[Nut-upsuser] CyberPower CST150UC: Question re: battery.runtime.low configuration settings

Charles Lepple clepple at gmail.com
Wed Apr 24 12:19:57 BST 2024


> On Apr 23, 2024, at 3:51 PM, tim.o via Nut-upsuser <nut-upsuser at alioth-lists.debian.net> wrote:
> 
> The value changed to battery.runtime.low: 16, instead of 3600. I don't understand why, because executing the command resulted in SUCCESS.

Unfortunately, the SUCCESS response is just saying that upsrw was able to send that request to upsd (i.e. the username/password were correct). As you saw, the real proof is in what you read back from upsc.

Have you tried any other values? 3600 is hex 0xe10, and 16 is 0x10, so it is quite possible the UPS is using an 8-bit field to store battery.runtime.low. I'm guessing the maximum is going to be 255.

This is not entirely surprising - we have a GitHub issue label specific to CPS for issues with their USB HID protocol implementation.

-- 