[Nut-upsuser] Synthesize low batt (LB) fron SNMP UPS which does not support this?
Carsten Aulbert
carsten.aulbert at aei.mpg.de
Mon May 22 10:48:52 BST 2023
Hi all,
On 5/19/23 15:11, Greg Troxel wrote:
> LB is baked in to nut behavior. So if a UPS doesn't report LB, then
> it makes sense to synthesize it. Synthetic LB is the cleanest fix at
> the earlier processing point.
I fully agree and thus this ought to be done in/near uspd IMHO. I
glanced over the server/ directory and was not sure where even to begin
hooking this in. Should this be directly in upsd (upsd.c) or rather
in/near the driver level (driver/main.c)?
>
> Yes, this could be in upsmon, but that's not synthetic LB, it's
> choosing to shutdown if battery is below X.
Yeah, this should be independent and fully on the client side (and thus
upsmon) where each client can choose how to react to a UPS on battery.
> We should be clear on "critical" vs "LB" and clean up the language to
> be consistent.
For upsmon, I would stay with critical as this is already mentioned in
upsmon(8) and I guess "LB" could stay for the server part as each user
could decide whether she wants to rely on LB from the UPS itself or on
the self-defined override.
> Beware that I'm a bit fuzzy on details beyond my comments and even
> some on things I commented on, so take them as such.
Same here, quite at a loss what is handled where on the server and
always low on time due to other projects/tasks.
Cheers and any pointers appreciated!
Carsten
--
Dr. Carsten Aulbert, Max Planck Institute for Gravitational Physics,
Callinstraße 38, 30167 Hannover, Germany, Phone +49 511 762 17185
-------------- next part --------------
A non-text attachment was scrubbed...
Name: smime.p7s
Type: application/pkcs7-signature
Size: 4827 bytes
Desc: S/MIME Cryptographic Signature
URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20230522/d77291d4/attachment.bin>
More information about the Nut-upsuser
mailing list