[Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade

Bill Gee bgee at campercaver.net
Thu Dec 1 16:43:04 GMT 2022


My email client (Thunderbird) does not truncate, but it does wrap.  The 
truncations come from the way systemctl runs its output through a pager. 
When I copy-paste from the bash session, it truncates at the right edge 
of the window.   I need to use the --full and --no-pager options to get 
the full text, which will be wrapped as needed.

Here is the output from upsd -DD:

===================================
[root at mythtv ~]# upsd -DD
Network UPS Tools upsd 2.8.0
    0.000000     fopen /var/run/upsd.pid: No such file or directory
    0.000030     Could not find PID file '/var/run/upsd.pid' to see if 
previous upsd instance is already running!

    0.000250     [D1] debug level is '2'
    0.000335     listening on ::1 port 3493
    0.000375     listening on 127.0.0.1 port 3493
    0.001417     /var/run is world readable
    0.001557     Can't connect to UPS [cyberpower] 
(usbhid-ups-cyberpower): No such file or directory
    0.002315     Running as foreground process, not saving a PID file
    0.002337     [D1] mainloop: UPS [cyberpower] is not currently connected
    0.002377     [D1] mainloop: UPS [cyberpower] is now connected as FD -1
    0.002399     [D2] mainloop: polling 2 filedescriptors
    2.003794     [D2] mainloop: no data available
    2.003842     [D1] mainloop: UPS [cyberpower] is not currently connected
    2.003897     [D1] mainloop: UPS [cyberpower] is now connected as FD -1
    2.003917     [D2] mainloop: polling 2 filedescriptors
    4.005963     [D2] mainloop: no data available
    4.006009     [D1] mainloop: UPS [cyberpower] is not currently connected
    4.006054     [D1] mainloop: UPS [cyberpower] is now connected as FD -1
    4.006073     [D2] mainloop: polling 2 filedescriptors
    6.008122     [D2] mainloop: no data available
==============================

Just for grins, I edited /etc/ups/upsd.conf to uncomment the STATEPATH 
line.  I set it to /run/nut.  When I ran upsd -DD again, it was still 
looking at /var/run.  However!  It successfully connected to the 
cyberpower device.  Upsc returns good information.


=================================
[root at mythtv ups]# upsd -DD
Network UPS Tools upsd 2.8.0
    0.000000     fopen /var/run/upsd.pid: No such file or directory
    0.000037     Could not find PID file '/var/run/upsd.pid' to see if 
previous upsd instance is already running!

    0.000271     [D1] debug level is '2'
    0.000357     listening on ::1 port 3493
    0.000395     listening on 127.0.0.1 port 3493
    0.001550     Connected to UPS [cyberpower]: usbhid-ups-cyberpower
    0.002323     Running as foreground process, not saving a PID file
    0.002347     [D2] mainloop: polling 3 filedescriptors
    0.002423     [D2] mainloop: polling 3 filedescriptors
    0.002493     [D2] mainloop: polling 3 filedescriptors
    0.002570     [D2] mainloop: polling 3 filedescriptors
    0.002648     [D2] mainloop: polling 3 filedescriptors
    0.002701     [D2] mainloop: polling 3 filedescriptors
    2.004311     [D2] mainloop: no data available
    2.004352     [D2] mainloop: polling 3 filedescriptors
    4.006061     [D2] mainloop: no data available

[root at mythtv ups]# systemctl --full --no-pager status nut-server
● nut-server.service - Network UPS Tools - power devices information server
      Loaded: loaded (/usr/lib/systemd/system/nut-server.service; 
disabled; preset: disabled)
      Active: active (running) since Thu 2022-12-01 10:35:01 CST; 18s ago
    Main PID: 3445 (upsd)
       Tasks: 1 (limit: 9482)
      Memory: 732.0K
         CPU: 4ms
      CGroup: /system.slice/nut-server.service
              └─3445 /usr/sbin/upsd -F

Dec 01 10:35:01 mythtv.billgee.local nut-server[3445]: fopen 
/var/run/upsd.pid: No such file or directory
Dec 01 10:35:01 mythtv.billgee.local nut-server[3445]: Could not find 
PID file '/var/run/upsd.pid' to see if previous upsd instance is already 
running!
