[Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade

Simon Wilson simon at simonandkate.net
Thu Dec 1 12:41:57 GMT 2022


Hi Bill, well at least you now have a fully operating,  
starts-on-reboot driver - so that is progress. One thing we need to  
know which I asked but you've not answered:
"Did you need to add the environment drop-in file? At which step did  
it work?" The answer to that may change next step.

nut-server *should* just work if there is a driver available and running.

OK, run:

  systemctl disable nut-server (stop it trying to run automatically)
  upsd -DD

And then Ctrl-C to stop it once you have got output to screen with  
startup messages.

Then copy back here the output from upsd -DD, preferably without  
truncating lines which your mail client seems to do :(

I'm pretty sure that nut-server is using /var/run as its STATEPATH.  
Can you also include your upsd.conf, minus commented lines.

Simon.

----- Message from Bill Gee <bgee at campercaver.net> ---------
    Date: Thu, 1 Dec 2022 06:14:10 -0600
    From: Bill Gee <bgee at campercaver.net>
Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
      To: nut-upsuser at alioth-lists.debian.net


> Hi Simon -
>
> I modified /usr/lib/tmpfiles.d/nut-client to use /run instead of  
> /var/run.  I checked the startup status of the nut services.
>
> =================
> [root at mythtv ~]# systemctl list-unit-files | grep -i nut
> nut-driver-enumerator.path  enabled         disabled
> nut-driver-enumerator.service  enabled         disabled
> nut-driver at .service  indirect        disabled
> nut-monitor.service  disabled        disabled
> nut-server.service  enabled         disabled
> nut-driver.target  disabled        disabled
> nut.target  disabled        disabled
> ==========================
>
> I did a shutdown/reboot on the system.  The usbhid driver loaded  
> without errors and did not complain about /var/run.  /run/nut exists  
> and contains the expected two files.
>
> nut-server also started since it is set to "enabled", but failed to  
> connect to the driver.  It complains about "no such file or  
> directory". What file is it looking for?  I ran journalctl on it but  
> got nothing more than what systemctl status reports.
>
> ===========================
> [root at mythtv ~]# systemctl status nut-driver at cyberpower
> ● nut-driver at cyberpower.service - Network UPS Tools - device driver  
> for NUT device 'cyberpower'
>      Loaded: loaded (/usr/lib/systemd/system/nut-driver at .service;  
> enabled; preset: disabled)
>     Drop-In: /etc/systemd/system/nut-driver at .service.d
>              └─environ.conf
>              /etc/systemd/system/nut-driver at cyberpower.service.d
>              └─nut-driver-enumerator-generated-checksum.conf,  
> nut-driver-enumerator-generated.conf
>      Active: active (running) since Thu 2022-12-01 05:56:04 CST; 9min ago
>     Process: 712 ExecStartPre=/usr/bin/systemd-tmpfiles --create  
> /usr/lib/tmpfiles.d/nut-client.conf (code=exited, stat>
>     Process: 719 ExecStart=/bin/sh -c  
> NUTDEV="`/usr/libexec/nut-driver-enumerator.sh  
> --get-device-for-service cyberpowe>
>    Main PID: 791 (usbhid-ups)
>       Tasks: 1 (limit: 9482)
>      Memory: 2.9M
>         CPU: 113ms
>      CGroup:  
> /system.slice/system-nut\x2ddriver.slice/nut-driver at cyberpower.service
>              └─791 /usr/sbin/usbhid-ups -a cyberpower
