[Nut-upsuser] Weird usbhid-ups issue with Eaton 9PX1500RT-L
    Jim Klimov 
    jimklimov+nut at gmail.com
       
    Tue Mar 25 08:06:35 GMT 2025
    
    
  
The dump you did collect has 1156 bytes, so one of the driver's guesses
about size was correct - although it picked another.
I haven't seen reports in 4K range, either (was surprised that this device
has so much to say?)
Apparently not only NUT has some unlucky heuristic picking the way to talk
to the device, so figuring out what usbhid-dump does would be useful, and
eventual PRs for NUT would be welcome.
As a local hotfix, you can build custom NUT and disable the other code path
which picks the bigger descriptor. I don't remember OTOH if there is a
config toggle for that to use in an existing binary build.
Jim
On Tue, Mar 25, 2025 at 3:44 AM Keith Amidon <camalot at picnicpark.org> wrote:
> I previously had NUT working correctly with a CyberPower UPS. In a bid to
> improve the longevity of the batteries and the reliability of power
> reporting, I replaced it with an Eaton 9PX1500RT-L. With the the ups
> driver is not coming up with the Eaton and best I can figure out it is
> because it finds it but then gets an error while reading information
> from it.
>
> This is on current unstable NixOS, using the packaged version of NUT,
> which is 2.8.2.
>
> My ups.conf is pretty simple:
>
> ------- start of ups.conf
> maxstartdelay = 45
>
> [Garage-Eaton9PX1500L]
>       driver = usbhid-ups
>       port = auto
>       desc = "UPS for garage systems"
>       sdorder = 0
>       serial = PG00R42NT5
> ------- end of ups.conf
>
> I have tried without the "serial" line as will. To debug, I'm running
> upsdrvctl manually as follows:
>
> NUT_CONFPATH=/etc/nut NUT_STATEPATH=/var/lib/nut/ upsdrvctl -DDD -d -u root start
>
> I'll paste the full output below, but I think the key information is
> the section when matching the UPS device:
>
> ----- start of extract of upsdrvctl debug output
>    0.039924     [D2] Checking device 2 of 14 (0463/FFFF)
>    0.061508     [D2] - VendorID: 0463
>    0.061520     [D2] - ProductID: ffff
>    0.061524     [D2] - Manufacturer: EATON
>    0.061528     [D2] - Product: Eaton 9PX
>    0.061532     [D2] - Serial Number: PG00R42NT5
>    0.061536     [D2] - Bus: 007
>    0.061540     [D2] - Bus Port: 004
>    0.061544     [D2] - Device: 002
>    0.061548     [D2] - Device release number: 0202
>    0.061564     [D2] Trying to match device
>    0.061569     [D2] match_function_subdriver (non-SHUT mode): matching a device...
>    0.061575     [D3] match_function_regex: matching a device...
>    0.061606     [D2] Device matches
>    0.061611     [D2] Reading configuration descriptor 1 of 1
>    0.061620     [D3] libusb_kernel_driver_active() returned 0: Success
>    0.061639     [D2] Claimed interface 0 successfully
>    0.061646     [D3] nut_usb_set_altinterface: skipped libusb_set_interface_alt_setting(udev, 0, 0)
>    0.065483     [D2] Retrieved HID descriptor (expected 9, got 9)
>    0.065498     [D3] HID descriptor, method 1: (9 bytes) => 09 21 10 01 21 01 22 5f 12
>    0.065502     [D3] HID descriptor length (method 1) 4703
>    0.065508     [D3] HID descriptor, method 2: (9 bytes) => 09 21 10 01 21 01 22 84 04
>    0.065513     [D3] HID descriptor length (method 2) 1156
>    0.065518     [D1] Eaton device v2.02. Using full report descriptor
>    0.065524     [D2] Warning: two different HID descriptors retrieved (Reportlen = 4703 vs. 1156)
>    0.065528     [D2] HID descriptor length 4703
>    0.065541     [D2] Unable to get Report descriptor: Resource temporarily unavailable
> ----- end of extract of upsdrvctl debug output
>
> After this it starts checking the next device. Notice the two HID
> descriptors reported and the error:
>
> Unable to get Report descriptor: Resource temporarily unavailable
>
> After this the next line is about checking the next device. I also
> get errors when dumping detailed information about the device using lsusb:
>
> ------- start of output of 'lsusb -d 0463:ffff -vv >/dev/null'
> can't get debug descriptor: Resource temporarily unavailable
> ------- end of output of 'lsusb -d 0463:ffff -vv >/dev/null'
>
> I omitted standard output because a lot of information is dumped. If it is useful
> I can provide it.
