Hi Simon -

Yes, I think that is a fair summary.  We may have to revisit some of 
this when the next Fedora 37 package for nut is released.  In the 
meantime I am getting what I want, which is a daily report of UPS status 
in logwatch.

I do not use nut-monitor nor do I have any nut users.  Those features 
are not part of my use case.  The system we have been working on is the 
only system I have with nut installed, and it is the only system 
protected by that particular UPS.  All my other systems are protected by 
APC UPSs and run apcupsd.  I suppose someday I need to switch since 
apcupsd has not seen any maintenance for many years.

Thank you for all your help.  I hope this thread lives on somewhere so 
that others can benefit.  I think I saw bits and pieces of it in the 
GitHub posts that Evgeny Klimek made a few days ago.

===============
Bill Gee

On 12/2/22 21:50, Simon Wilson via Nut-upsuser wrote:
> Aha!! Bingo, that resolved the issue for upsd. You may not have picked 
> iut up Bill but the new "error" message shows it.
> 
> Going back to your message from yesterday, upsd logged this:
> Dec 01 10:35:01 mythtv.billgee.local nut-server[3445]: fopen 
> /var/run/upsd.pid: No such file or directory
> Dec 01 10:35:01 mythtv.billgee.local nut-server[3445]: Could not find 
> PID file '/var/run/upsd.pid' to see if previous upsd instance is already 
> running!
> 
> With an environ.conf setting NUT_STATEPATH upsd logged this:
> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: fopen 
> /run/nut/upsd.pid: No such file or directory
> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: Could not find 
> PID file '/run/nut/upsd.pid' to see if previous upsd instance is already 
> running!
> 
> Note the difference - it is now looking in the CORRECT FOLDER /run/nut! 
> There is not a pid there, that is fine - that pid check is to see if 
> there is a upsd already running. Now it is pointing at a folder that nut 
> can write too, that should work as designed. Awesome...
> 
> 
> So, I think I'm right in summarising as follows for Bill's situation:
> 
> On Fedora / RH packages for 2.8.0
> 
> * need to create a /usr/lib/tmpfiles.d/nut-client.conf which contains "D 
> /run/nut 0770 root nut - -" to ensure the path exists for services which 
> look for it (or edit the service files to point to nut-common.conf - but 
> my preference is not to edit service files directly to prevent later 
> breaks)
> 
> * nut-driver
> -- setting/uncommenting STATEPATH in upsd.conf to /var/run/nut or 
> /run/nut as the *only* fix does NOT allow driver to start - it still 
> tries to go to /var/run (this one I am not 100% sure of from looking 
> back through the thread, but I *think* is correct)
> -- can be fixed by dropping in a service.d/ drop-in file which sets 
> Environment=NUT_STATEPATH=/run/nut
> 
> * nut-server
> -- setting STATEPATH in upsd.conf to /var/run/nut or /run/nut **does** 
> allow server to start (unlike the driver)
> -- can also be fixed by dropping in a service.d/ drop-in file which sets 
> Environment=NUT_STATEPATH=/run/nut
> -- the drop-in is a better fix than uncommenting/setting STATEPATH, as 
> it makes upsd look in the correct folder for all of its pid tests
> 
> 
> 
> Bill, have I summarised those correctly?
> 
> It would seem that using drop-in files to set NUT_STATEPATH for both 
> upsdrvctl (nut-driver) and upsd (nut-server) is probably the best 
> short-term fix.
> 
> 
> What is curious is the variation between packages and OSs though.
> - For Bill on F37 all the above fixes were needed - nut-client.conf, and 
> both nut-driver and nut-server needed fixing for STATEPATH, with two x 
> drop-in files.
> - For me on RHEL8.7 (which comes with a working 2.7.4 btw, so I'm my own 
> worst enemy there), installing the available 2.8.0-1.el8 package was 
> broken, but I only needed to fix the nut-client.conf issue, I did not 
> need to uncomment STATEPATH in upsd.conf or add drop-in files to set 
> NUT_STATEPATH - and driver and server both start fine, looking in /run/nut.
> 
> Bill, you should now have a fully working nut stack. I assume you have 
> configured users and got nut-monitor working?
> 
> Simon
> 
> ----- Message from Bill Gee <bgee at campercaver.net> ---------
>     Date: Fri, 2 Dec 2022 10:19:20 -0600
>     From: Bill Gee <bgee at campercaver.net>
> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
>       To: nut-upsuser at alioth-lists.debian.net
> 
> 
>> Oops, sorry about missing your test two.  I did not read it all the 
>> way through.