Dec 01 10:35:01 mythtv.billgee.local nut-server[3445]: listening on ::1 
port 3493
Dec 01 10:35:01 mythtv.billgee.local nut-server[3445]: listening on 
127.0.0.1 port 3493
Dec 01 10:35:01 mythtv.billgee.local upsd[3445]: listening on ::1 port 3493
Dec 01 10:35:01 mythtv.billgee.local upsd[3445]: listening on 127.0.0.1 
port 3493
Dec 01 10:35:01 mythtv.billgee.local nut-server[3445]: Connected to UPS 
[cyberpower]: usbhid-ups-cyberpower
Dec 01 10:35:01 mythtv.billgee.local upsd[3445]: Connected to UPS 
[cyberpower]: usbhid-ups-cyberpower
Dec 01 10:35:01 mythtv.billgee.local upsd[3445]: Running as foreground 
process, not saving a PID file
Dec 01 10:35:01 mythtv.billgee.local nut-server[3445]: Running as 
foreground process, not saving a PID file

[root at mythtv ups]# upsc cyberpower at localhost
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 2100
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 13.3
battery.voltage.nominal: 12
device.mfr: CPS
device.model: UPS CP1000AVRLCD
device.type: ups
driver.name: usbhid-ups
[-- snip --]


===============
Bill Gee

On 12/1/22 06:41, Simon Wilson via Nut-upsuser wrote:
> Hi Bill, well at least you now have a fully operating, starts-on-reboot 
> driver - so that is progress. One thing we need to know which I asked 
> but you've not answered:
> "Did you need to add the environment drop-in file? At which step did it 
> work?" The answer to that may change next step.
> 
> nut-server *should* just work if there is a driver available and running.
> 
> OK, run:
> 
>   systemctl disable nut-server (stop it trying to run automatically)
>   upsd -DD
> 
> And then Ctrl-C to stop it once you have got output to screen with 
> startup messages.
> 
> Then copy back here the output from upsd -DD, preferably without 
> truncating lines which your mail client seems to do :(
> 
> I'm pretty sure that nut-server is using /var/run as its STATEPATH. Can 
> you also include your upsd.conf, minus commented lines.
> 
> Simon.
> 
> ----- Message from Bill Gee <bgee at campercaver.net> ---------
>     Date: Thu, 1 Dec 2022 06:14:10 -0600
>     From: Bill Gee <bgee at campercaver.net>
> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
>       To: nut-upsuser at alioth-lists.debian.net
> 
> 
>> Hi Simon -
>>
>> I modified /usr/lib/tmpfiles.d/nut-client to use /run instead of 
>> /var/run.  I checked the startup status of the nut services.
>>
>> =================
>> [root at mythtv ~]# systemctl list-unit-files | grep -i nut
>> nut-driver-enumerator.path  enabled         disabled
>> nut-driver-enumerator.service  enabled         disabled
>> nut-driver at .service  indirect        disabled
>> nut-monitor.service  disabled        disabled
>> nut-server.service  enabled         disabled
>> nut-driver.target  disabled        disabled
>> nut.target  disabled        disabled
>> ==========================
>>
>> I did a shutdown/reboot on the system.  The usbhid driver loaded 
>> without errors and did not complain about /var/run.  /run/nut exists 
>> and contains the expected two files.
>>
>> nut-server also started since it is set to "enabled", but failed to 
>> connect to the driver.  It complains about "no such file or 
>> directory". What file is it looking for?  I ran journalctl on it but 
>> got nothing more than what systemctl status reports.