>
> Dec 01 05:56:04 mythtv.billgee.local nut-driver at cyberpower[787]:  
> Using subdriver: CyberPower HID 0.6
> Dec 01 05:56:04 mythtv.billgee.local nut-driver at cyberpower[787]:  
> Network UPS Tools - Generic HID driver 0.47 (2.8.0)
> Dec 01 05:56:04 mythtv.billgee.local nut-driver at cyberpower[787]: USB  
> communication driver (libusb 1.0) 0.43
> Dec 01 05:56:04 mythtv.billgee.local nut-driver at cyberpower[787]:  
> cps_adjust_battery_scale: battery readings will be sca>
> Dec 01 05:56:04 mythtv.billgee.local nut-driver at cyberpower[719]:  
> Network UPS Tools - UPS driver controller 2.8.0
> Dec 01 05:56:04 mythtv.billgee.local usbhid-ups[791]: Startup successful
>
> [root at mythtv ~]# systemctl status nut-server
> ● nut-server.service - Network UPS Tools - power devices information server
>      Loaded: loaded (/usr/lib/systemd/system/nut-server.service;  
> enabled; preset: disabled)
>      Active: active (running) since Thu 2022-12-01 05:56:07 CST; 9min ago
>    Main PID: 809 (upsd)
>       Tasks: 1 (limit: 9482)
>      Memory: 1000.0K
>         CPU: 15ms
>      CGroup: /system.slice/nut-server.service
>              └─809 /usr/sbin/upsd -F
>
> Dec 01 05:56:08 mythtv.billgee.local upsd[809]: listening on ::1 port 3493
> Dec 01 05:56:08 mythtv.billgee.local upsd[809]: listening on  
> 127.0.0.1 port 3493
> Dec 01 05:56:08 mythtv.billgee.local nut-server[809]: /var/run is  
> world readable
> Dec 01 05:56:08 mythtv.billgee.local nut-server[809]: Can't connect  
> to UPS [cyberpower] (usbhid-ups-cyberpower): No suc>
> Dec 01 05:56:08 mythtv.billgee.local upsd[809]: /var/run is world readable
> Dec 01 05:56:08 mythtv.billgee.local upsd[809]: Can't connect to UPS  
> [cyberpower] (usbhid-ups-cyberpower): No such file>
> Dec 01 05:56:10 mythtv.billgee.local nut-server[809]: Running as  
> foreground process, not saving a PID file
> Dec 01 05:56:10 mythtv.billgee.local upsd[809]: Running as  
> foreground process, not saving a PID file
> Dec 01 06:01:08 mythtv.billgee.local nut-server[809]: Can't connect  
> to UPS [cyberpower] (usbhid-ups-cyberpower): No suc>
> Dec 01 06:01:08 mythtv.billgee.local upsd[809]: Can't connect to UPS  
> [cyberpower] (usbhid-ups-cyberpower): No such file>
> ================================
>
>
>
> ===============
> Bill Gee
>
> On 11/30/22 21:14, Simon Wilson via Nut-upsuser wrote:
>> ----- Message from Bill Gee <bgee at campercaver.net> ---------
>>    Date: Wed, 30 Nov 2022 19:26:46 -0600
>>    From: Bill Gee <bgee at campercaver.net>
>> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
>>      To: nut-upsuser at alioth-lists.debian.net
>>
>>
>>> Hi Simon -
>>>
>>> I ran through the steps you gave below.  To quote Gilbert&Sullivan  
>>> ... "Modified Rapture!"  I suppose I should try a reboot to make  
>>> sure everything starts properly.
>>
>> Not yet with the reboot. Baby steps... :) you have a driver running  
>> from the service file! Celebrations are in order.
>>
>> Did you need to add the environment drop-in file? At which step did it work?
>>
>>> But first, there is a problem with upsc. Also nut-server complains  
>>> that it cannot connect to the device.
>>
>> Ok, that's next... your comments are wrong way around :) nut-server  
>> not starting is why upsc doesn't give you anything.
>>
>>>
>>> /run/nut exists and contains two files.
>>>
