an update w.r.t NUT support for " ABB UPS Powervalue 11RT G2".
I can confirm it works with the configuration listed below when using the
driver "nutdrv_qx".
With the caveat that "battery.voltage" is under reported.
Sometimes it helps to RTFM.
--snip--
*override.battery.packs =* *value*
Some devices report a part of the total battery voltage. For instance, if
*battery.voltage.nominal* is 24 V, but it reports a *battery.voltage* of
around 2 V, the number of *battery.packs* to correct this reading would be
12. The driver will attempt to detect this automatically, but if this fails
somehow, you may want to override this value.
--snip--
+ Working Config:
--snip--
[abb1kva]
driver = "nutdrv_qx"
port = "auto"
vendorid = "0665"
productid = "5161"
bus = "001"
desc = "ABB PowerValue G2 1KVA"
# runtimecal from ABB UPS documentation
runtimecal = 240,100,360,75,1200,50,1380,25
override.battery.packs = 12
--snip--
+ Output:
--snip--
[root at threepi01 ~]# upsc abb1kva
battery.charge: 100
battery.packs: 12
battery.runtime: 2400
battery.voltage: 2.28 <== under reported
battery.voltage.high: 26.00
battery.voltage.low: 20.80
battery.voltage.nominal: 24.0
device.model: WPHVR1K0
device.type: ups
driver.name: nutdrv_qx
driver.parameter.bus: 001
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.productid: 5161
driver.parameter.runtimecal: 240,100,360,75,1200,50,1380,25
driver.parameter.synchronous: auto
driver.parameter.vendorid: 0665
driver.version: 2.8.0
driver.version.data: Megatec 0.06
driver.version.internal: 0.32
driver.version.usb: libusb-1.0.26 (API: 0x1000109)
input.current.nominal: 4.0
input.frequency: 50.0
input.frequency.nominal: 50
input.voltage: 237.9
input.voltage.fault: 238.1
input.voltage.nominal: 240
output.voltage: 237.9
ups.beeper.status: enabled
ups.delay.shutdown: 30
ups.delay.start: 180
ups.firmware: 02724.08
ups.load: 18
ups.productid: 5161
ups.status: OL BYPASS
ups.temperature: 20.7
ups.type: online
ups.vendorid: 0665
--snip--
Q. Is it possible to fix the battery.voltage output ?
Q. What is the proper way to get the model and vendor recognized ?
Kind Regards,
Yogesh
On Fri, Jul 1, 2022 at 11:09 AM Yogesh Bhanu <yogesh.bhanu at gmail.com> wrote:
> Hi,
>
> I just installed an ABB UPS Powervalue 11RT G2 1KVA. I'm using NUT version
> 2.8.0 on a RPI3 running ArchLinux.
> # config
> --snip--
> [abb1kva]
> driver = "nutdrv_qx"
> port = "auto"
> vendorid = "0665"
> productid = "5161"
> bus = "001"
> desc = "ABB PowerValue G2 1KVA"
> runtimecal = 240,100,360,75,1200,50,1380,25
> --snip--
>
> I get the following output :
>
> --snip--
> [root at threepi01 nut]# upsdrvctl -u nut -DDD start
> Network UPS Tools - UPS driver controller 2.8.0
> 0.000000 [D2]
> If you're not a NUT core developer, chances are that you're told to enable
> debugging
> to see why a driver isn't working for you. We're sorry for the confusion,
> but this is
> the 'upsdrvctl' wrapper, not the driver you're interested in.
>
> Below you'll find one or more lines starting with 'exec:' followed by an
> absolute
> path to the driver binary and some command line option. This is what the
> driver
> starts and you need to copy and paste that line and append the debug flags
> to that
> line (less the 'exec:' prefix).
>
> Alternately, provide an additional '-d' (lower-case) parameter to
> 'upsdrvctl' to
> pass its current debug level to the launched driver.
>
> 0.000602 [D1] Starting UPS: abb1kva
> 0.000774 [D2] 3 remaining attempts
> 0.000820 [D2] exec: /usr/lib/nut/nutdrv_qx -a abb1kva -u nut
> Network UPS Tools - Generic Q* USB/Serial driver 0.32 (2.8.0)
> USB communication driver (libusb 1.0) 0.43
> Protocol [PI05] is not supported by this driver
> Protocol [PI05] is not supported by this driver
> Protocol [PI05] is not supported by this driver
> Protocol [PI05] is not supported by this driver
> Protocol [PI05] is not supported by this driver
> Protocol [PI05] is not supported by this driver
> Using protocol: Megatec 0.06
> No values for battery high/low voltages
> Using 'guesstimation' (low: 20.800000, high: 26.000000)!
