ups
port = auto
Create a new udev ruleset:
cat /etc/udev/rules.d/90-nut-ups.rules
Put this rule in place
# /etc/udev/rules.d/90-nut-ups.rules
ACTION=="add", \
SUBSYSTEM=="usb", \
ATTR{idVendor}=="09ae", ATTR{idProduct}=="3024", \
MODE="0660", GROUP="nut"
Reload the udev rules
udevadm control --reload-rules && udevadm trigger
(and maybe unplug/replug the UPS)
Then
sudo systemctl start nut-driver
Loads the driver, and following the rest of the steps ih the howto I see this output from upsc
pi at elmer:/home/macbackup $ upsc tripplite
Init SSL without certificate database
battery.charge: 100
battery.charge.warning: 30
battery.runtime: 1753
battery.type: PbAC
battery.voltage: 0.0
battery.voltage.nominal: 12.0
device.mfr: Tripp Lite
device.model: INTERNET600U
device.serial: 2922BVLBC87B601706
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.productid: 3024
driver.parameter.synchronous: no
driver.version: 2.7.4
driver.version.data: TrippLite HID 0.82
driver.version.internal: 0.41
input.frequency: 6020.0
input.transfer.high: 145.0
input.transfer.low: 95.0
input.voltage: 0.0
input.voltage.nominal: 120
output.current: 50.0
output.frequency: 6020.0
output.frequency.nominal: 60
output.voltage: 0.0
output.voltage.nominal: 120
ups.beeper.status: muted
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 11
ups.mfr: Tripp Lite
ups.model: INTERNET600U
ups.power: 37.0
ups.power.nominal: 600
ups.productid: 3024
ups.serial: 2922BVLBC87B601706
ups.status: OL
ups.timer.reboot: 65535
ups.timer.shutdown: 65535
ups.timer.start: 65535
ups.vendorid: 09ae
ups.watchdog.status: 0
---- On Wed, 20 May 2020 14:56:14 -0400 David Zomaya <David_Zomaya at tripplite.com<mailto:David_Zomaya at tripplite.com>> wrote ----
________________________________
This message is for the addressee's use only. It may contain confidential information. If you receive this message in error, please delete it and notify the sender. Tripp Lite disclaims all warranties and liabilities, and assumes no responsibility for viruses which may infect an email sent to you from Tripp Lite and which damage your electronic systems or information. It is your responsibility to maintain virus detection systems to prevent damage to your electronic systems and information.
"Can't claim USB device [09ae:3024]: could not detach kernel driver from interface 0: Operation not permitted"
Is probably an issue with NUT grabbing the UPS... can you disconnect and reconnect the USB cable and try again?
If that fails, maybe a udev rule will help.
Thank you,
David Zomaya
Tripp Lite
<http://www.tripplite.com/>
________________________________
From: Tom Cooper <tom at cooperfamily.xyz<mailto:tom at cooperfamily.xyz>>
Sent: Wednesday, May 20, 2020 1:54:20 PM
To: David Zomaya
Cc: nut-upsuser
Subject: Re: [POSSIBLE FRAUD] Re: [Nut-upsuser] [EXTERNAL] Re: Help with Tripp Lite Internet600U
David,
I appreciate the quick feedback!
If I didn't fat finger any of the parameters you sent me, it's still not working.
Here's the output from the attempt to start. (BTW - nothing appears in the daemon.log when I use the upsdrvctl command.)
pi at elmer:/home/macbackup $ sudo vi /etc/nut/nut.conf
pi at elmer:/home/macbackup $ sudo vi /etc/nut/ups.conf
pi at elmer:/home/macbackup $ sudo vi /etc/nut/upsd.conf
pi at elmer:/home/macbackup $ sudo upsdrvctl start
Network UPS Tools - UPS driver controller 2.7.4
Network UPS Tools - Generic HID driver 0.41 (2.7.4)
USB communication driver 0.33
Can't claim USB device [09ae:3024]: could not detach kernel driver from interface 0: Operation not permitted
Driver failed to start (exit status=1)
Network UPS Tools - Generic HID driver 0.41 (2.7.4)
USB communication driver 0.33
Can't claim USB device [09ae:3024]: could not detach kernel driver from interface 0: Operation not permitted
Driver failed to start (exit status=1)
Network UPS Tools - Generic HID driver 0.41 (2.7.4)
USB communication driver 0.33
Can't claim USB device [09ae:3024]: could not detach kernel driver from interface 0: Operation not permitted
Driver failed to start (exit status=1)
---- On Wed, 20 May 2020 14:03:09 -0400 David Zomaya <David_Zomaya at tripplite.com<mailto:David_Zomaya at tripplite.com>> wrote ----
My thoughts for a test:
* Just have
MODE=standalone
in nut.conf
* Put
[tripplite]
driver = usbhid-ups
port = auto
productid=3024
desc = "Tripp Lite Internet600U"
In ups.conf
* Put
LISTEN 127.0.0.1 3493
LISTEN ::1 3493
[tripplite]
driver = usbhid-ups
port = auto
in upsd.conf
That may be suboptimal but will probably work for a test.