>>
>> That test is done, and nut-server starts successfully.  Upsc will give 
>> back information about the device.  I did have to run a daemon-reload. 
>> It does complain about not finding the PID file.
>>
>> =================================
>> [root at mythtv ups]# cat 
>> /etc/systemd/system/nut-server.service.d/environ.conf
>> [Service]
>> Environment=NUT_STATEPATH=/run/nut
>> [root at mythtv ups]# cat 
>> /etc/systemd/system/nut-driver at .service.d/environ.conf
>> [Service]
>> Environment=NUT_STATEPATH=/run/nut
>>
>> [root at mythtv ups]# systemctl --full --no-pager status nut-server
>> ● nut-server.service - Network UPS Tools - power devices information 
>> server
>>      Loaded: loaded (/usr/lib/systemd/system/nut-server.service; 
>> enabled; preset: disabled)
>>     Drop-In: /etc/systemd/system/nut-server.service.d
>>              └─environ.conf
>>      Active: active (running) since Fri 2022-12-02 10:11:18 CST; 9s ago
>>    Main PID: 12675 (upsd)
>>       Tasks: 1 (limit: 9482)
>>      Memory: 732.0K
>>         CPU: 5ms
>>      CGroup: /system.slice/nut-server.service
>>              └─12675 /usr/sbin/upsd -F
>>
>> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: fopen 
>> /run/nut/upsd.pid: No such file or directory
>> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: Could not find 
>> PID file '/run/nut/upsd.pid' to see if previous upsd instance is 
>> already running!
>> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: listening on 
>> ::1 port 3493
>> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: listening on 
>> 127.0.0.1 port 3493
>> Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: listening on ::1 
>> port 3493
>> Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: listening on 
>> 127.0.0.1 port 3493
>> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: Connected to 
>> UPS [cyberpower]: usbhid-ups-cyberpower
>> Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: Connected to UPS 
>> [cyberpower]: usbhid-ups-cyberpower
>> Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: Running as 
>> foreground process, not saving a PID file
>> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: Running as 
>> foreground process, not saving a PID file
>> =============================
>>
>> ===============
>> Bill Gee
>>
>> On 12/2/22 06:24, Simon Wilson via Nut-upsuser wrote:
>>> Hi Bill,
>>>
>>> OK your test 1 and 2 line up with my ask for test 1 :)
>>>
>>> Have another read of the Test 2 ask please if you can:
>>>
>>>>> 2. Second test:- copy the edited 
>>>>> /etc/systemd/system/nut-driver at .service.d/environ.conf to 
>>>>> /etc/systemd/system/nut-server.service.d/environ.conf. So you 
>>>>> should at that point have both locations with a file saying
>>>>>   [Service]
>>>>>   Environment=NUT_STATEPATH=/run/nut
>>>>> Then comment out STATEPATH line (back to default) in upsd.conf and 
>>>>> restart nut-server - does it still start, and does it still pop a 
>>>>> "Could not find PID file '/var/run/upsd.pid'" message? That tests 
>>>>> whether the drop-in file is a better, more consistent fix for now 
>>>>> (until the packages are resolved). Calling the nut-server process 
>>>>> with that variable set for upsd *even before it reads upsd.conf* 
>>>>> may remove the first error 'Could not find PID file 
>>>>> '/var/run/upsd.pid''
>>>
>>> Your test 3 and 4 are not quite what is needed, unless you did copy 
>>> the environ.conf file into /etc/systemd/system/nut-server.service.d/ 
>>> but didn't say so?
>>>
>>> Could you please copy your nut-driver's environ.conf file to 
>>> /etc/systemd/system/nut-server.service.d/ THEN comment out the 
>>> STATEPATH line and see if nut-server starts.
>>>
>>> Why am I asking this>
>>> At the moment you are using one fix to resolve the driver (an 
>>> environ.conf file) and a different fix to get nut-server going 
>>> (STATEPATH). Trying to see if one fix (the environ.conf file fix) 
>>> will resolve both driver and server, and in doing so also get rid of 
>>> the error message 'Could not find PID file '/var/run/upsd.pid''.
