[Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade

Simon Wilson simon at simonandkate.net
Sat Dec 3 03:50:23 GMT 2022


Aha!! Bingo, that resolved the issue for upsd. You may not have picked  
iut up Bill but the new "error" message shows it.

Going back to your message from yesterday, upsd logged this:
Dec 01 10:35:01 mythtv.billgee.local nut-server[3445]: fopen  
/var/run/upsd.pid: No such file or directory
Dec 01 10:35:01 mythtv.billgee.local nut-server[3445]: Could not find  
PID file '/var/run/upsd.pid' to see if previous upsd instance is  
already running!

With an environ.conf setting NUT_STATEPATH upsd logged this:
Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: fopen  
/run/nut/upsd.pid: No such file or directory
Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: Could not find  
PID file '/run/nut/upsd.pid' to see if previous upsd instance is  
already running!

Note the difference - it is now looking in the CORRECT FOLDER  
/run/nut! There is not a pid there, that is fine - that pid check is  
to see if there is a upsd already running. Now it is pointing at a  
folder that nut can write too, that should work as designed. Awesome...


So, I think I'm right in summarising as follows for Bill's situation:

On Fedora / RH packages for 2.8.0

* need to create a /usr/lib/tmpfiles.d/nut-client.conf which contains  
"D /run/nut 0770 root nut - -" to ensure the path exists for services  
which look for it (or edit the service files to point to  
nut-common.conf - but my preference is not to edit service files  
directly to prevent later breaks)

* nut-driver
-- setting/uncommenting STATEPATH in upsd.conf to /var/run/nut or  
/run/nut as the *only* fix does NOT allow driver to start - it still  
tries to go to /var/run (this one I am not 100% sure of from looking  
back through the thread, but I *think* is correct)
-- can be fixed by dropping in a service.d/ drop-in file which sets  
Environment=NUT_STATEPATH=/run/nut

* nut-server
-- setting STATEPATH in upsd.conf to /var/run/nut or /run/nut **does**  
allow server to start (unlike the driver)
-- can also be fixed by dropping in a service.d/ drop-in file which  
sets Environment=NUT_STATEPATH=/run/nut
-- the drop-in is a better fix than uncommenting/setting STATEPATH, as  
it makes upsd look in the correct folder for all of its pid tests



Bill, have I summarised those correctly?

It would seem that using drop-in files to set NUT_STATEPATH for both  
upsdrvctl (nut-driver) and upsd (nut-server) is probably the best  
short-term fix.


What is curious is the variation between packages and OSs though.
- For Bill on F37 all the above fixes were needed - nut-client.conf,  
and both nut-driver and nut-server needed fixing for STATEPATH, with  
two x drop-in files.
- For me on RHEL8.7 (which comes with a working 2.7.4 btw, so I'm my  
own worst enemy there), installing the available 2.8.0-1.el8 package  
was broken, but I only needed to fix the nut-client.conf issue, I did  
not need to uncomment STATEPATH in upsd.conf or add drop-in files to  
set NUT_STATEPATH - and driver and server both start fine, looking in  
/run/nut.

Bill, you should now have a fully working nut stack. I assume you have  
configured users and got nut-monitor working?

Simon

----- Message from Bill Gee <bgee at campercaver.net> ---------
    Date: Fri, 2 Dec 2022 10:19:20 -0600
    From: Bill Gee <bgee at campercaver.net>
Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
      To: nut-upsuser at alioth-lists.debian.net