Side note: I use "upsdrvctl start/stop" to start and stop the driver.
Thank you,
David Zomaya
Tripp Lite
________________________________
From: Tom Cooper <tom at cooperfamily.xyz<mailto:tom at cooperfamily.xyz>>
Sent: Wednesday, May 20, 2020 12:55 PM
To: David Zomaya
Cc: nut-upsuser
Subject: Re: [POSSIBLE FRAUD] Re: [Nut-upsuser] [EXTERNAL] Re: Help with Tripp Lite Internet600U
David,
That's exciting - but I am not seeing similar results.
I *must* be doing something dumb - but I can't see it.
I've got nut-2.7.4-8 installed on my pi
Hope you can help.
Tom
pi at elmer:/home/macbackup $ lsusb | grep ipp
Bus 001 Device 004: ID 09ae:3024 Tripp Lite
pi at elmer:/home/macbackup $ sudo cat /etc/nut/nut.conf
# Network UPS Tools: example nut.conf
#
##############################################################################
# General section
##############################################################################
# The MODE determines which part of the NUT is to be started, and which
# configuration files must be modified.
#
# This file try to standardize the various files being found in the field, like
# /etc/default/nut on Debian based systems, /etc/sysconfig/ups on RedHat based
# systems, ... Distribution's init script should source this file to see which
# component(s) has to be started.
#
# The values of MODE can be:
# - none: NUT is not configured, or use the Integrated Power Management, or use
# some external system to startup NUT components. So nothing is to be started.
# - standalone: This mode address a local only configuration, with 1 UPS
# protecting the local system. This implies to start the 3 NUT layers (driver,
# upsd and upsmon) and the matching configuration files. This mode can also
# address UPS redundancy.
# - netserver: same as for the standalone configuration, but also need
# some more network access controls (firewall, tcp-wrappers) and possibly a
# specific LISTEN directive in upsd.conf.
# Since this MODE is opened to the network, a special care should be applied
# to security concerns.
# - netclient: this mode only requires upsmon.
#
# IMPORTANT NOTE:
# This file is intended to be sourced by shell scripts.
# You MUST NOT use spaces around the equal sign!
MODE=none
[tripplite]
driver = usbhid-ups
port = auto
productid=3024
desc = "Tripp Lite Internet600U"
pi at elmer:/home/macbackup $ sudo systemctl start nut-driver
Job for nut-driver.service failed because the control process exited with error code.
See "systemctl status nut-driver.service" and "journalctl -xe" for details.
>From the log file:
May 20 13:51:47 elmer systemd[1]: Starting Network UPS Tools - power device driver controller...
May 20 13:51:47 elmer upsdrvctl[2658]: This TrippLite device (09ae:3024) is not (or perhaps not yet) supported
May 20 13:51:47 elmer upsdrvctl[2658]: by usbhid-ups. Please make sure you have an up-to-date version of NUT. If
May 20 13:51:47 elmer upsdrvctl[2658]: this does not fix the problem, try running the driver with the
May 20 13:51:47 elmer upsdrvctl[2658]: '-x productid=3024' option. Please report your results to the NUT user's
May 20 13:51:47 elmer upsdrvctl[2658]: mailing list <nut-upsuser at lists.alioth.debian.org<mailto:nut-upsuser at lists.alioth.debian.org>>.