>
> However, I can read a descriptor using usbhid-dump:
>
> -------- start of 'usbhid-dump -a 7:2' output
> 007:002:000:DESCRIPTOR         1742839889.022109
>  05 84 09 04 A1 01 09 10 A1 00 09 12 A1 00 06 FF
>  FF 09 90 85 21 75 08 95 01 15 00 26 FF 00 65 00
>  55 00 B1 83 05 85 09 83 85 23 75 20 27 FF FF FF
>  7F 67 01 10 10 00 B1 83 05 84 09 02 A1 02 09 60
>  85 27 75 08 26 FF 00 65 00 B1 83 09 60 81 83 C0
>  06 FF FF 09 EC 85 26 B1 83 05 84 09 58 85 24 B1
>  82 06 FF FF 09 40 85 26 B1 83 C0 05 84 09 14 A1
>  00 06 FF FF 09 6B B1 83 05 84 09 02 A1 02 06 FF
>  FF 09 79 85 27 B1 83 09 79 81 83 05 84 09 62 B1
>  83 09 62 81 83 09 6D B1 83 09 6D 81 83 06 FF FF
>  09 74 B1 83 09 74 81 83 09 75 B1 83 09 75 81 83
>  C0 09 E9 85 26 B1 83 C0 C0 09 E0 85 FF 95 FF 27
>  FF FF FF 7F B1 82 09 E0 85 FE 95 0A B1 82 05 84
>  09 1E A1 81 09 42 85 14 95 01 26 FF 00 66 01 F0
>  B1 83 09 40 67 21 D1 F0 00 55 07 B1 83 09 1F 85
>  0B 65 00 55 00 B1 03 C0 09 1E A1 84 09 44 85 74
>  75 10 27 FF FF 00 00 66 21 D1 55 07 B1 83 09 43
>  B1 83 09 42 85 0D 75 08 26 FF 00 66 01 F0 55 00
>  B1 82 09 40 85 72 75 10 27 FF FF 00 00 67 21 D1
>  F0 00 55 07 B1 82 09 1F 85 0B 75 08 26 FF 00 65
>  00 55 00 B1 03 C0 09 18 A1 00 09 20 A1 81 C0 09
>  20 A1 82 C0 09 20 A1 83 C0 C0 09 16 A1 00 06 FF
>  FF 09 12 A1 00 05 84 09 36 85 42 75 10 27 FF FF
>  00 00 67 01 00 01 00 B1 83 C0 06 FF FF 09 41 85
>  4A 75 08 26 FF 00 65 00 B1 03 09 14 A1 00 05 84
>  09 36 85 42 75 10 27 FF FF 00 00 67 01 00 01 00
>  B1 83 C0 09 1C A1 00 09 34 66 21 D1 55 07 B1 83
>  09 33 B1 83 09 31 67 01 00 10 00 55 0F B1 83 06
>  FF FF 09 86 75 08 26 FF 00 65 00 55 00 B1 83 05
>  84 09 32 75 10 27 FF FF 00 00 66 01 F0 55 0F B1
>  83 06 FF FF 09 69 75 08 26 FF 00 65 00 55 00 B1
>  83 05 84 09 30 75 10 27 FF FF 00 00 67 21 D1 F0
>  00 55 06 B1 83 C0 06 FF FF 09 16 A1 00 05 84 09
>  36 67 01 00 01 00 55 00 B1 83 C0 06 FF FF 09 40
>  85 4A 75 08 26 FF 00 65 00 B1 03 C0 05 84 09 24
>  A1 00 06 FF FF 09 22 A1 00 09 98 85 07 75 10 27
>  FF FF 00 00 B1 83 09 97 75 20 27 FF FF FF 7F 66
>  01 10 B1 83 C0 05 85 09 8D 85 0C 75 08 26 FF 00
>  65 00 B1 03 09 2C B1 03 06 FF FF 09 98 85 0B B1
