[Nut-upsuser] Cyber Power System CP1500 AVR UPS: changing battery.charge.low value
Roger Price
roger at rogerprice.org
Fri Mar 8 12:07:21 GMT 2024
On Mon, 4 Mar 2024, Alan C. Bonnici via Nut-upsuser wrote:
> Platform: Proxmox VE 8.1.4
> NUT version: Network UPS Tools upsstats 2.8.0
>
> I configured Proxmox and I can pull up the UPS stats.
> Typing in `upsrw -l cyberpower at localhost` I get the following:
>
> [battery.charge.low]
> Remaining battery level when UPS switches to LB (percent)
> Type: STRING
> Maximum length: 10
> Value: 10
>
> When I type `upsrw -s battery.charge.low=50 -u admin -p 12345678 cyberpower at localhost` Iget an OK, yet after rebooting the setting is
> still 10.
>
> I would like to push up the shutdown process to initiate when the ups is at 50% rather than 10% mainly because there is a need to down
> other servers.
>
> Is there a work around?
Perhaps setting lowbatt = 50 in ups.conf would help.
Roger Any comment to the list. Thanks.