>>>
>>> Simon
>>>
>>> ----- Message from Bill Gee <bgee at campercaver.net> ---------
>>>    Date: Fri, 2 Dec 2022 06:07:20 -0600
>>>    From: Bill Gee <bgee at campercaver.net>
>>> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
>>>      To: nut-upsuser at alioth-lists.debian.net
>>>
>>>
>>>> Test 1 - I moved the environ.conf file to /tmp.  I ran systemctl 
>>>> daemon-reload, then restarted nut-driver at cyberpower.service.  Results:
>>>>
>>>> =====================================
>>>> [root at mythtv nut-driver at .service.d]# systemctl restart 
>>>> nut-driver at cyberpower.service
>>>> Job for nut-driver at cyberpower.service failed because the control 
>>>> process exited with error code.
>>>> See "systemctl status nut-driver at cyberpower.service" and "journalctl 
>>>> -xeu nut-driver at cyberpower.service" for details.
>>>> [root at mythtv nut-driver at .service.d]# systemctl --full --no-pager 
>>>> status nut-driver at cyberpower.service
>>>> ● nut-driver at cyberpower.service - Network UPS Tools - device driver 
>>>> for NUT device 'cyberpower'
>>>>      Loaded: loaded (/usr/lib/systemd/system/nut-driver at .service; 
>>>> enabled; preset: disabled)
>>>>     Drop-In: /etc/systemd/system/nut-driver at cyberpower.service.d
>>>>              └─nut-driver-enumerator-generated-checksum.conf, 
>>>> nut-driver-enumerator-generated.conf
>>>>      Active: activating (auto-restart) (Result: exit-code) since Fri 
>>>> 2022-12-02 05:54:03 CST; 2s ago
>>>>     Process: 10732 ExecStartPre=/usr/bin/systemd-tmpfiles --create 
>>>> /usr/lib/tmpfiles.d/nut-client.conf (code=exited, status=0/SUCCESS)
>>>>     Process: 10733 ExecStart=/bin/sh -c 
>>>> NUTDEV="`/usr/libexec/nut-driver-enumerator.sh 
>>>> --get-device-for-service cyberpower`" && [ -n "$NUTDEV" ] || { echo 
>>>> "FATAL: Could not find a NUT device section for service unit 
>>>> cyberpower" >&2 ; exit 1 ; } ; /usr/sbin/upsdrvctl start "$NUTDEV" 
>>>> (code=exited, status=1/FAILURE)
>>>>         CPU: 80ms
>>>> =========================================
>>>>
>>>> It seems that the nut device driver requires environ.conf to be 
>>>> present.
>>>>
>>>> Test 2 - I moved environ.conf back to the correct place.  I edited 
>>>> the file to use "Environment=NUT_STATEPATH=/run/nut".  I did a 
>>>> daemon-reload then started the nut-driver.  It worked - no errors.
>>>>
>>>> Test 3 - I modified /etc/ups/upsd.conf to comment out the STATEPATH 
>>>> line.  I restarted nut-server.service.  It failed.
>>>>
>>>> ================================
>>>> [root at mythtv ups]# systemctl --full --no-pager status nut-server
>>>> ● nut-server.service - Network UPS Tools - power devices information 
>>>> server
>>>>      Loaded: loaded (/usr/lib/systemd/system/nut-server.service; 
>>>> enabled; preset: disabled)
>>>>      Active: active (running) since Fri 2022-12-02 06:00:54 CST; 13s 
>>>> ago
>>>>    Main PID: 11452 (upsd)
>>>>       Tasks: 1 (limit: 9482)
>>>>      Memory: 728.0K
>>>>         CPU: 5ms
>>>>      CGroup: /system.slice/nut-server.service
>>>>              └─11452 /usr/sbin/upsd -F
>>>>
>>>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: listening on 
>>>> ::1 port 3493
>>>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: listening on 
>>>> 127.0.0.1 port 3493
>>>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: listening on ::1 
>>>> port 3493
>>>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: listening on 
>>>> 127.0.0.1 port 3493
>>>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: /var/run is 
>>>> world readable
>>>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: /var/run is world 
>>>> readable
>>>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: Can't connect to 
>>>> UPS [cyberpower] (usbhid-ups-cyberpower): No such file or directory
>>>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: Can't 
>>>> connect to UPS [cyberpower] (usbhid-ups-cyberpower): No such file or 
>>>> directory
>>>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: Running as 
>>>> foreground process, not saving a PID file
>>>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: Running as 
>>>> foreground process, not saving a PID file
>>>> ===================================
>>>>
>>>> Test 4 - I uncommented the STATEPATH line in upsd.conf.  It points 
>>>> to /run/nut.  I restarted nut-server.  Success.