May 20 13:51:47 elmer upsdrvctl[2658]: Network UPS Tools - Generic HID driver 0.41 (2.7.4)
May 20 13:51:47 elmer upsdrvctl[2658]: USB communication driver 0.33
May 20 13:51:47 elmer upsdrvctl[2658]: No matching HID UPS found
May 20 13:51:47 elmer upsdrvctl[2658]: Driver failed to start (exit status=1)
May 20 13:51:52 elmer upsdrvctl[2658]: This TrippLite device (09ae:3024) is not (or perhaps not yet) supported
May 20 13:51:52 elmer upsdrvctl[2658]: by usbhid-ups. Please make sure you have an up-to-date version of NUT. If
May 20 13:51:52 elmer upsdrvctl[2658]: this does not fix the problem, try running the driver with the
May 20 13:51:52 elmer upsdrvctl[2658]: '-x productid=3024' option. Please report your results to the NUT user's
May 20 13:51:52 elmer upsdrvctl[2658]: mailing list <nut-upsuser at lists.alioth.debian.org<mailto:nut-upsuser at lists.alioth.debian.org>>.
May 20 13:51:52 elmer upsdrvctl[2658]: Network UPS Tools - Generic HID driver 0.41 (2.7.4)
May 20 13:51:52 elmer upsdrvctl[2658]: USB communication driver 0.33
May 20 13:51:52 elmer upsdrvctl[2658]: No matching HID UPS found
May 20 13:51:52 elmer upsdrvctl[2658]: Driver failed to start (exit status=1)
May 20 13:51:58 elmer upsdrvctl[2658]: This TrippLite device (09ae:3024) is not (or perhaps not yet) supported
May 20 13:51:58 elmer upsdrvctl[2658]: by usbhid-ups. Please make sure you have an up-to-date version of NUT. If
May 20 13:51:58 elmer upsdrvctl[2658]: this does not fix the problem, try running the driver with the
May 20 13:51:58 elmer upsdrvctl[2658]: '-x productid=3024' option. Please report your results to the NUT user's
May 20 13:51:58 elmer upsdrvctl[2658]: mailing list <nut-upsuser at lists.alioth.debian.org<mailto:nut-upsuser at lists.alioth.debian.org>>.
May 20 13:51:58 elmer upsdrvctl[2658]: Network UPS Tools - Generic HID driver 0.41 (2.7.4)
May 20 13:51:58 elmer upsdrvctl[2658]: USB communication driver 0.33
May 20 13:51:58 elmer upsdrvctl[2658]: No matching HID UPS found
May 20 13:51:58 elmer systemd[1]: nut-driver.service: Control process exited, code=exited, status=1/FAILURE
May 20 13:51:58 elmer upsdrvctl[2658]: Driver failed to start (exit status=1)
May 20 13:51:58 elmer upsdrvctl[2658]: Network UPS Tools - UPS driver controller 2.7.4
May 20 13:51:58 elmer systemd[1]: nut-driver.service: Failed with result 'exit-code'.
May 20 13:51:58 elmer systemd[1]: Failed to start Network UPS Tools - power device driver controller.
---- On Wed, 20 May 2020 13:46:09 -0400 David Zomaya <David_Zomaya at tripplite.com<mailto:David_Zomaya at tripplite.com>> wrote ----
Tested a Ubuntu 18.04 LTS virtual machine with NUT 2.7.4 and a 3024 protocol Tripp Lite UPS (mine is a INTERNET550U, but same protocol)
:/etc/nut$ lsusb | grep Tripp
Bus 002 Device 004: ID 09ae:3024 Tripp Lite
I it got generally working (outputting reasonable responses to upsc, although there are some issues with variables like frequency) by adding productid=3024 to my ups.conf. Like this:
[TrippLiteUPS3024]
driver = usbhid-ups
port = auto
productid=3024
Here is the upsc output:
:/etc/nut$ sudo upsc TrippLiteUPS3024
Init SSL without certificate database
battery.charge: 100
battery.charge.warning: 30
battery.runtime: 1850
battery.type: PbAc
battery.voltage: 0.0
battery.voltage.nominal: 12.0
device.mfr: Tripp Lite
device.model: INTERNET550U
device.serial: 2951EVLBC87B503245
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.productid: 3024
driver.parameter.synchronous: no
driver.version: 2.7.4
driver.version.data: TrippLite HID 0.82
driver.version.internal: 0.41
input.frequency: 6010.0
input.transfer.high: 145.0
input.transfer.low: 95.0
input.voltage: 0.0
input.voltage.nominal: 120
output.current: 0.0
output.frequency: 6010.0
output.frequency.nominal: 60
output.voltage: 0.0
output.voltage.nominal: 120
ups.beeper.status: disabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 0
ups.mfr: Tripp Lite
ups.model: INTERNET550U
ups.power: 0.0
ups.power.nominal: 550
ups.productid: 3024
ups.serial: 2951EVLBC87B503245
ups.status: OL
ups.timer.reboot: 65535
ups.timer.shutdown: 65535
ups.timer.start: 65535
ups.vendorid: 09ae
ups.watchdog.status: 0
:/etc/nut$
Tom: Let me know if this helps you.