>>
>> ===========================
>> [root at mythtv ~]# systemctl status nut-driver at cyberpower
>> ● nut-driver at cyberpower.service - Network UPS Tools - device driver 
>> for NUT device 'cyberpower'
>>      Loaded: loaded (/usr/lib/systemd/system/nut-driver at .service; 
>> enabled; preset: disabled)
>>     Drop-In: /etc/systemd/system/nut-driver at .service.d
>>              └─environ.conf
>>              /etc/systemd/system/nut-driver at cyberpower.service.d
>>              └─nut-driver-enumerator-generated-checksum.conf, 
>> nut-driver-enumerator-generated.conf
>>      Active: active (running) since Thu 2022-12-01 05:56:04 CST; 9min ago
>>     Process: 712 ExecStartPre=/usr/bin/systemd-tmpfiles --create 
>> /usr/lib/tmpfiles.d/nut-client.conf (code=exited, stat>
>>     Process: 719 ExecStart=/bin/sh -c 
>> NUTDEV="`/usr/libexec/nut-driver-enumerator.sh 
>> --get-device-for-service cyberpowe>
>>    Main PID: 791 (usbhid-ups)
>>       Tasks: 1 (limit: 9482)
>>      Memory: 2.9M
>>         CPU: 113ms
>>      CGroup: 
>> /system.slice/system-nut\x2ddriver.slice/nut-driver at cyberpower.service
>>              └─791 /usr/sbin/usbhid-ups -a cyberpower
>>
>> Dec 01 05:56:04 mythtv.billgee.local nut-driver at cyberpower[787]: Using 
>> subdriver: CyberPower HID 0.6
>> Dec 01 05:56:04 mythtv.billgee.local nut-driver at cyberpower[787]: 
>> Network UPS Tools - Generic HID driver 0.47 (2.8.0)
>> Dec 01 05:56:04 mythtv.billgee.local nut-driver at cyberpower[787]: USB 
>> communication driver (libusb 1.0) 0.43
>> Dec 01 05:56:04 mythtv.billgee.local nut-driver at cyberpower[787]: 
>> cps_adjust_battery_scale: battery readings will be sca>
>> Dec 01 05:56:04 mythtv.billgee.local nut-driver at cyberpower[719]: 
>> Network UPS Tools - UPS driver controller 2.8.0
>> Dec 01 05:56:04 mythtv.billgee.local usbhid-ups[791]: Startup successful
>>
>> [root at mythtv ~]# systemctl status nut-server
>> ● nut-server.service - Network UPS Tools - power devices information 
>> server
>>      Loaded: loaded (/usr/lib/systemd/system/nut-server.service; 
>> enabled; preset: disabled)
>>      Active: active (running) since Thu 2022-12-01 05:56:07 CST; 9min ago
>>    Main PID: 809 (upsd)
>>       Tasks: 1 (limit: 9482)
>>      Memory: 1000.0K
>>         CPU: 15ms
>>      CGroup: /system.slice/nut-server.service
>>              └─809 /usr/sbin/upsd -F
>>
>> Dec 01 05:56:08 mythtv.billgee.local upsd[809]: listening on ::1 port 
>> 3493
>> Dec 01 05:56:08 mythtv.billgee.local upsd[809]: listening on 127.0.0.1 
>> port 3493
>> Dec 01 05:56:08 mythtv.billgee.local nut-server[809]: /var/run is 
>> world readable
>> Dec 01 05:56:08 mythtv.billgee.local nut-server[809]: Can't connect to 
>> UPS [cyberpower] (usbhid-ups-cyberpower): No suc>
>> Dec 01 05:56:08 mythtv.billgee.local upsd[809]: /var/run is world 
>> readable
>> Dec 01 05:56:08 mythtv.billgee.local upsd[809]: Can't connect to UPS 
>> [cyberpower] (usbhid-ups-cyberpower): No such file>
>> Dec 01 05:56:10 mythtv.billgee.local nut-server[809]: Running as 
>> foreground process, not saving a PID file
>> Dec 01 05:56:10 mythtv.billgee.local upsd[809]: Running as foreground 
>> process, not saving a PID file
>> Dec 01 06:01:08 mythtv.billgee.local nut-server[809]: Can't connect to 
>> UPS [cyberpower] (usbhid-ups-cyberpower): No suc>
>> Dec 01 06:01:08 mythtv.billgee.local upsd[809]: Can't connect to UPS 
>> [cyberpower] (usbhid-ups-cyberpower): No such file>
>> ================================
>>
>>
>>
>> ===============
>> Bill Gee
>>
>> On 11/30/22 21:14, Simon Wilson via Nut-upsuser wrote:
>>> ----- Message from Bill Gee <bgee at campercaver.net> ---------
>>>    Date: Wed, 30 Nov 2022 19:26:46 -0600
>>>    From: Bill Gee <bgee at campercaver.net>
>>> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
>>>      To: nut-upsuser at alioth-lists.debian.net
>>>
>>>
>>>> Hi Simon -
>>>>
>>>> I ran through the steps you gave below.  To quote Gilbert&Sullivan 
>>>> ... "Modified Rapture!"  I suppose I should try a reboot to make 
>>>> sure everything starts properly.
