[Nut-upsuser] Cyber Power System CP1500 AVR UPS: changing battery.charge.low value

Charles Lepple clepple at gmail.com
Fri Mar 8 12:07:14 GMT 2024


On Mar 4, 2024, at 3:23 PM, Alan C. Bonnici via Nut-upsuser <nut-upsuser at alioth-lists.debian.net> wrote:
> 
> I would like to push up the shutdown process to initiate when the ups is at 50% rather than 10% mainly because there is a need to down other servers.
> 

Some UPSes have a limited range for adjusting the LB threshold, or do not save the threshold in non-volatile storage. To work around this, you can use the "ignorelb" setting to ignore the UPS low battery indication, and have the driver generate the LB flag based on the UPS reported runtime or charge level:

https://networkupstools.org/docs/man/ups.conf.html#_ups_fields

-- 
Charles Lepple
clepple at gmail




More information about the Nut-upsuser mailing list