[Nut-upsuser] Synthesize low batt (LB) fron SNMP UPS which does not support this?
Greg Troxel
gdt at lexort.com
Fri May 19 14:11:51 BST 2023
My $0.02:
LB is baked in to nut behavior. So if a UPS doesn't report LB, then
it makes sense to synthesize it. Synthetic LB is the cleanest fix at
the earlier processing point.
One could have a config that is basically
synthetic-lowbatt-percent
that generates LB if (as Jim says) on battery, not calibrating, and
batt% <= that.
One could have a similar config
synthetic-lowbatt-voltage
same thing except voltage. The mapping from voltage and current (and
history) to % is difficult, but this lets people have another option
and is easy to implement.
I think it makes sense to allow this even when the UPS will report LB.
I want to shut down earlier than max runtime to be nicer to the
battery. Once the outage is over an hour it's usually 4, for me.
It might make sense to also be able to ignore UPS-provided LB via
ignore-hardware-lb: true
but probably there is little need as most UPS units seem to throw LB
later than wanted vs early. But again easy.
Yes, this could be in upsmon, but that's not synthetic LB, it's
choosing to shutdown if battery is below X.
We should be clear on "critical" vs "LB" and clean up the language to
be consistent.
Beware that I'm a bit fuzzy on details beyond my comments and even
some on things I commented on, so take them as such.