>>>
>>> Not yet with the reboot. Baby steps... :) you have a driver running 
>>> from the service file! Celebrations are in order.
>>>
>>> Did you need to add the environment drop-in file? At which step did 
>>> it work?
>>>
>>>> But first, there is a problem with upsc. Also nut-server complains 
>>>> that it cannot connect to the device.
>>>
>>> Ok, that's next... your comments are wrong way around :) nut-server 
>>> not starting is why upsc doesn't give you anything.
>>>
>>>>
>>>> /run/nut exists and contains two files.
>>>>
>>>> Here are some outputs:
>>>>
>>>> ======================================
>>>> [root at mythtv ~]# journalctl -u nut-driver at cyberpower.service -f
>>>> Nov 30 19:00:20 mythtv.billgee.local systemd[1]: Starting 
>>>> nut-driver at cyberpower.service - Network UPS Tools - device driver 
>>>> for NUT device 'cyberpower'...
>>>> Nov 30 19:00:20 mythtv.billgee.local systemd-tmpfiles[28689]: 
>>>> /usr/lib/tmpfiles.d/nut-client.conf:2: Line references path below 
>>>> legacy directory /var/run/, updating /var/run/nut → /run/nut; please 
>>>> update the tmpfiles.d/ drop-in file accordingly.
>>>
>>> That line is the "noise" error I mentioned. Edit 
>>> /usr/lib/tmpfiles.d/nut-client.conf to read /run/nut, not /var/run/nut
>>>
>>>> Nov 30 19:00:20 mythtv.billgee.local systemd-tmpfiles[28689]: 
>>>> /usr/lib/tmpfiles.d/nut-client.conf:3: Line references path below 
>>>> legacy directory /var/run/, updating /var/run/nut → /run/nut; please 
>>>> update the tmpfiles.d/ drop-in file accordingly.
>>>
>>> Ditto, although you probably don't need line 3 in the file anyway.
>>>
>>>> Nov 30 19:00:21 mythtv.billgee.local nut-driver at cyberpower[28719]: 
>>>> Using subdriver: CyberPower HID 0.6
>>>> Nov 30 19:00:21 mythtv.billgee.local nut-driver at cyberpower[28719]: 
>>>> Network UPS Tools - Generic HID driver 0.47 (2.8.0)
>>>> Nov 30 19:00:21 mythtv.billgee.local nut-driver at cyberpower[28719]: 
>>>> USB communication driver (libusb 1.0) 0.43
>>>> Nov 30 19:00:21 mythtv.billgee.local nut-driver at cyberpower[28719]: 
>>>> cps_adjust_battery_scale: battery readings will be scaled by 2/3
>>>> Nov 30 19:00:21 mythtv.billgee.local usbhid-ups[28769]: Startup 
>>>> successful
>>>> Nov 30 19:00:21 mythtv.billgee.local nut-driver at cyberpower[28691]: 
>>>> Network UPS Tools - UPS driver controller 2.8.0
>>>> Nov 30 19:00:21 mythtv.billgee.local systemd[1]: Started 
>>>> nut-driver at cyberpower.service - Network UPS Tools - device driver 
>>>> for NUT device 'cyberpower'.
