[Nut-upsuser] [EXTERNAL] Tripp Lite "Remote Shutdown" when USB cable is attached

Fairfax, Charles A. FairfaxC at missouri.edu
Tue Feb 2 16:05:50 GMT 2021


Sorry, the list address got dropped on prior send.

Charles Fairfax

-----Original Message-----
From: Fairfax, Charles A. 
Sent: Tuesday, February 2, 2021 9:18 AM
To: David Zomaya <David_Zomaya at tripplite.com>; Adam Talbot <ajtalbot1 at gmail.com>
Subject: RE: [Nut-upsuser] [EXTERNAL] Tripp Lite "Remote Shutdown" when USB cable is attached

I don't know that my experience is helpful except that I had what sounds like a similar experience with a similar UPS in October of 2016.  I was attaching a Raspberry Pi (Raspbian wheezy) with NUT 2.6.4 to a TrippLite SU3000XLCD via USB and the UPS shut down, dropping the load.  I had never seen this  happen before with the 8 or so other older model TrippLite UPSs I have in service.  

Unfortunately I was not at liberty to perform much troubleshooting owing to the nature of the load and don't have another UPS of the same model.  I tried serial communication but was not successful.  Eventually I did get the UPS link to work.   If I remember correctly I booted the Pi after connecting the USB cable.  It has been working since and I have not unplugged the USB cable.

Have you tried booting the computer after connecting the USB cable?

-----Original Message-----
From: Nut-upsuser <nut-upsuser-bounces+fairfaxc=missouri.edu at alioth-lists.debian.net> On Behalf Of David Zomaya via Nut-upsuser
Sent: Monday, February 1, 2021 4:43 PM
To: Adam Talbot <ajtalbot1 at gmail.com>; nut-upsuser at alioth-lists.debian.net
Subject: Re: [Nut-upsuser] [EXTERNAL] Tripp Lite "Remote Shutdown" when USB cable is attached

I don't have a quick answer for you but I'll be in the office later this week and can grab a model with the same protocol and run a test on one of my Ubuntu boxes (which should be close enough to your Pi setup).


Thank you,
David Zomaya
Tripp Lite








From: Nut-upsuser <nut-upsuser-bounces+david_zomaya=tripplite.com at alioth-lists.debian.net> on behalf of Adam Talbot via Nut-upsuser <nut-upsuser at alioth-lists.debian.net>
Sent: Monday, February 1, 2021 3:39 PM
To: nut-upsuser at alioth-lists.debian.net
Subject: [EXTERNAL] [Nut-upsuser] Tripp Lite "Remote Shutdown" when USB cable is attached

This is an EXTERNAL email. Please take a moment and think before clicking any links or opening any attachments from this email. If suspicious, please forward to ishelpdesk at tripplite.com for review.
I am kinda stuck on this one.  Whenever I attach (USB to a linux box) my TrippLite UPS, it "REMOTE SHUTDOWN".  This is a new problem that has cropped up in the last 6 months.  At first I thought it was a NUT configuration issue, but now I believe this  to be some kind of kernel bug?  When I plug in the UPS, I can see the system logs show the UPS, then everything powers off.


UPS LCD shows the below error when I plug in the USB cable:
"OUTPUT OFF"
"REMOTE SHUTDOWN"


I tested this against 2 different X86 boxes and a Raspberry Pi. All cause the same result in the UPS.  Only one box (nas) has NUT installed and configured.


UPS is a Tripp Lite SU3000RTXLCD2U.


I am totally stumped on this one.  Below is a dump of basically all my specs.  Any ideas?
-Adam



root at nas:~# uname -a
Linux nas 5.4.78-2-pve #1 SMP PVE 5.4.78-2 (Thu, 03 Dec 2020 14:26:17 +0100) x86_64 GNU/Linux

root at nas:~# cat /etc/nut/nut.conf
MODE=netserver
root at nas:~# cat /etc/nut/ups.conf
[ups1]
driver=usbhid-ups
port=auto
root at nas:~# cat /etc/nut/upsd.conf
LISTEN 127.0.0.1 3493
LISTEN 10.1.1.2
root at nas:~# cat /etc/nut/upsmon.conf
root at nas:~# cat /etc/nut/upssched.conf
root at nas:~#

root at nas:~# cat /etc/debian_version
10.7



Before all this broke, I was able to monitor the UPS and get the following info:
battery.charge: 100
battery.charge.low: 20
battery.charge.warning: 20
battery.runtime: 6662
battery.temperature: 29.9
battery.type: PbAc
battery.voltage: 81.0
battery.voltage.nominal: 72.0
device.mfr: TRIPPLITE
device.model: TRIPPLITE UPS
device.serial: XXXXXXXXXXXXXX
device.type: ups
driver.name:  usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.synchronous: no
driver.version: 2.7.4
driver.version.data: TrippLite HID 0.82
driver.version.internal: 0.41
input.frequency: 60.0
input.transfer.high: 150.0
input.transfer.high.max: 150
input.transfer.high.min: 145
input.transfer.low: 55.0
input.transfer.low.max: 60
input.transfer.low.min: 55
input.voltage: 123.0
input.voltage.nominal: 120
output.current: 1.9
output.frequency: 60.0
output.frequency.nominal: 60
output.voltage: 120.0
output.voltage.nominal: 120
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.firmware: 64
ups.load: 8
ups.mfr: TRIPPLITE
ups.model: TRIPPLITE UPS
ups.power: 226.0
ups.power.nominal: 3000
ups.productid: 4004
ups.serial: 2620ELCPS87A200020
ups.status: OL
ups.test.result: Done and passed
ups.timer.reboot: 0
ups.timer.shutdown: -1
ups.timer.start: 0
ups.vendorid: 09ae
ups.watchdog.status: 0


root at nas:/var/log# zcat messages.*.gz | grep -i tripp
Jan 15 11:05:05 nas kernel: [    1.571857] usb 3-1: Product: TRIPPLITE UPS
Jan 15 11:05:05 nas kernel: [    1.571858] usb 3-1: Manufacturer: TRIPPLITE
Jan 15 11:05:05 nas kernel: [    1.629210] hid-generic 0003:09AE:4004.0001: hiddev0,hidraw0: USB HID v1.11 Device [TRIPPLITE        TRIPPLITE UPS   ] on usb-0000:2e:00.3-1/input0



________________________________
 This message is for the addressee's use only. It may contain confidential information. If you receive this message in error, please delete it and notify the sender. Tripp Lite disclaims all warranties and liabilities, and assumes no responsibility for viruses which may infect an email sent to you from Tripp Lite and which damage your electronic systems or information. It is your responsibility to maintain virus detection systems to prevent damage to your electronic systems and information.