>>> Here are some outputs:
>>>
>>> ======================================
>>> [root at mythtv ~]# journalctl -u nut-driver at cyberpower.service -f
>>> Nov 30 19:00:20 mythtv.billgee.local systemd[1]: Starting  
>>> nut-driver at cyberpower.service - Network UPS Tools - device driver  
>>> for NUT device 'cyberpower'...
>>> Nov 30 19:00:20 mythtv.billgee.local systemd-tmpfiles[28689]:  
>>> /usr/lib/tmpfiles.d/nut-client.conf:2: Line references path below  
>>> legacy directory /var/run/, updating /var/run/nut → /run/nut;  
>>> please update the tmpfiles.d/ drop-in file accordingly.
>>
>> That line is the "noise" error I mentioned. Edit  
>> /usr/lib/tmpfiles.d/nut-client.conf to read /run/nut, not  
>> /var/run/nut
>>
>>> Nov 30 19:00:20 mythtv.billgee.local systemd-tmpfiles[28689]:  
>>> /usr/lib/tmpfiles.d/nut-client.conf:3: Line references path below  
>>> legacy directory /var/run/, updating /var/run/nut → /run/nut;  
>>> please update the tmpfiles.d/ drop-in file accordingly.
>>
>> Ditto, although you probably don't need line 3 in the file anyway.
>>
>>> Nov 30 19:00:21 mythtv.billgee.local nut-driver at cyberpower[28719]:  
>>> Using subdriver: CyberPower HID 0.6
>>> Nov 30 19:00:21 mythtv.billgee.local nut-driver at cyberpower[28719]:  
>>> Network UPS Tools - Generic HID driver 0.47 (2.8.0)
>>> Nov 30 19:00:21 mythtv.billgee.local nut-driver at cyberpower[28719]:  
>>> USB communication driver (libusb 1.0) 0.43
>>> Nov 30 19:00:21 mythtv.billgee.local nut-driver at cyberpower[28719]:  
>>> cps_adjust_battery_scale: battery readings will be scaled by 2/3
>>> Nov 30 19:00:21 mythtv.billgee.local usbhid-ups[28769]: Startup successful
>>> Nov 30 19:00:21 mythtv.billgee.local nut-driver at cyberpower[28691]:  
>>> Network UPS Tools - UPS driver controller 2.8.0
>>> Nov 30 19:00:21 mythtv.billgee.local systemd[1]: Started  
>>> nut-driver at cyberpower.service - Network UPS Tools - device driver  
>>> for NUT device 'cyberpower'.
>>>
>>> [root at mythtv ups]# ll /run/nut
>>> total 4
>>> srw-rw---- 1 nut nut 0 Nov 30 19:00 usbhid-ups-cyberpower
>>> -rw-r--r-- 1 nut nut 6 Nov 30 19:00 usbhid-ups-cyberpower.pid
>>>
>>>
>>> [root at mythtv ups]# systemctl --no-pager --full status nut-server
>>> ● nut-server.service - Network UPS Tools - power devices information server
>>>      Loaded: loaded (/usr/lib/systemd/system/nut-server.service;  
>>> enabled; preset: disabled)
>>>      Active: active (running) since Wed 2022-11-30 19:06:53 CST; 13min ago
>>>    Main PID: 28918 (upsd)
>>>       Tasks: 1 (limit: 9482)
>>>      Memory: 736.0K
>>>         CPU: 20ms
>>>      CGroup: /system.slice/nut-server.service
>>>              └─28918 /usr/sbin/upsd -F
>>>
>>> Nov 30 19:06:53 mythtv.billgee.local nut-server[28918]: /var/run  
>>> is world readable
>>> Nov 30 19:06:53 mythtv.billgee.local upsd[28918]: /var/run is  
>>> world readable
>>> Nov 30 19:06:53 mythtv.billgee.local upsd[28918]: Can't connect to  
>>> UPS [cyberpower] (usbhid-ups-cyberpower): Connection refused
>>> Nov 30 19:06:53 mythtv.billgee.local nut-server[28918]: Can't  
>>> connect to UPS [cyberpower] (usbhid-ups-cyberpower): Connection  
>>> refused
>>> Nov 30 19:06:53 mythtv.billgee.local nut-server[28918]: Running as  
>>> foreground process, not saving a PID file
>>> Nov 30 19:06:53 mythtv.billgee.local upsd[28918]: Running as  
>>> foreground process, not saving a PID file