>>>>
>>>> [root at mythtv ups]# ll /run/nut
>>>> total 4
>>>> srw-rw---- 1 nut nut 0 Nov 30 19:00 usbhid-ups-cyberpower
>>>> -rw-r--r-- 1 nut nut 6 Nov 30 19:00 usbhid-ups-cyberpower.pid
>>>>
>>>>
>>>> [root at mythtv ups]# systemctl --no-pager --full status nut-server
>>>> ● nut-server.service - Network UPS Tools - power devices information 
>>>> server
>>>>      Loaded: loaded (/usr/lib/systemd/system/nut-server.service; 
>>>> enabled; preset: disabled)
>>>>      Active: active (running) since Wed 2022-11-30 19:06:53 CST; 
>>>> 13min ago
>>>>    Main PID: 28918 (upsd)
>>>>       Tasks: 1 (limit: 9482)
>>>>      Memory: 736.0K
>>>>         CPU: 20ms
>>>>      CGroup: /system.slice/nut-server.service
>>>>              └─28918 /usr/sbin/upsd -F
>>>>
>>>> Nov 30 19:06:53 mythtv.billgee.local nut-server[28918]: /var/run is 
>>>> world readable
>>>> Nov 30 19:06:53 mythtv.billgee.local upsd[28918]: /var/run is world 
>>>> readable
>>>> Nov 30 19:06:53 mythtv.billgee.local upsd[28918]: Can't connect to 
>>>> UPS [cyberpower] (usbhid-ups-cyberpower): Connection refused
>>>> Nov 30 19:06:53 mythtv.billgee.local nut-server[28918]: Can't 
>>>> connect to UPS [cyberpower] (usbhid-ups-cyberpower): Connection refused
>>>> Nov 30 19:06:53 mythtv.billgee.local nut-server[28918]: Running as 
>>>> foreground process, not saving a PID file
>>>> Nov 30 19:06:53 mythtv.billgee.local upsd[28918]: Running as 
>>>> foreground process, not saving a PID file
>>>> Nov 30 19:11:53 mythtv.billgee.local nut-server[28918]: Can't 
>>>> connect to UPS [cyberpower] (usbhid-ups-cyberpower): Connection refused
>>>> Nov 30 19:11:53 mythtv.billgee.local upsd[28918]: Can't connect to 
>>>> UPS [cyberpower] (usbhid-ups-cyberpower): Connection refused
>>>> Nov 30 19:16:53 mythtv.billgee.local nut-server[28918]: Can't 
>>>> connect to UPS [cyberpower] (usbhid-ups-cyberpower): Connection refused
>>>> Nov 30 19:16:53 mythtv.billgee.local upsd[28918]: Can't connect to 
>>>> UPS [cyberpower] (usbhid-ups-cyberpower): Connection refused
>>>>
>>>> [root at mythtv ups]# ps ax | grep ups
>>>>     768 ?        Ss     0:00 /usr/sbin/cupsd -l
>>>>     773 ?        Ss     0:00 sshd: /usr/sbin/sshd -D [listener] 0 of 
>>>> 10-100 startups
>>>>   28769 ?        Ss     0:00 /usr/sbin/usbhid-ups -a cyberpower
>>>>   28918 ?        Ss     0:00 /usr/sbin/upsd -F
>>>>   28929 pts/1    S+     0:00 grep --color=auto ups
>>>>
>>>> [root at mythtv ups]# upsc cyberpower at localhost
>>>> Error: Driver not connected
>>>
>>> upsc won't work without nut-server running, so this is expected based 
>>> on the above failure to start nut-server.
>>>
>>>>
>>>>
>>>
>>> So... next.
>>>
>>> Fix nut-client.conf contents, and make sure that you can start / 
>>> restart the driver as needed with no errors. Set 
>>> nut-driver at cyberpower.service to enabled for autostart, so with ONLY 
>>> the enumerator services and nut-driver at cyberpower.service enabled, 
>>> you should see something like the following for 'systemctl 
>>> list-unit-files | grep -i nut':
>>>
>>> [root at emp80 ups]# systemctl list-unit-files | grep -i nut
>>> nut-driver-enumerator.path                                          
>>>    enabled
>>> nut-driver-enumerator.service                                       
>>>    enabled
>>> nut-driver at .service                                                 
>>>    indirect
>>> nut-monitor.service                                                 
>>>    disabled
>>> nut-server.service                                                  
>>>    disabled
>>> nut-driver.target                                                   
>>>    disabled
>>> nut.target                                                          
>>>    disabled
>>>
>>> Stop any running nut processes, and reboot. On reboot the only thing 
>>> that should autostart is nut-driver at cyberpower.service (from the 
>>> 'indirect' call via nut-driver at .service). upsc will still not work.
>>>
>>> Monitor the driver for a while 'journalctl -u 
>>> nut-driver at cyberpower.service -f' and make sure it is stable and 
>>> stays connected - google searches show some flakiness with some 
>>> cyberpower UPSs.
>>>
>>> Once you are confident that the driver is reliable, starting OK and 
>>> staying up then move on to nut-server.
>>>
>>> I'll check in this evening and we can do some more digging on that.
>>>
>>> Simon
>>>
>>>>
>>>> ===============
>>>> Bill Gee
>>>>
>>>> On 11/30/22 07:21, Simon Wilson via Nut-upsuser wrote:
>>>>> Comments inline.