>  83 05 84 09 40 85 0D 75 10 27 FF FF 00 00 67 21
>  D1 F0 00 55 07 B1 03 06 FF FF 09 95 85 0B 75 08
>  26 FF 00 65 00 55 00 B1 03 05 84 09 57 85 09 75
>  20 15 FF 27 FF FF FF 7F 66 01 10 B1 82 09 56 85
>  0A B1 82 05 85 09 83 85 0C 75 08 15 00 26 FF 00
>  65 00 B1 03 05 84 09 1F 85 0B B1 03 05 85 09 67
>  85 0C B1 03 09 89 85 10 B1 03 05 84 09 FD B1 03
>  06 FF FF 09 F0 B1 03 05 85 09 8F B1 03 06 FF FF
>  09 F3 B1 03 05 84 09 FE B1 03 06 FF FF 09 F4 B1
>  03 05 84 09 FF B1 03 06 FF FF 09 F1 B1 03 09 94
>  85 07 B1 83 05 84 09 35 B1 83 09 25 85 0B B1 03
>  09 02 A1 02 05 85 09 D0 85 01 B1 83 09 D0 81 83
>  09 42 B1 83 09 42 81 83 09 44 B1 83 09 44 81 83
>  05 84 09 73 85 03 B1 83 09 73 81 83 06 FF FF 09
>  2E B1 83 09 2D 85 01 B1 83 09 2D 81 83 05 85 09
>  45 B1 83 09 45 81 83 06 FF FF 09 68 85 03 B1 83
>  09 68 81 83 09 77 B1 83 09 77 81 83 05 84 09 61
>  85 01 B1 83 09 61 81 83 09 62 85 02 B1 83 09 62
>  81 83 05 85 09 4B B1 83 09 4B 81 83 05 84 09 65
>  B1 83 09 65 81 83 09 67 85 03 B1 83 09 67 81 83
>  09 69 85 02 B1 83 09 69 81 83 09 6C 85 05 B1 82
>  09 6C 81 82 06 FF FF 09 AE 85 02 B1 83 09 AE 81
>  83 C0 05 85 09 66 85 06 B1 83 09 66 81 83 09 29
>  85 08 B1 83 06 FF FF 09 4D 85 12 B1 82 05 85 09
>  2A 85 17 75 10 27 FF FF 00 00 66 01 10 B1 82 06
>  FF FF 09 5F 85 0E 75 08 26 FF 00 65 00 B1 82 05
>  85 09 68 85 06 75 20 27 FF FF FF 7F 66 01 10 B1
>  83 09 68 81 83 06 FF FF 09 48 85 11 75 08 26 FF
>  00 65 00 B1 82 09 E9 85 07 B1 83 05 84 09 36 75
>  10 27 FF FF 00 00 67 01 00 01 00 B1 83 06 FF FF
>  09 97 85 29 75 20 27 FF FF FF 7F 66 01 10 B1 82
>  09 91 85 07 B1 83 05 84 09 30 75 10 27 FF FF 00
>  00 67 21 D1 F0 00 55 06 B1 83 C0 06 FF FF 09 E5
>  A1 00 C0 C0
> -------- end of 'usbhid-dump -a 7:2' output
>
> Based on this I don't think NUT specifically is at fault, though most
> results from relevant Google searches seem to indicate that this is likely
> a hardware or device firmware issue. Since the USB port on the computer was
> working fine with the Cyberpower UPS I'm suspecting a firmware issue with
> the Eaton. However, it isn't obvious to me that there are updates from
> Eaton's web site.