List in general: would this help solve general 3024 issues?
Thank you,
David Zomaya
Tripp Lite<http://www.tripplite.com/>
________________________________
From: Nut-upsuser <nut-upsuser-bounces+david_zomaya=tripplite.com at alioth-lists.debian.net<mailto:tripplite.com at alioth-lists.debian.net>> on behalf of David Zomaya
Sent: Wednesday, May 20, 2020 8:49 AM
To: Tom Cooper
Cc: nut-upsuser
Subject: [POSSIBLE FRAUD] Re: [Nut-upsuser] [EXTERNAL] Re: Help with Tripp Lite Internet600U
Will do. Ball in my court for now.
Thank you,
David Zomaya
Tripp Lite<http://www.tripplite.com/>
________________________________
From: Tom Cooper <tom at cooperfamily.xyz<mailto:tom at cooperfamily.xyz>>
Sent: Wednesday, May 20, 2020 8:47:28 AM
To: David Zomaya
Cc: nut-upsuser
Subject: Re: [EXTERNAL] Re: [Nut-upsuser] Help with Tripp Lite Internet600U
That would be great. If there is something I can do to collect data or troubleshoot, please let me know.
---- On Wed, 20 May 2020 08:51:14 -0400 David Zomaya <David_Zomaya at tripplite.com<mailto:David_Zomaya at tripplite.com>> wrote ----
I'm still working remotely, but I should be able to get something set up soon.
I'll reply all here once I have something to report.
Thank you,
David Zomaya
Tripp Lite<http://www.tripplite.com/>
________________________________
From: Tom Cooper <tom at cooperfamily.xyz<mailto:tom at cooperfamily.xyz>>
Sent: Wednesday, May 20, 2020 7:48:32 AM
To: David Zomaya
Cc: nut-upsuser
Subject: Re: [EXTERNAL] Re: [Nut-upsuser] Help with Tripp Lite Internet600U
I'm running Raspbian Buster, but given that the error seems to be "higher order" than a hardware issue - one of parsing the protocol? I suspect that Ubuntu would be a decent "lookalike" to model the issue.
---- On Tue, 19 May 2020 22:31:56 -0400 David Zomaya <David_Zomaya at tripplite.com<mailto:David_Zomaya at tripplite.com>> wrote ----
If I installed and tested against Ubuntu, how useful would that be in general and in this specific case?
I think we've seen a few reports of issues with the newer 3024 protocols and I'd like to help get them sorted out.
Thank you,
David Zomaya
Tripp Lite
________________________________
From: Nut-upsuser <nut-upsuser-bounces+david_zomaya=tripplite.com at alioth-lists.debian.net<mailto:tripplite.com at alioth-lists.debian.net>> on behalf of Charles Lepple <clepple at gmail.com<mailto:clepple at gmail.com>>
Sent: Tuesday, May 19, 2020 9:24 PM
To: Tom Cooper
Cc: nut-upsuser
Subject: [EXTERNAL] Re: [Nut-upsuser] Help with Tripp Lite Internet600U
This is an EXTERNAL email. Please take a moment and think before clicking any links or opening any attachments from this email. If suspicious, please forward to ishelpdesk at tripplite.com<mailto:ishelpdesk at tripplite.com> for review.
______________________________________________________________________
On May 19, 2020, at 9:21 PM, Tom Cooper <tom at cooperfamily.xyz<mailto:tom at cooperfamily.xyz>> wrote:
>
> Bus 001 Device 004: ID 09ae:3024 Tripp Lite
>
We have only had reports of success with protocol 2010 of INTERNET600U (which would be 09ae:2010 in lsusb).