>>>>>
>>>>> ----- Message from Bill Gee <bgee at campercaver.net> ---------
>>>>>    Date: Wed, 30 Nov 2022 06:04:14 -0600
>>>>>    From: Bill Gee <bgee at campercaver.net>
>>>>> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 
>>>>> upgrade
>>>>>      To: nut-upsuser at alioth-lists.debian.net
>>>>>
>>>>>
>>>>>> Hi Simon --
>>>>>>
>>>>>> Yes, I am pretty sure this is the RedHat packaging problem.  I 
>>>>>> sure hope they get it squared away.  I have only one system using 
>>>>>> nut and that is because all my other systems have APC battery 
>>>>>> backup and run apcupsd. Apcupsd may be old, grey and unmaintained, 
>>>>>> but it Just Works.
>>>>>>
>>>>>> You mention that the STATEPATH line in upsd.conf will override 
>>>>>> other settings.  It does not appear to be the case for me.  The 
>>>>>> only way I could get the driver to run was by setting 
>>>>>> NUT_STATEPATH on the command line.  Perhaps that is an issue with 
>>>>>> the driver and not nut-server?
>>>>>>
>>>>>> In answer to your questions:
>>>>>>
>>>>>> 1) /usr/lib/systemd/system/nut-driver at .service exists.  I have 
>>>>>> made no changes to it so far.  Here are the contents, 
>>>>>> unfortunately line-wrapped by Thunderbird.
>>>>>>
>>>>>> ================================
>>>>>> [root at mythtv system]# grep -v '^#' nut-driver at .service
>>>>>> [Unit]
>>>>>> Description=Network UPS Tools - device driver for %I
>>>>>> After=local-fs.target
>>>>>>
>>>>>>
>>>>>> PartOf=nut-driver.target
>>>>>>
>>>>>>
>>>>>> [Service]
>>>>>> EnvironmentFile=-/etc/ups/nut.conf
>>>>>> SyslogIdentifier=%N
>>>>>> ExecStartPre=-/usr/bin/systemd-tmpfiles --create 
>>>>>> /usr/lib/tmpfiles.d/nut-client.conf
>>>>>> ExecStart=/bin/sh -c 
>>>>>> 'NUTDEV="`/usr/libexec/nut-driver-enumerator.sh 
>>>>>> --get-device-for-service %i`" && [ -n "$NUTDEV" ] || { echo 
>>>>>> "FATAL: Could not find a NUT device section for service unit %i" 
>>>>>> >&2 ; exit 1 ; } ; /usr/sbin/upsdrvctl start "$NUTDEV"'
>>>>>> ExecStop=/bin/sh -c 
>>>>>> 'NUTDEV="`/usr/libexec/nut-driver-enumerator.sh 
>>>>>> --get-device-for-service %i`" && [ -n "$NUTDEV" ] || { echo 
>>>>>> "FATAL: Could not find a NUT device section for service unit %i" 
>>>>>> >&2 ; exit 1 ; } ; /usr/sbin/upsdrvctl stop "$NUTDEV"'
>>>>>> StartLimitInterval=0
>>>>>> Restart=always
>>>>>> RestartSec=15s
>>>>>> Type=forking
>>>>>>
>>>>>> [Install]
>>>>>> WantedBy=nut-driver.target
>>>>>> ===================================
>>>>>
>>>>> OK, so that's the same as mine. It's ExecStartPre task is to create 
>>>>> the pid folder from your answer to the third (unasked) question :) 
>>>>> which is that outlined in /usr/lib/tmpfiles.d/nut-client.conf
>>>>>
>>>>> You have /var/run/nut 0770 root nut - so systemd should ensure that 
>>>>> exists.
>>>>>
>>>>> By the way, having it with "/var/run/nut" will trigger a 'noise' 
>>>>> error about the "/var" path - change it to just be /run/nut in 
>>>>> nut-client.conf.
>>>>>
>>>>> As a test, what happens if you:
>>>>>
>>>>> - make sure nut.conf has MODE=standalone
>>>>> - make sure ALL nut services are stopped, i.e. 'ps -ax | grep ups' 
>>>>> should give you only the grep process as an answer
>>>>> - delete /run/nut folder (it will get re-created automatically)
>>>>> - take /etc/ups/upsd.conf back to have commented out STATEPATH as 
>>>>> distributed in the package
>>>>> - run "systemctl enable nut-driver-enumerator.path 
>>>>> nut-driver-enumerator.service --now" - this will enable and start 
>>>>> the services that monitor ups.conf for changes and then write the 
>>>>> actual driver service file; the second one also runs early in boot 
>>>>> and ensures that the service file exists and is correct.