> No charge time specified, using built in default [43200 seconds]
> No idle load specified, using built in default [10.0 %]
>
> [root at threepi01 nut]# upsc abb1kva
> battery.charge: 0
> battery.voltage: 2.28
> battery.voltage.high: 26.00
> battery.voltage.low: 20.80
> battery.voltage.nominal: 24.0
> device.model: WPHVR1K0
> device.type: ups
> driver.name: nutdrv_qx
> driver.parameter.bus: 001
> driver.parameter.pollfreq: 30
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.parameter.productid: 5161
> driver.parameter.runtimecal: 240,100,360,75,1200,50,1380,25
> driver.parameter.synchronous: auto
> driver.parameter.vendorid: 0665
> driver.version: 2.8.0
> driver.version.data: Megatec 0.06
> driver.version.internal: 0.32
> driver.version.usb: libusb-1.0.26 (API: 0x1000109)
> input.current.nominal: 4.0
> input.frequency: 50.0
> input.frequency.nominal: 50
> input.voltage: 236.3
> input.voltage.fault: 236.7
> input.voltage.nominal: 240
> output.voltage: 239.7
> ups.beeper.status: enabled
> ups.delay.shutdown: 30
> ups.delay.start: 180
> ups.firmware: 02724.08
> ups.load: 20
> ups.productid: 5161
> ups.status: OL
> ups.temperature: 20.1
> ups.type: online
> ups.vendorid: 0665
> --snip--
>
>
>
>
> But with the blazer_usb.
> # config:
>
> --snip--
> [abb1kva]
> driver = "blazer_usb"
> port = "auto"
> vendorid = "0665"
> productid = "5161"
> bus = "001"
> desc = "ABB PowerValue G2 1KVA"
> runtimecal = 240,100,360,75,1200,50,1380,25
> --snip--
>
> I get the following output:
>
> --snip--
> [root at threepi01 nut]# upsdrvctl -u nut -DDD start
> Network UPS Tools - UPS driver controller 2.8.0
> 0.000000 [D2]
> If you're not a NUT core developer, chances are that you're told to enable
> debugging
> to see why a driver isn't working for you. We're sorry for the confusion,
> but this is
> the 'upsdrvctl' wrapper, not the driver you're interested in.
>
> Below you'll find one or more lines starting with 'exec:' followed by an
> absolute
> path to the driver binary and some command line option. This is what the
> driver
> starts and you need to copy and paste that line and append the debug flags
> to that
> line (less the 'exec:' prefix).
>
> Alternately, provide an additional '-d' (lower-case) parameter to
> 'upsdrvctl' to
> pass its current debug level to the launched driver.
>
> 0.000573 [D1] Starting UPS: abb1kva
> 0.000621 [D2] 3 remaining attempts
> 0.000655 [D2] exec: /usr/lib/nut/blazer_usb -a abb1kva -u nut
> Network UPS Tools - Megatec/Q1 protocol USB driver 0.14 (2.8.0)
> Please note that this driver is deprecated and will not receive
> new development. If it works for managing your devices - fine,
> but if you are running it to try setting up a new device, please
> consider the newer nutdrv_qx instead, which should handle all 'Qx'
> protocol variants for NUT. (Please also report if your device works
> with this driver, but nutdrv_qx would not actually support it with
> any subdriver!)
>
> Supported UPS detected with megatec protocol
> Vendor information read in 1 tries
> No values provided for battery high/low voltages in ups.conf
>
> Using 'guestimation' (low: 20.800000, high: 26.000000)!
> No charge time specified, using built in default [43200 seconds]
> No idle load specified, using built in default [10.0 %]
>
> [root at threepi01 nut]# upsc abb1kva
> battery.charge: 93
> battery.runtime: 2237
> battery.voltage: 27.24
> battery.voltage.high: 26.00
> battery.voltage.low: 20.80
> battery.voltage.nominal: 24.0
> device.mfr:
> device.model: WPHVR1K0
> device.type: ups
> driver.name: blazer_usb
> driver.parameter.bus: 001
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.parameter.productid: 5161
> driver.parameter.runtimecal: 240,100,360,75,1200,50,1380,25
> driver.parameter.synchronous: auto
> driver.parameter.vendorid: 0665
> driver.version: 2.8.0
> driver.version.internal: 0.14
> driver.version.usb: libusb-1.0.26 (API: 0x1000109)
> input.current.nominal: 4.0
> input.frequency: 50.0
> input.frequency.nominal: 50
> input.voltage: 237.7
> input.voltage.fault: 237.5
> input.voltage.nominal: 240
> output.voltage: 239.7
> ups.beeper.status: enabled
> ups.delay.shutdown: 30
> ups.delay.start: 180
> ups.firmware: 02724.08
> ups.load: 18
> ups.mfr:
> ups.model: WPHVR1K0
> ups.productid: 5161
> ups.status: OL
> ups.temperature: 20.1
> ups.type: online
> ups.vendorid: 0665
> --snip--
> Q: How can I get the new driver to display the correct outputs for ?
> --snip--
> battery.charge: 0
> battery.voltage: 2.28
> --snip--
>
> Q: is it possible to fix the battery Voltage values as the reported
> voltage "battery.voltage: 27.24":
> is correct ( confirmed on the panel)
>
> battery.voltage.high: 26.00
> battery.voltage.low: 20.80
>
> Q: Do I have to upload a DDL to get the following output sorted.
>
> From:
> --snip--
> ups.mfr:
> ups.model: WPHVR1K0
> --snip--
>
> To:
> --snip--
> ups.mfr: ABB
> ups.model: Powervalue 11RT G2 1kva
> --snip--
>
> Q. What does "input.voltage.fault" mean ?
>
> Thanks in advance,
>
> Yogesh
>
-------------- next part --------------