> Oops, sorry about missing your test two.  I did not read it all the  
> way through.
>
> That test is done, and nut-server starts successfully.  Upsc will  
> give back information about the device.  I did have to run a  
> daemon-reload. It does complain about not finding the PID file.
>
> =================================
> [root at mythtv ups]# cat /etc/systemd/system/nut-server.service.d/environ.conf
> [Service]
> Environment=NUT_STATEPATH=/run/nut
> [root at mythtv ups]# cat /etc/systemd/system/nut-driver at .service.d/environ.conf
> [Service]
> Environment=NUT_STATEPATH=/run/nut
>
> [root at mythtv ups]# systemctl --full --no-pager status nut-server
> ● nut-server.service - Network UPS Tools - power devices information server
>      Loaded: loaded (/usr/lib/systemd/system/nut-server.service;  
> enabled; preset: disabled)
>     Drop-In: /etc/systemd/system/nut-server.service.d
>              └─environ.conf
>      Active: active (running) since Fri 2022-12-02 10:11:18 CST; 9s ago
>    Main PID: 12675 (upsd)
>       Tasks: 1 (limit: 9482)
>      Memory: 732.0K
>         CPU: 5ms
>      CGroup: /system.slice/nut-server.service
>              └─12675 /usr/sbin/upsd -F
>
> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: fopen  
> /run/nut/upsd.pid: No such file or directory
> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: Could not  
> find PID file '/run/nut/upsd.pid' to see if previous upsd instance  
> is already running!
> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: listening on  
> ::1 port 3493
> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: listening on  
> 127.0.0.1 port 3493
> Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: listening on ::1 port 3493
> Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: listening on  
> 127.0.0.1 port 3493
> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: Connected to  
> UPS [cyberpower]: usbhid-ups-cyberpower
> Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: Connected to UPS  
> [cyberpower]: usbhid-ups-cyberpower
> Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: Running as  
> foreground process, not saving a PID file
> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: Running as  
> foreground process, not saving a PID file
> =============================
>
> ===============
> Bill Gee
>
> On 12/2/22 06:24, Simon Wilson via Nut-upsuser wrote:
>> Hi Bill,
>>
>> OK your test 1 and 2 line up with my ask for test 1 :)
>>
>> Have another read of the Test 2 ask please if you can:
>>
>>>> 2. Second test:- copy the edited  
>>>> /etc/systemd/system/nut-driver at .service.d/environ.conf to  
>>>> /etc/systemd/system/nut-server.service.d/environ.conf. So you  
>>>> should at that point have both locations with a file saying
>>>>   [Service]
>>>>   Environment=NUT_STATEPATH=/run/nut
>>>> Then comment out STATEPATH line (back to default) in upsd.conf  
>>>> and restart nut-server - does it still start, and does it still  
>>>> pop a "Could not find PID file '/var/run/upsd.pid'" message? That  
>>>> tests whether the drop-in file is a better, more consistent fix  
>>>> for now (until the packages are resolved). Calling the nut-server  
>>>> process with that variable set for upsd *even before it reads  
>>>> upsd.conf* may remove the first error 'Could not find PID file  
>>>> '/var/run/upsd.pid''
>>
>> Your test 3 and 4 are not quite what is needed, unless you did copy  
>> the environ.conf file into  
>> /etc/systemd/system/nut-server.service.d/ but didn't say so?
>>
>> Could you please copy your nut-driver's environ.conf file to  
>> /etc/systemd/system/nut-server.service.d/ THEN comment out the  
>> STATEPATH line and see if nut-server starts.
>>
>> Why am I asking this>
>> At the moment you are using one fix to resolve the driver (an  
>> environ.conf file) and a different fix to get nut-server going  
>> (STATEPATH). Trying to see if one fix (the environ.conf file fix)  