>>>>> - run 'nut-scanner -U' and copy its output into ups.conf instead of 
>>>>> your current definition with name heading [cyberpower], save and 
>>>>> exit: this will trigger the above enumerators to run and re-do the 
>>>>> nut-driver at cyberpower.service file
>>>>>
>>>>> Based on an out of the box install, you have at this point done 
>>>>> enough that the driver should run (*should*!!!!)
>>>>>
>>>>> - run "journalctl -u nut-driver at cyberpower.service -f" in one 
>>>>> terminal while you run "systemctl start 
>>>>> nut-driver at cyberpower.service" in another - what does journalctl 
>>>>> output?
>>>>>
>>>>> Assuming it does not start (based on what you have said below), 
>>>>> show the messages.
>>>>>
>>>>> If it still does not start as configured above, but you \can/ run 
>>>>> /usr/sbin/usbhid-ups with your environment variables specified like 
>>>>> you had done before, and it *does* run, then do the following steps 
>>>>> to create a systemd drop-in file for the variable, but make the 
>>>>> steps use /run/nut instead of /var/run/nut:  
>>>>> https://bugzilla.redhat.com/show_bug.cgi?id=2127269#c8  (comment 8, 
>>>>> formatted for ease of reading). You want to get back to the 
>>>>> RH/Fedora default of using /run/nut, not /var/state/ups
>>>>>
>>>>>   1. uncomment the "STATEPATH /var/run/nut" as already mentioned
>>>>>   2. create: /etc/systemd/system/nut-driver at .service.d/environ.conf
>>>>>    with these two lines:
>>>>>
>>>>>     [Service]
>>>>>     Environment=NUT_STATEPATH=/var/run/nut
>>>>>
>>>>>   3. and finally do: systemctl daemon-reload
>>>>>
>>>>> ...then try and run systemctl start nut-driver at cyberpower.service 
>>>>> again, while monitoring journalctl.
>>>>>
>>>>>
>>>>> If that does not work - then I'm out of ideas at this point lol... :-D
>>>>>
>>>>> 'set' has nothing BTW on my working system related to nut.
>>>>>
>>>>>>
>>>>>> 2) In /etc/ups/upsd.conf, the original STATEPATH line is
>>>>>>
>>>>>> STATEPATH /var/run/nut
>>>>>>
>>>>>> Right now the original line is commented and I added another line 
>>>>>> to point at /var/state/ups.
>>>>>>
>>>>>> 3) You only asked two questions, but I sense a third might be 
>>>>>> important.  Originally the system had 
>>>>>> /usr/lib/tmpfiles.d/nut-common.conf.  I have modified that file 
>>>>>> and no longer have the original.  I copied that file to 
>>>>>> nut-client.conf, and both have the same contents:
>>>>>>
>>>>>> =======================
>>>>>> # State file (e.g. upsd to driver) and pidfile location for NUT:
>>>>>> D /var/run/nut 0770 root nut - -
>>>>>> X /var/run/nut
>>>>>> ========================
>>>>>>
>>>>>> 4) And one more unasked question!  :-)  When I look at the 
>>>>>> environment variables on the system, I see this:
>>>>>>
>>>>>> ========================
>>>>>> [root at mythtv tmpfiles.d]# set | grep -i nut
>>>>>> _=/etc/ups/nut.conf
>>>>>> ========================
>>>>>>
>>>>>>
>>>>>>
>>>>>> Bill Gee
>>>>>>
>>>>>> On 11/30/22 01:20, Simon Wilson via Nut-upsuser wrote:
>>>>>>> ----- Message from Bill Gee <bgee at campercaver.net> ---------
>>>>>>>    Date: Tue, 29 Nov 2022 19:25:19 -0600
>>>>>>>    From: Bill Gee <bgee at campercaver.net>
>>>>>>> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 
>>>>>>> upgrade
>>>>>>>      To: Jim Klimov <jimklimov+nut at gmail.com>
>>>>>>>      Cc: Arnaud Quette via Nut-upsuser 
>>>>>>> <nut-upsuser at alioth-lists.debian.net>
>>>>>>>
>>>>>>>
>>>>>>>> I got it to run, but what a mess ...
