[Nut-upsuser] How to change shutdown notification threshold on Fortron UPS Champs (blazer_usb)?
Pavel Hofman
pavel.hofman at ivitera.com
Fri Sep 2 12:27:43 BST 2022
Dne 29. 08. 22 v 12:53 Jim Klimov napsal(a):
> The debug_min option is part of NUT 2.8.0, and your driver "screenshot"
> was from 2.7.4.
>
> With older releases, you should manually ensure several `-D` options on
> the driver command line to increase verbosity.
Hi Jim,
Thanks a lot. Is there any way to tell upsdrvctl to add the -D option
when it starts the specific driver on that older version? I tried adding
-D to upsdrvctl (in its systemd unit), to no avail.
Thanks,
Pavel.
>
> On Mon, Aug 29, 2022, 10:18 Pavel Hofman <pavel.hofman at ivitera.com
> <mailto:pavel.hofman at ivitera.com>> wrote:
>
>
>
> Dne 19. 08. 22 v 12:49 Pavel Hofman napsal(a):
> > Hi,
> >
> > I am trying to configure the shutdown threshold for Fortron UPS
> Champs.
> >
> > upsc reports:
> >
> > Init SSL without certificate database
> > battery.charge: 100
> > battery.voltage: 55.20
> > battery.voltage.high: 52.00
> > battery.voltage.low: 41.60
> > battery.voltage.nominal: 48.0
> > device.mfr:
> > device.model: WPHVT2K0
> > device.type: ups
> > driver.name <http://driver.name>: blazer_usb
> > driver.parameter.pollinterval: 2
> > driver.parameter.port: /dev/hidraw2
> > driver.parameter.synchronous: no
> > driver.version: 2.7.4
> > driver.version.internal: 0.12
> > input.current.nominal: 8.0
> > input.frequency: 50.0
> > input.frequency.nominal: 50
> > input.voltage: 234.5
> > input.voltage.fault: 234.5
> > input.voltage.nominal: 230
> > output.voltage: 229.7
> > ups.beeper.status: enabled
> > ups.delay.shutdown: 30
> > ups.delay.start: 180
> > ups.firmware: 01060.07
> > ups.load: 46
> > ups.mfr:
> > ups.model: WPHVT2K0
> > ups.productid: 5161
> > ups.status: OL
> > ups.temperature: 26.3
> > ups.type: online
> > ups.vendorid: 0665
> >
> >
> > Please note there is no battery.charge.low, the battery.charge is
> > provided by the blazer_usb driver
> >
> https://networkupstools.org/docs/man/blazer_usb.html#_notes_for_the_previous_user_of_megatec_drivers
> <https://networkupstools.org/docs/man/blazer_usb.html#_notes_for_the_previous_user_of_megatec_drivers>
>
> >
> >
> > I tried to configure override.battery.charge.low for the device in
> > ups.conf (after ignorelb), nothing reported in upsc.
> >
> > I do not need any times, just being able to set charge level or
> voltage
> > level at which NUTS will issue the shutdown command to my servers
> > connected to the UPS a communicating with the nuts-server (their
> > shutdown takes a while). I could not find any info how to do that
> apart
> > of
> >
> https://github.com/networkupstools/nut/issues/561#issuecomment-398791357
> <https://github.com/networkupstools/nut/issues/561#issuecomment-398791357>
>
> > which did not work for me (no battery.charge.low info appeared in
> upcs
> > after this setting and reloading all nuts-related daemons (server,
> > client, monitor), nothing found in the logs.
> >
> > Thank you very much for any help or hints.
> >
>
> I tried to increase debug_min = 10 in non-driver/global section of
> ups.conf and no extra logs appeared in /var/log/syslog. Neither did
> with
> debug_min = 0 or 1, no effect. I do not know if the number should be
> high or low, could not find it in any docs online.
>
> Thanks a lot,
>
> Pavel.