>>>>
>>>>
>>>> ===============
>>>> Bill Gee
>>>>
>>>> On 12/1/22 18:35, Simon Wilson via Nut-upsuser wrote:
>>>>> Resending as original was too big for list acceptance.
>>>>>
>>>>> Hi Bill,
>>>>>
>>>>> /etc/systemd/system/nut-driver at .service.d/environ.conf sets the 
>>>>> nut-driver service's environment variable, such that it sees a 
>>>>> workable NUT_STATEPATH of /var/run/nut when upsdrvctl is run by the 
>>>>> service, regardless of what is set in upsd.conf, and explains why 
>>>>> the driver worked yesterday but upsd didn't.
>>>>>
>>>>> Tests which may be interesting:
>>>>>
>>>>> 1. First test:- move nut-driver's environ.conf file to somewhere 
>>>>> else temporarily; leave upsd.conf STATEPATH uncommented saying 
>>>>> /run/nut; restart nut-driver at cyberpower.service; and see if it 
>>>>> runs. This tests to see if it *needs* the drop-in service file *or* 
>>>>> will work with only STATEPATH explicitly set in upsd.conf to 
>>>>> /run/nut.  If this prevents the driver from working, put the 
>>>>> environ.conf file back (but edit it, it should say /run/nut, not 
>>>>> /var/run/nut)
>>>>>
>>>>> 2. Second test:- copy the edited 
>>>>> /etc/systemd/system/nut-driver at .service.d/environ.conf to 
>>>>> /etc/systemd/system/nut-server.service.d/environ.conf. So you 
>>>>> should at that point have both locations with a file saying
>>>>>   [Service]
>>>>>   Environment=NUT_STATEPATH=/run/nut
>>>>> Then comment out STATEPATH line (back to default) in upsd.conf and 
>>>>> restart nut-server - does it still start, and does it still pop a 
>>>>> "Could not find PID file '/var/run/upsd.pid'" message? That tests 
>>>>> whether the drop-in file is a better, more consistent fix for now 
>>>>> (until the packages are resolved). Calling the nut-server process 
>>>>> with that variable set for upsd *even before it reads upsd.conf* 
>>>>> may remove the first error 'Could not find PID file 
>>>>> '/var/run/upsd.pid''
>>>>>
>>>>> And definitely document any changes you make to your setup as 
>>>>> subsequent package releases will likely change all of this :)
>>>>>
>>>>> Couple more comments inline below.
>>>>>
>>>>> Simon
>>>>>
>>>>>
>>>>> ----- Message from Bill Gee <bgee at campercaver.net> ---------
>>>>>    Date: Thu, 1 Dec 2022 16:49:14 -0600
>>>>>    From: Bill Gee <bgee at campercaver.net>
>>>>> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 
>>>>> upgrade
>>>>>      To: nut-upsuser at alioth-lists.debian.net
>>>>>
>>>>>> Checking now - There is a file called 
>>>>>> /etc/systemd/system/nut-driver at .service.d/environ.conf.  Its 
>>>>>> contents are
>>>>>>
>>>>>> ==========================
>>>>>> [root at mythtv nut-driver at .service.d]# ll
>>>>>> total 8
>>>>>> -rw-r--r-- 1 root root 49 Nov 29 18:14 environ.conf
>>>>>> -rw-r--r-- 1 root root 81 Nov 30 18:58 
>>>>>> nut-driver-enumerator-generated-checksum.conf
>>>>>>
>>>>>> [root at mythtv nut-driver at .service.d]# cat environ.conf
>>>>>> [Service]
>>>>
>>>> [snip]
>>>>
>>>> _______________________________________________
>>>> Nut-upsuser mailing list
>>>> Nut-upsuser at alioth-lists.debian.net
>>>> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>>>
>>>
>>> ----- End message from Bill Gee <bgee at campercaver.net> -----
>>>
>>>
>>>
>>
>> _______________________________________________
>> Nut-upsuser mailing list
>> Nut-upsuser at alioth-lists.debian.net
>> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
> 
> 
> ----- End message from Bill Gee <bgee at campercaver.net> -----
> 
> 
> 