>
> I tried a few different index values for usb_hid_rep_index and
> usb_hid_ep_in in the hope that might avoid the resource unavailable error.
>
> Does anyone more knowledgeable about NUT than I am have suggestions for me?
>
> Thanks in advance for any help you can provide!
>
> --- Keith
>
>
> ------ start of full upsdrvctl debug output
>    0.000000    [D1] upsdrvctl commanding all drivers (1 found): (null)
>    0.000017    [D1] Starting UPS: Garage-Eaton9PX1500L
>    0.000026    [D1] WARNING: Requested a debugging level but not explicitly a backgrounding mode - driver may never try to fork away; however the upsdrvctl tool will fork it and not wait.
>    0.000031    [D2] 1 remaining attempts
>    0.000036    [D2] exec:  /nix/store/wz0wy2qy7gmj84fnjxp4y3pyy7zvy3b0-nut-2.8.2/bin/usbhid-ups -DDD -a Garage-Eaton9PX1500L -u root
>    0.000249    [D2] Starting driver with debug but without explicit backgrounding: will not wait for it to fork and detach, continuing...
>    0.000277    [D1] upsdrvctl: successfully finished
>    0.000282    [D1] Completed the job of upsdrvctl tool, cleaning up and exiting now
>    0.000290    [D1] Completed the job of upsdrvctl tool, clean-up finished, exiting now
> Network UPS Tools - UPS driver controller 2.8.2
>    0.000000    [D1] upsdrv_makevartable...
>    0.000030    [D1] Using USB implementation: libusb-1.0.27 (API: 0x100010a)
>    0.000072    [D3] do_global_args: var='maxstartdelay' val='45'
>    0.000079    [D3] main_arg: var='driver' val='usbhid-ups'
>    0.000087    [D3] main_arg: var='port' val='auto'
>    0.000092    [D3] main_arg: var='desc' val='UPS for garage systems'
>    0.000096    [D3] main_arg: var='sdorder' val='0'
>    0.000099    [D3] main_arg: var='serial' val='PG00R42NT5'
>    0.000110    [D1] Built-in default or configured user for drivers 'nobody' was ignored due to 'root' specified on command line
>    0.000113    [D1] Network UPS Tools version 2.8.2 (release/snapshot of 2.8.2) built with gcc (GCC) 13.3.0 and configured with flags: --disable-static --disable-dependency-tracking --prefix=/nix/store/wz0wy2qy7gmj84fnjxp4y3pyy7zvy3b0-nut-2.8.2 --with-all --with-ssl --without-powerman --with-systemdsystemunitdir=$(out)/lib/systemd/system --with-systemdshutdowndir=$(out)/lib/systemd/system-shutdown --with-systemdtmpfilesdir=$(out)/lib/tmpfiles.d --with-udev-dir=$(out)/etc/udev
>    0.000122    [D1] debug level is '3'
>    0.001149    [D1] Succeeded to become_user(root): now UID=0 GID=0
>    0.001179    [D1] upsdrv_initups (non-SHUT)...
>    0.001184    [D2] Initializing an USB-connected UPS with library libusb-1.0.27 (API: 0x100010a) (NUT subdriver name='USB communication driver (libusb 1.0)' ver='0.47')
>    0.017847    [D2] Checking device 1 of 14 (1D6B/0003)
>    0.039346    [D1] nut_libusb_open: invalid libusb bus number 0
>    0.039496    [D2] - VendorID: 1d6b
>    0.039500    [D2] - ProductID: 0003
>    0.039503    [D2] - Manufacturer: Linux 6.6.83 xhci-hcd
>    0.039506    [D2] - Product: xHCI Host Controller
>    0.039509    [D2] - Serial Number: 0000:44:00.3
>    0.039512    [D2] - Bus: 008
>    0.039515    [D2] - Bus Port: unknown
>    0.039518    [D2] - Device: 001
>    0.039521    [D2] - Device release number: 0606
>    0.039524    [D2] Trying to match device
>    0.039528    [D2] match_function_subdriver (non-SHUT mode): matching a device...