More details: https://urldefense.proofpoint.com/v2/url?u=https-3A__alioth-2Dlists.debian.net_pipermail_nut-2Dupsuser_2020-2DApril_011803.html&d=DwIGaQ&c=f9s1WCuF-N6cmD_YaZ7gBg&r=lhr3k4au5dVQgHY_iS-v_t9g8PHVkn8Px_wyaupZGfQ&m=PY3fmIYRp20XyPJAWtuIoMta82maER1CGSdOB3x6HEM&s=9Ri1IbEOy_cyZZctw4a1IFxUMKAIwhu2xTRnjanyorI&e=
_______________________________________________
Nut-upsuser mailing list
Nut-upsuser at alioth-lists.debian.net<mailto:Nut-upsuser at alioth-lists.debian.net>
https://urldefense.proofpoint.com/v2/url?u=https-3A__alioth-2Dlists.debian.net_cgi-2Dbin_mailman_listinfo_nut-2Dupsuser&d=DwIGaQ&c=f9s1WCuF-N6cmD_YaZ7gBg&r=lhr3k4au5dVQgHY_iS-v_t9g8PHVkn8Px_wyaupZGfQ&m=PY3fmIYRp20XyPJAWtuIoMta82maER1CGSdOB3x6HEM&s=374XOzWi2asZji_KmGBZFGWtzgxtuHrjfrzcGP8Fsvw&e=
_______________________________________________
Nut-upsuser mailing list
Nut-upsuser at alioth-lists.debian.net<mailto:Nut-upsuser at alioth-lists.debian.net>
https://urldefense.proofpoint.com/v2/url?u=https-3A__alioth-2Dlists.debian.net_cgi-2Dbin_mailman_listinfo_nut-2Dupsuser&d=DwIGaQ&c=f9s1WCuF-N6cmD_YaZ7gBg&r=lhr3k4au5dVQgHY_iS-v_t9g8PHVkn8Px_wyaupZGfQ&m=PY3fmIYRp20XyPJAWtuIoMta82maER1CGSdOB3x6HEM&s=374XOzWi2asZji_KmGBZFGWtzgxtuHrjfrzcGP8Fsvw&e=
________________________________
This message is for the addressee's use only. It may contain confidential information. If you receive this message in error, please delete it and notify the sender. Tripp Lite disclaims all warranties and liabilities, and assumes no responsibility for viruses which may infect an email sent to you from Tripp Lite and which damage your electronic systems or information. It is your responsibility to maintain virus detection systems to prevent damage to your electronic systems and information.
________________________________
This message is for the addressee's use only. It may contain confidential information. If you receive this message in error, please delete it and notify the sender. Tripp Lite disclaims all warranties and liabilities, and assumes no responsibility for viruses which may infect an email sent to you from Tripp Lite and which damage your electronic systems or information. It is your responsibility to maintain virus detection systems to prevent damage to your electronic systems and information.
________________________________
This message is for the addressee's use only. It may contain confidential information. If you receive this message in error, please delete it and notify the sender. Tripp Lite disclaims all warranties and liabilities, and assumes no responsibility for viruses which may infect an email sent to you from Tripp Lite and which damage your electronic systems or information. It is your responsibility to maintain virus detection systems to prevent damage to your electronic systems and information.
________________________________
This message is for the addressee's use only. It may contain confidential information. If you receive this message in error, please delete it and notify the sender. Tripp Lite disclaims all warranties and liabilities, and assumes no responsibility for viruses which may infect an email sent to you from Tripp Lite and which damage your electronic systems or information. It is your responsibility to maintain virus detection systems to prevent damage to your electronic systems and information.
________________________________
This message is for the addressee's use only. It may contain confidential information. If you receive this message in error, please delete it and notify the sender. Tripp Lite disclaims all warranties and liabilities, and assumes no responsibility for viruses which may infect an email sent to you from Tripp Lite and which damage your electronic systems or information. It is your responsibility to maintain virus detection systems to prevent damage to your electronic systems and information.
________________________________
This message is for the addressee's use only. It may contain confidential information. If you receive this message in error, please delete it and notify the sender. Tripp Lite disclaims all warranties and liabilities, and assumes no responsibility for viruses which may infect an email sent to you from Tripp Lite and which damage your electronic systems or information. It is your responsibility to maintain virus detection systems to prevent damage to your electronic systems and information.
________________________________
This message is for the addressee's use only. It may contain confidential information. If you receive this message in error, please delete it and notify the sender. Tripp Lite disclaims all warranties and liabilities, and assumes no responsibility for viruses which may infect an email sent to you from Tripp Lite and which damage your electronic systems or information. It is your responsibility to maintain virus detection systems to prevent damage to your electronic systems and information.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20200521/8276e330/attachment-0001.html>
More information about the Nut-upsuser
mailing list