[Nut-upsuser] New Cyber Power UPS
Mike
the.lists at mgm51.com
Wed Mar 12 16:14:21 GMT 2025
On 3/11/2025 7:46 AM, Greg Troxel via Nut-upsuser wrote:
> Mike via Nut-upsuser <nut-upsuser at alioth-lists.debian.net> writes:
>
>> The new one is a Cyber Power CP1500AVRLCD3
>
> Today I don't need a new UPS but I like to be ready.
>
> Thus I have a few questions/comments, if you are inclined and of course
> feel entirely free to not answer or to answer what you can without
> effort.
>
> It looks like this has a UL 1776 approval:
> https://www.bhphotovideo.com/c/product/1751073-REG/cyberpower_cp1500avrlcd3_1500va_900w_line_interactive_lcd.html/specs
> Is that right?
Yes, there is the UL seal on the label on the bottom of the UPS.
>
> It is configured for 10 as battery.charge.low and 20 for warning. I
> would be tempted to increase those to 20/40, depending on your real
> goals. But I don't know how real they are anyway.
>
> I am most concerned about safety, reliability, and runtime at around
> 100 VA, as I am thinking about router, switch and POE. (For desktops,
> I'm ok with a plan of powering down once power has been out for a
> minute.)
> > Your load value is 12, and I'm guessing that's 12% of 900 VA
which is
> 108 VA.
108VA sounds abut right. It is powering two servers
>
> It looks like this takes 2 batteries, 12V 9 Ah. Do you think that's
> right?
I know it takes two batteries, I don't know their rating.
>
> In theory that's 216 Wh as a 'not to exceed' value. The specs about
> say 108 Vah (a typo for VAh, but that doesn't really make sense as VA
> is an AC concept). Assuming 100 Wh usable from the battery (which I
> guessed before finding the above specs), and 75% efficiency (?), this
> should last maybe 45 minutes. Specs claim 12 minutes at half load.
> The runtime shown by nut is 4750. Lots of conflicting information.
I have NUT configured to shut one server down after 10 minutes, the
other after 30 minutes, then NUT shuts down the UPS. So I don't run the
batteries longer than that.
>
> Have you put a power meter on your load (to read VA and W) to check
> the "12"?
I haven't checked the power draw with a wattmeter.
> Have you done a simulated failure test to obtaind the
> actual runtime, and even better to log the battery voltage and claimed
> runtime during the rundown?
I have simulated failure, but only with the time constraints mentioned
above.
> This is a little rough on the batteries
> but my take is that if batteries aren't tested once a year, you really
> don't know if they are ok, and once a year testing isn't what kills
> them.
I (or the power company :) ) usually test the UPS a couple times a year.
>
> It seems like the trend is to have more and more output power from the
> same 2 medium batteries. (At work long ago I had an APC 1500 VA that
> had 2 12V 18Ah batteries.) I wonder if the efficiency at 100 VA is
> as ok as it used to be. To me "runtime at 100 VA" is the big thing,
> but the specs are price and max power/VA.
>
> Did you think about the sine-wave version CP1500PFCLCD?
Never looked at it.
Hope this helped.
More information about the Nut-upsuser
mailing list