>> will resolve both driver and server, and in doing so also get rid  
>> of the error message 'Could not find PID file '/var/run/upsd.pid''.
>>
>> Simon
>>
>> ----- Message from Bill Gee <bgee at campercaver.net> ---------
>>    Date: Fri, 2 Dec 2022 06:07:20 -0600
>>    From: Bill Gee <bgee at campercaver.net>
>> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
>>      To: nut-upsuser at alioth-lists.debian.net
>>
>>
>>> Test 1 - I moved the environ.conf file to /tmp.  I ran systemctl  
>>> daemon-reload, then restarted nut-driver at cyberpower.service.   
>>> Results:
>>>
>>> =====================================
>>> [root at mythtv nut-driver at .service.d]# systemctl restart  
>>> nut-driver at cyberpower.service
>>> Job for nut-driver at cyberpower.service failed because the control  
>>> process exited with error code.
>>> See "systemctl status nut-driver at cyberpower.service" and  
>>> "journalctl -xeu nut-driver at cyberpower.service" for details.
>>> [root at mythtv nut-driver at .service.d]# systemctl --full --no-pager  
>>> status nut-driver at cyberpower.service
>>> ● nut-driver at cyberpower.service - Network UPS Tools - device  
>>> driver for NUT device 'cyberpower'
>>>      Loaded: loaded (/usr/lib/systemd/system/nut-driver at .service;  
>>> enabled; preset: disabled)
>>>     Drop-In: /etc/systemd/system/nut-driver at cyberpower.service.d
>>>              └─nut-driver-enumerator-generated-checksum.conf,  
>>> nut-driver-enumerator-generated.conf
>>>      Active: activating (auto-restart) (Result: exit-code) since  
>>> Fri 2022-12-02 05:54:03 CST; 2s ago
>>>     Process: 10732 ExecStartPre=/usr/bin/systemd-tmpfiles --create  
>>> /usr/lib/tmpfiles.d/nut-client.conf (code=exited, status=0/SUCCESS)
>>>     Process: 10733 ExecStart=/bin/sh -c  
>>> NUTDEV="`/usr/libexec/nut-driver-enumerator.sh  
>>> --get-device-for-service cyberpower`" && [ -n "$NUTDEV" ] || {  
>>> echo "FATAL: Could not find a NUT device section for service unit  
>>> cyberpower" >&2 ; exit 1 ; } ; /usr/sbin/upsdrvctl start "$NUTDEV"  
>>> (code=exited, status=1/FAILURE)
>>>         CPU: 80ms
>>> =========================================
>>>
>>> It seems that the nut device driver requires environ.conf to be present.
>>>
>>> Test 2 - I moved environ.conf back to the correct place.  I edited  
>>> the file to use "Environment=NUT_STATEPATH=/run/nut".  I did a  
>>> daemon-reload then started the nut-driver.  It worked - no errors.
>>>
>>> Test 3 - I modified /etc/ups/upsd.conf to comment out the  
>>> STATEPATH line.  I restarted nut-server.service.  It failed.
>>>
>>> ================================
>>> [root at mythtv ups]# systemctl --full --no-pager status nut-server
>>> ● nut-server.service - Network UPS Tools - power devices information server
>>>      Loaded: loaded (/usr/lib/systemd/system/nut-server.service;  
>>> enabled; preset: disabled)
>>>      Active: active (running) since Fri 2022-12-02 06:00:54 CST; 13s ago
>>>    Main PID: 11452 (upsd)
>>>       Tasks: 1 (limit: 9482)
>>>      Memory: 728.0K
>>>         CPU: 5ms
>>>      CGroup: /system.slice/nut-server.service
>>>              └─11452 /usr/sbin/upsd -F
>>>
>>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: listening  
>>> on ::1 port 3493
>>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: listening  
>>> on 127.0.0.1 port 3493
>>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: listening on ::1  
>>> port 3493
>>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: listening on  
>>> 127.0.0.1 port 3493
>>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: /var/run  
>>> is world readable
>>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: /var/run is  
>>> world readable
>>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: Can't connect to  
>>> UPS [cyberpower] (usbhid-ups-cyberpower): No such file or directory
>>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: Can't  
>>> connect to UPS [cyberpower] (usbhid-ups-cyberpower): No such file  
