[Nut-upsuser] Can't get CyberPower UPS to work with Raspberry Pi 4

Robert Stocker kneadtoknow at gmail.com
Sun Oct 25 15:52:27 GMT 2020


This was very helpful for me, thank you!

On Sat, Oct 24, 2020 at 9:06 AM Charles Lepple <clepple at gmail.com> wrote:

> The easiest way to tell if upsd is working is to run "upsc -l" on the same
> system, which will list the NUT UPS names, and then run e.g. "upsc mge"
> (replacing "mge" with the name returned by "upsc -l")
>
Here was the output I got from the second command:

Init SSL without certificate database
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 15690
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 24.0
battery.voltage.nominal: 24
device.mfr: CPS
device.model: CST135XLU
device.serial: CR7EO2003120
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 5
driver.parameter.port: auto
driver.parameter.synchronous: no
driver.version: 2.7.4
driver.version.data: CyberPower HID 0.4
driver.version.internal: 0.41
input.voltage: 121.0
input.voltage.nominal: 120
output.voltage: 137.0
ups.beeper.status: disabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 4
ups.mfr: CPS
ups.model: CST135XLU
ups.productid: 0501
ups.realpower.nominal: 810
ups.serial: CR7EO2003120
ups.status: OL
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764


> If you run systemctl, you should see something like this:
>

And here's what I got from that:

 nut-driver.service       loaded active running   Network UPS Tools - power
device driver controller
 nut-monitor.service       loaded active running   Network UPS Tools -
power device monitor and shutdown controller
 nut-server.service       loaded active running   Network UPS Tools - power
devices information server
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20201025/96fb71de/attachment.html>


More information about the Nut-upsuser mailing list