>>> Nov 30 19:11:53 mythtv.billgee.local nut-server[28918]: Can't  
>>> connect to UPS [cyberpower] (usbhid-ups-cyberpower): Connection  
>>> refused
>>> Nov 30 19:11:53 mythtv.billgee.local upsd[28918]: Can't connect to  
>>> UPS [cyberpower] (usbhid-ups-cyberpower): Connection refused
>>> Nov 30 19:16:53 mythtv.billgee.local nut-server[28918]: Can't  
>>> connect to UPS [cyberpower] (usbhid-ups-cyberpower): Connection  
>>> refused
>>> Nov 30 19:16:53 mythtv.billgee.local upsd[28918]: Can't connect to  
>>> UPS [cyberpower] (usbhid-ups-cyberpower): Connection refused
>>>
>>> [root at mythtv ups]# ps ax | grep ups
>>>     768 ?        Ss     0:00 /usr/sbin/cupsd -l
>>>     773 ?        Ss     0:00 sshd: /usr/sbin/sshd -D [listener] 0  
>>> of 10-100 startups
>>>   28769 ?        Ss     0:00 /usr/sbin/usbhid-ups -a cyberpower
>>>   28918 ?        Ss     0:00 /usr/sbin/upsd -F
>>>   28929 pts/1    S+     0:00 grep --color=auto ups
>>>
>>> [root at mythtv ups]# upsc cyberpower at localhost
>>> Error: Driver not connected
>>
>> upsc won't work without nut-server running, so this is expected  
>> based on the above failure to start nut-server.
>>
>>>
>>>
>>
>> So... next.
>>
>> Fix nut-client.conf contents, and make sure that you can start /  
>> restart the driver as needed with no errors. Set  
>> nut-driver at cyberpower.service to enabled for autostart, so with  
>> ONLY the enumerator services and nut-driver at cyberpower.service  
>> enabled, you should see something like the following for 'systemctl  
>> list-unit-files | grep -i nut':
>>
>> [root at emp80 ups]# systemctl list-unit-files | grep -i nut
>> nut-driver-enumerator.path                                           
>>    enabled
>> nut-driver-enumerator.service                                        
>>    enabled
>> nut-driver at .service                                                  
>>    indirect
>> nut-monitor.service                                                  
>>    disabled
>> nut-server.service                                                   
>>    disabled
>> nut-driver.target                                                    
>>    disabled
>> nut.target                                                           
>>    disabled
>>
>> Stop any running nut processes, and reboot. On reboot the only  
>> thing that should autostart is nut-driver at cyberpower.service (from  
>> the 'indirect' call via nut-driver at .service). upsc will still not  
>> work.
>>
>> Monitor the driver for a while 'journalctl -u  
>> nut-driver at cyberpower.service -f' and make sure it is stable and  
>> stays connected - google searches show some flakiness with some  
>> cyberpower UPSs.
>>
>> Once you are confident that the driver is reliable, starting OK and  
>> staying up then move on to nut-server.
>>
>> I'll check in this evening and we can do some more digging on that.
>>
>> Simon
>>
>>>
>>> ===============
>>> Bill Gee
>>>
>>> On 11/30/22 07:21, Simon Wilson via Nut-upsuser wrote:
>>>> Comments inline.
>>>>
>>>> ----- Message from Bill Gee <bgee at campercaver.net> ---------
>>>>    Date: Wed, 30 Nov 2022 06:04:14 -0600
>>>>    From: Bill Gee <bgee at campercaver.net>
>>>> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
>>>>      To: nut-upsuser at alioth-lists.debian.net
>>>>
>>>>
>>>>> Hi Simon --
>>>>>