>>> or directory
>>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: Running as  
>>> foreground process, not saving a PID file
>>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: Running as  
>>> foreground process, not saving a PID file
>>> ===================================
>>>
>>> Test 4 - I uncommented the STATEPATH line in upsd.conf.  It points  
>>> to /run/nut.  I restarted nut-server.  Success.
>>>
>>>
>>> ===============
>>> Bill Gee
>>>
>>> On 12/1/22 18:35, Simon Wilson via Nut-upsuser wrote:
>>>> Resending as original was too big for list acceptance.
>>>>
>>>> Hi Bill,
>>>>
>>>> /etc/systemd/system/nut-driver at .service.d/environ.conf sets the  
>>>> nut-driver service's environment variable, such that it sees a  
>>>> workable NUT_STATEPATH of /var/run/nut when upsdrvctl is run by  
>>>> the service, regardless of what is set in upsd.conf, and explains  
>>>> why the driver worked yesterday but upsd didn't.
>>>>
>>>> Tests which may be interesting:
>>>>
>>>> 1. First test:- move nut-driver's environ.conf file to somewhere  
>>>> else temporarily; leave upsd.conf STATEPATH uncommented saying  
>>>> /run/nut; restart nut-driver at cyberpower.service; and see if it  
>>>> runs. This tests to see if it *needs* the drop-in service file  
>>>> *or* will work with only STATEPATH explicitly set in upsd.conf to  
>>>> /run/nut.  If this prevents the driver from working, put the  
>>>> environ.conf file back (but edit it, it should say /run/nut, not  
>>>> /var/run/nut)
>>>>
>>>> 2. Second test:- copy the edited  
>>>> /etc/systemd/system/nut-driver at .service.d/environ.conf to  
>>>> /etc/systemd/system/nut-server.service.d/environ.conf. So you  
>>>> should at that point have both locations with a file saying
>>>>   [Service]
>>>>   Environment=NUT_STATEPATH=/run/nut
>>>> Then comment out STATEPATH line (back to default) in upsd.conf  
>>>> and restart nut-server - does it still start, and does it still  
>>>> pop a "Could not find PID file '/var/run/upsd.pid'" message? That  
>>>> tests whether the drop-in file is a better, more consistent fix  
>>>> for now (until the packages are resolved). Calling the nut-server  
>>>> process with that variable set for upsd *even before it reads  
>>>> upsd.conf* may remove the first error 'Could not find PID file  
>>>> '/var/run/upsd.pid''
>>>>
>>>> And definitely document any changes you make to your setup as  
>>>> subsequent package releases will likely change all of this :)
>>>>
>>>> Couple more comments inline below.
>>>>
>>>> Simon
>>>>
>>>>
>>>> ----- Message from Bill Gee <bgee at campercaver.net> ---------
>>>>    Date: Thu, 1 Dec 2022 16:49:14 -0600
>>>>    From: Bill Gee <bgee at campercaver.net>
>>>> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
>>>>      To: nut-upsuser at alioth-lists.debian.net
>>>>
>>>>> Checking now - There is a file called  
>>>>> /etc/systemd/system/nut-driver at .service.d/environ.conf.  Its  
>>>>> contents are
>>>>>
>>>>> ==========================
>>>>> [root at mythtv nut-driver at .service.d]# ll
>>>>> total 8
>>>>> -rw-r--r-- 1 root root 49 Nov 29 18:14 environ.conf
>>>>> -rw-r--r-- 1 root root 81 Nov 30 18:58  
>>>>> nut-driver-enumerator-generated-checksum.conf
>>>>>
>>>>> [root at mythtv nut-driver at .service.d]# cat environ.conf
>>>>> [Service]
>>>
>>> [snip]
>>>
>>> _______________________________________________
>>> Nut-upsuser mailing list
>>> Nut-upsuser at alioth-lists.debian.net
>>> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>>
>>
>> ----- End message from Bill Gee <bgee at campercaver.net> -----
>>
>>
>>
>
> _______________________________________________
> Nut-upsuser mailing list
> Nut-upsuser at alioth-lists.debian.net
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser


----- End message from Bill Gee <bgee at campercaver.net> -----



-- 
Simon Wilson
M: 0400 12 11 16




More information about the Nut-upsuser mailing list