>>>>>>>>
>>>>>>>> Yes, I am running systemctl daemon-reload and systemctl restart 
>>>>>>>> nut-server after each change I make.
>>>>>>>>
>>>>>>>
>>>>>>> Hi Bill,
>>>>>>>
>>>>>>> Drivers and upsd share defaults (see 'man nutupsdrv').
>>>>>>>
>>>>>>> Your original error message ("writepid: fopen 
>>>>>>> /var/run/usbhid-ups-cyberpower.pid: Permission denied") would 
>>>>>>> seem to indicate, same as the Red Hat bug, that your driver's 
>>>>>>> default pid path is /var/run.
>>>>>>>
>>>>>>> The driver by default uses STATEPATH (which can be over-ridden in 
>>>>>>> upsd.conf) to store pid files. The driver .service file is 
>>>>>>> supposed to make sure that path exists by running the 
>>>>>>> ExecStartPre line, which gets its instructions from the 
>>>>>>> referenced ".conf" file from /usr/lib/tmpfiles.d. The .service 
>>>>>>> file then calls 'upsdrvctl start' to start your usbhid-ups 
>>>>>>> driver, as defined in ups.conf. Those all need to align...
>>>>>>>
>>>>>>> 2 x questions:
>>>>>>>
>>>>>>> 1. Without its comments, what are the active lines (as installed, 
>>>>>>> without any changes) in 
>>>>>>> /usr/lib/systemd/system/nut-driver at .service (or wherever that 
>>>>>>> service file is located on your system)?
>>>>>>> 2. in your upsd.conf (also as installed, without any changes), 
>>>>>>> what is the commented out STATEPATH you later mention uncommenting?
>>>>>>>
>>>>>>>> I created /usr/lib/tmpfiles.d/nut-client.conf   The owner is 
>>>>>>>> root:root and permissions are 0644.  The contents are
>>>>>>>>
>>>>>>>> # State file (e.g. upsd to driver) and pidfile location for NUT:
>>>>>>>> D /var/run/nut 0770 root nut - -
>>>>>>>> X /var/run/nut
>>>>>>>>
>>>>>>>> I uncommented the STATEPATH line in /etc/ups/upsd.conf.
>>>>>>>>
>>>>>>>> I created a directory /var/state/ups, set to 777 permissions.  
>>>>>>>> Changed the STATEPATH line in upsd.conf.  No success.
>>>>>>>>
>>>>>>>> I looked at /usr/lib/systemd/system/nut-driver at .service but 
>>>>>>>> could not see any changes to be made.  The bug report at RedHat 
>>>>>>>> mentions that a file identified in ExecStartPre does not exist, 
>>>>>>>> but I could not duplicate.
>>>>>>>>
>>>>>>>> I tried running this as root:
>>>>>>>>
>>>>>>>> NUT_STATEPATH=/var/state/ups NUT_ALTPIDPATH=/var/state/ups 
>>>>>>>> /usr/sbin/usbhid-ups -u nut -g nut -s cyberpower -x port=auto
>>>>>>>>
>>>>>>>> And it works.  I tried it with only one or the other of the two 
>>>>>>>> environment variables, but did not work.  It has to have both.
>>>>>>>>
>>>>>>>> ===============
>>>>>>>> Bill Gee
>>>>>>>>
>>>>>>
>>>>>> _______________________________________________
>>>>>> Nut-upsuser mailing list
>>>>>> Nut-upsuser at alioth-lists.debian.net
>>>>>> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>>>>>
>>>>>
>>>>> ----- End message from Bill Gee <bgee at campercaver.net> -----
>>>>>
>>>>>
>>>>>
>>>>
>>>> _______________________________________________
>>>> Nut-upsuser mailing list
>>>> Nut-upsuser at alioth-lists.debian.net
>>>> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>>>
>>>
>>> ----- End message from Bill Gee <bgee at campercaver.net> -----
>>>
>>>
>>>
>>
>> _______________________________________________
>> Nut-upsuser mailing list
>> Nut-upsuser at alioth-lists.debian.net
>> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
> 
> 
> ----- End message from Bill Gee <bgee at campercaver.net> -----
> 
> 
> 



More information about the Nut-upsuser mailing list