>>>>> Yes, I am pretty sure this is the RedHat packaging problem.  I  
>>>>> sure hope they get it squared away.  I have only one system  
>>>>> using nut and that is because all my other systems have APC  
>>>>> battery backup and run apcupsd. Apcupsd may be old, grey and  
>>>>> unmaintained, but it Just Works.
>>>>>
>>>>> You mention that the STATEPATH line in upsd.conf will override  
>>>>> other settings.  It does not appear to be the case for me.  The  
>>>>> only way I could get the driver to run was by setting  
>>>>> NUT_STATEPATH on the command line.  Perhaps that is an issue  
>>>>> with the driver and not nut-server?
>>>>>
>>>>> In answer to your questions:
>>>>>
>>>>> 1) /usr/lib/systemd/system/nut-driver at .service exists.  I have  
>>>>> made no changes to it so far.  Here are the contents,  
>>>>> unfortunately line-wrapped by Thunderbird.
>>>>>
>>>>> ================================
>>>>> [root at mythtv system]# grep -v '^#' nut-driver at .service
>>>>> [Unit]
>>>>> Description=Network UPS Tools - device driver for %I
>>>>> After=local-fs.target
>>>>>
>>>>>
>>>>> PartOf=nut-driver.target
>>>>>
>>>>>
>>>>> [Service]
>>>>> EnvironmentFile=-/etc/ups/nut.conf
>>>>> SyslogIdentifier=%N
>>>>> ExecStartPre=-/usr/bin/systemd-tmpfiles --create  
>>>>> /usr/lib/tmpfiles.d/nut-client.conf
>>>>> ExecStart=/bin/sh -c  
>>>>> 'NUTDEV="`/usr/libexec/nut-driver-enumerator.sh  
>>>>> --get-device-for-service %i`" && [ -n "$NUTDEV" ] || { echo  
>>>>> "FATAL: Could not find a NUT device section for service unit %i"  
>>>>> >&2 ; exit 1 ; } ; /usr/sbin/upsdrvctl start "$NUTDEV"'
>>>>> ExecStop=/bin/sh -c  
>>>>> 'NUTDEV="`/usr/libexec/nut-driver-enumerator.sh  
>>>>> --get-device-for-service %i`" && [ -n "$NUTDEV" ] || { echo  
>>>>> "FATAL: Could not find a NUT device section for service unit %i"  
>>>>> >&2 ; exit 1 ; } ; /usr/sbin/upsdrvctl stop "$NUTDEV"'
>>>>> StartLimitInterval=0
>>>>> Restart=always
>>>>> RestartSec=15s
>>>>> Type=forking
>>>>>
>>>>> [Install]
>>>>> WantedBy=nut-driver.target
>>>>> ===================================
>>>>
>>>> OK, so that's the same as mine. It's ExecStartPre task is to  
>>>> create the pid folder from your answer to the third (unasked)  
>>>> question :) which is that outlined in  
>>>> /usr/lib/tmpfiles.d/nut-client.conf
>>>>
>>>> You have /var/run/nut 0770 root nut - so systemd should ensure  
>>>> that exists.
>>>>
>>>> By the way, having it with "/var/run/nut" will trigger a 'noise'  
>>>> error about the "/var" path - change it to just be /run/nut in  
>>>> nut-client.conf.
>>>>
>>>> As a test, what happens if you:
>>>>
>>>> - make sure nut.conf has MODE=standalone
>>>> - make sure ALL nut services are stopped, i.e. 'ps -ax | grep  
>>>> ups' should give you only the grep process as an answer
>>>> - delete /run/nut folder (it will get re-created automatically)
>>>> - take /etc/ups/upsd.conf back to have commented out STATEPATH as  
>>>> distributed in the package
>>>> - run "systemctl enable nut-driver-enumerator.path  
>>>> nut-driver-enumerator.service --now" - this will enable and start  
>>>> the services that monitor ups.conf for changes and then write the  
>>>> actual driver service file; the second one also runs early in  
>>>> boot and ensures that the service file exists and is correct.
>>>> - run 'nut-scanner -U' and copy its output into ups.conf instead  
