[Nut-upsuser] UPS not Shutting Down
Roger Price
roger at rogerprice.org
Sun Jun 2 17:14:02 BST 2024
On Sun, 2 Jun 2024, chribonn at duck.com wrote:
> # if the charge is less than 75 percent trigger a LB status
> override.battery.charge.low = 75
> # if the remaining charge is less than 1200s (20 minutes) trigger a low battery status
> override.battery.runtime.low = 1200
> # wait 5 minutes for ups to power off
> override.ups.delay.shutdown = 300
> # Could offdelay act as an ovverride for override.ups.delay.shutdown?
> offdelay = 300
> Is the comment about offdelay (in red) correct / can this line be eliminated?.
My understanding is "yes", but others may have deeper knowledge.
In general you don't need any "override" variables. See the comment about
override.<variable> at https://networkupstools.org/docs/man/ups.conf.html
> Can the UPS automatically come online one the ondelay passes -- I presume this
> can vary with the UPS brand and NUT driver.
The UPS will be online and recharging once wall power returns, but will not feed
power to the server until ondelay passes.
> ---------------------------------------------- My goal is to tell a story of
> how Proxmox with Windows Guests can be configured with NUT so that if there is
> a power failure. I hope to design this such that others can add alternative
> methods and update HowTo modules for each step.
> I feel I am at the tail end of a long long learning curve and would like to
> document the story of how one should go abo
Not only will this be useful as your own documentation, but also useful for many
others.
Roger