[Nut-upsuser] CyberPower CST150UC: Question re: battery.runtime.low configuration settings

tim.o carukia at live.com
Wed Apr 24 20:45:05 BST 2024


> Unfortunately, the SUCCESS response is just saying that upsrw was able to send that request to upsd (i.e. the username/password were correct). As you saw, the real proof is in what you read back from upsc.
Ah, gotcha.

> Have you tried any other values? 3600 is hex 0xe10, and 16 is 0x10, so it is quite possible the UPS is using an 8-bit field to store battery.runtime.low. I'm guessing the maximum is going to be 255.
I am not sure I follow. Would you mind unpacking this for me?
When I initially issued 'upsrw' this is what was returned. What does the 
value '300' indicate, if not seconds; and attempting to change it to 
'3600' sets it two '16'. Is this what you mean when you're referring to 
a '8-bit field'?

upsrw CST150UC
             [battery.runtime.low]
             Remaining battery runtime when UPS switches to LB (seconds)
             Type: STRING
             Maximum length: 10
             Value: 300

In my research I found that editing 'ups.conf' may allow to change the 
'battery.runtime.low' as well, but I haven't tested it yet. I figured 
using the supported UPS variables may be the way to go first.

mcedit /etc/nut/ups.conf

[cyberpower]
     driver = usbhid-ups
     port = auto
     desc = "ups"
     offdelay = 20
     ondelay = 0
     ignorelb
     override.battery.runtime.low = 20
     override.battery.runtime.low = 40
     pollinterval = 15

Thank you, Charles

On 4/24/24 04:19, Charles Lepple wrote:
>> On Apr 23, 2024, at 3:51 PM, tim.o via Nut-upsuser<nut-upsuser at alioth-lists.debian.net>  wrote:
>>
>> The value changed to battery.runtime.low: 16, instead of 3600. I don't understand why, because executing the command resulted in SUCCESS.
> Unfortunately, the SUCCESS response is just saying that upsrw was able to send that request to upsd (i.e. the username/password were correct). As you saw, the real proof is in what you read back from upsc.
>
> Have you tried any other values? 3600 is hex 0xe10, and 16 is 0x10, so it is quite possible the UPS is using an 8-bit field to store battery.runtime.low. I'm guessing the maximum is going to be 255.
>
> This is not entirely surprising - we have a GitHub issue label specific to CPS for issues with their USB HID protocol implementation.
>