>>>> of your current definition with name heading [cyberpower], save  
>>>> and exit: this will trigger the above enumerators to run and  
>>>> re-do the nut-driver at cyberpower.service file
>>>>
>>>> Based on an out of the box install, you have at this point done  
>>>> enough that the driver should run (*should*!!!!)
>>>>
>>>> - run "journalctl -u nut-driver at cyberpower.service -f" in one  
>>>> terminal while you run "systemctl start  
>>>> nut-driver at cyberpower.service" in another - what does journalctl  
>>>> output?
>>>>
>>>> Assuming it does not start (based on what you have said below),  
>>>> show the messages.
>>>>
>>>> If it still does not start as configured above, but you \can/ run  
>>>> /usr/sbin/usbhid-ups with your environment variables specified  
>>>> like you had done before, and it *does* run, then do the  
>>>> following steps to create a systemd drop-in file for the  
>>>> variable, but make the steps use /run/nut instead of  
>>>> /var/run/nut:   
>>>> https://bugzilla.redhat.com/show_bug.cgi?id=2127269#c8  (comment  
>>>> 8, formatted for ease of reading). You want to get back to the  
>>>> RH/Fedora default of using /run/nut, not /var/state/ups
>>>>
>>>>   1. uncomment the "STATEPATH /var/run/nut" as already mentioned
>>>>   2. create: /etc/systemd/system/nut-driver at .service.d/environ.conf
>>>>    with these two lines:
>>>>
>>>>     [Service]
>>>>     Environment=NUT_STATEPATH=/var/run/nut
>>>>
>>>>   3. and finally do: systemctl daemon-reload
>>>>
>>>> ...then try and run systemctl start nut-driver at cyberpower.service  
>>>> again, while monitoring journalctl.
>>>>
>>>>
>>>> If that does not work - then I'm out of ideas at this point lol... :-D
>>>>
>>>> 'set' has nothing BTW on my working system related to nut.
>>>>
>>>>>
>>>>> 2) In /etc/ups/upsd.conf, the original STATEPATH line is
>>>>>
>>>>> STATEPATH /var/run/nut
>>>>>
>>>>> Right now the original line is commented and I added another  
>>>>> line to point at /var/state/ups.
>>>>>
>>>>> 3) You only asked two questions, but I sense a third might be  
>>>>> important.  Originally the system had  
>>>>> /usr/lib/tmpfiles.d/nut-common.conf.  I have modified that file  
>>>>> and no longer have the original.  I copied that file to  
>>>>> nut-client.conf, and both have the same contents:
>>>>>
>>>>> =======================
>>>>> # State file (e.g. upsd to driver) and pidfile location for NUT:
>>>>> D /var/run/nut 0770 root nut - -
>>>>> X /var/run/nut
>>>>> ========================
>>>>>
>>>>> 4) And one more unasked question!  :-)  When I look at the  
>>>>> environment variables on the system, I see this:
>>>>>
>>>>> ========================
>>>>> [root at mythtv tmpfiles.d]# set | grep -i nut
>>>>> _=/etc/ups/nut.conf
>>>>> ========================
>>>>>
>>>>>
>>>>>
>>>>> Bill Gee
>>>>>
>>>>> On 11/30/22 01:20, Simon Wilson via Nut-upsuser wrote:
>>>>>> ----- Message from Bill Gee <bgee at campercaver.net> ---------
>>>>>>    Date: Tue, 29 Nov 2022 19:25:19 -0600
>>>>>>    From: Bill Gee <bgee at campercaver.net>
>>>>>> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
>>>>>>      To: Jim Klimov <jimklimov+nut at gmail.com>
>>>>>>      Cc: Arnaud Quette via Nut-upsuser  
>>>>>> <nut-upsuser at alioth-lists.debian.net>
>>>>>>
>>>>>>
>>>>>>> I got it to run, but what a mess ...
>>>>>>>
>>>>>>> Yes, I am running systemctl daemon-reload and systemctl  
>>>>>>> restart nut-server after each change I make.
>>>>>>>
>>>>>>
>>>>>> Hi Bill,
>>>>>>
>>>>>> Drivers and upsd share defaults (see 'man nutupsdrv').
>>>>>>
>>>>>> Your original error message ("writepid: fopen  
>>>>>> /var/run/usbhid-ups-cyberpower.pid: Permission denied") would  
>>>>>> seem to indicate, same as the Red Hat bug, that your driver's  
>>>>>> default pid path is /var/run.
>>>>>>
>>>>>> The driver by default uses STATEPATH (which can be over-ridden  
>>>>>> in upsd.conf) to store pid files. The driver .service file is  
>>>>>> supposed to make sure that path exists by running the  
>>>>>> ExecStartPre line, which gets its instructions from the  
>>>>>> referenced ".conf" file from /usr/lib/tmpfiles.d. The .service  
>>>>>> file then calls 'upsdrvctl start' to start your usbhid-ups  
>>>>>> driver, as defined in ups.conf. Those all need to align...
>>>>>>
>>>>>> 2 x questions:
>>>>>>
>>>>>> 1. Without its comments, what are the active lines (as  
>>>>>> installed, without any changes) in  
>>>>>> /usr/lib/systemd/system/nut-driver at .service (or wherever that  
>>>>>> service file is located on your system)?
>>>>>> 2. in your upsd.conf (also as installed, without any changes),  
>>>>>> what is the commented out STATEPATH you later mention  
>>>>>> uncommenting?
>>>>>>
>>>>>>> I created /usr/lib/tmpfiles.d/nut-client.conf   The owner is  
>>>>>>> root:root and permissions are 0644.  The contents are
>>>>>>>
>>>>>>> # State file (e.g. upsd to driver) and pidfile location for NUT:
>>>>>>> D /var/run/nut 0770 root nut - -
>>>>>>> X /var/run/nut
>>>>>>>
>>>>>>> I uncommented the STATEPATH line in /etc/ups/upsd.conf.
>>>>>>>
>>>>>>> I created a directory /var/state/ups, set to 777 permissions.   
>>>>>>> Changed the STATEPATH line in upsd.conf.  No success.
>>>>>>>
>>>>>>> I looked at /usr/lib/systemd/system/nut-driver at .service but  
>>>>>>> could not see any changes to be made.  The bug report at  
>>>>>>> RedHat mentions that a file identified in ExecStartPre does  
>>>>>>> not exist, but I could not duplicate.
>>>>>>>
>>>>>>> I tried running this as root:
>>>>>>>
>>>>>>> NUT_STATEPATH=/var/state/ups NUT_ALTPIDPATH=/var/state/ups  
>>>>>>> /usr/sbin/usbhid-ups -u nut -g nut -s cyberpower -x port=auto
>>>>>>>
>>>>>>> And it works.  I tried it with only one or the other of the  
>>>>>>> two environment variables, but did not work.  It has to have  
>>>>>>> both.
>>>>>>>
>>>>>>> ===============
>>>>>>> Bill Gee
>>>>>>>
>>>>>
>>>>> _______________________________________________
>>>>> Nut-upsuser mailing list
>>>>> Nut-upsuser at alioth-lists.debian.net
>>>>> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>>>>
>>>>
>>>> ----- End message from Bill Gee <bgee at campercaver.net> -----
>>>>
>>>>
>>>>
>>>
>>> _______________________________________________
>>> Nut-upsuser mailing list
>>> Nut-upsuser at alioth-lists.debian.net
>>> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>>
>>
>> ----- End message from Bill Gee <bgee at campercaver.net> -----
>>
>>
>>
>
> _______________________________________________
> Nut-upsuser mailing list
> Nut-upsuser at alioth-lists.debian.net
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser


----- End message from Bill Gee <bgee at campercaver.net> -----



-- 
Simon Wilson
M: 0400 12 11 16




More information about the Nut-upsuser mailing list