>    0.039544    [D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
>    0.039548    [D2] Device does not match - skipping
>    0.039673    [D2] Checking device 2 of 14 (0463/FFFF)
>    0.061759    [D2] - VendorID: 0463
>    0.061767    [D2] - ProductID: ffff
>    0.061770    [D2] - Manufacturer: EATON
>    0.061772    [D2] - Product: Eaton 9PX
>    0.061775    [D2] - Serial Number: PG00R42NT5
>    0.061778    [D2] - Bus: 007
>    0.061781    [D2] - Bus Port: 004
>    0.061784    [D2] - Device: 002
>    0.061786    [D2] - Device release number: 0202
>    0.061800    [D2] Trying to match device
>    0.061803    [D2] match_function_subdriver (non-SHUT mode): matching a device...
>    0.061807    [D3] match_function_regex: matching a device...
>    0.061838    [D2] Device matches
>    0.061841    [D2] Reading configuration descriptor 1 of 1
>    0.061849    [D3] libusb_kernel_driver_active() returned 0: Success
>    0.061869    [D2] Claimed interface 0 successfully
>    0.061872    [D3] nut_usb_set_altinterface: skipped libusb_set_interface_alt_setting(udev, 0, 0)
>    0.065784    [D2] Retrieved HID descriptor (expected 9, got 9)
>    0.065794    [D3] HID descriptor, method 1: (9 bytes) => 09 21 10 01 21 01 22 5f 12
>    0.065798    [D3] HID descriptor length (method 1) 4703
>    0.065802    [D3] HID descriptor, method 2: (9 bytes) => 09 21 10 01 21 01 22 84 04
>    0.065815    [D3] HID descriptor length (method 2) 1156
>    0.065818    [D1] Eaton device v2.02. Using full report descriptor
>    0.065822    [D2] Warning: two different HID descriptors retrieved (Reportlen = 4703 vs. 1156)
>    0.065825    [D2] HID descriptor length 4703
>    0.065836    [D2] Unable to get Report descriptor: Resource temporarily unavailable
>    0.065856    [D2] Checking device 3 of 14 (1D6B/0002)
>    0.065877    [D1] nut_libusb_open: invalid libusb bus number 0
>    0.066011    [D2] - VendorID: 1d6b
>    0.066015    [D2] - ProductID: 0002
>    0.066018    [D2] - Manufacturer: Linux 6.6.83 xhci-hcd
>    0.066021    [D2] - Product: xHCI Host Controller
>    0.066023    [D2] - Serial Number: 0000:44:00.3
>    0.066026    [D2] - Bus: 007
>    0.066029    [D2] - Bus Port: unknown
>    0.066032    [D2] - Device: 001
>    0.066035    [D2] - Device release number: 0606
>    0.066038    [D2] Trying to match device
>    0.066041    [D2] match_function_subdriver (non-SHUT mode): matching a device...
>    0.066046    [D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
>    0.066049    [D2] Device does not match - skipping
>    0.066057    [D2] Checking device 4 of 14 (1D6B/0003)
>    0.087349    [D1] nut_libusb_open: invalid libusb bus number 0
>    0.087484    [D2] - VendorID: 1d6b
>    0.087488    [D2] - ProductID: 0003
>    0.087491    [D2] - Manufacturer: Linux 6.6.83 xhci-hcd
>    0.087494    [D2] - Product: xHCI Host Controller
>    0.087497    [D2] - Serial Number: 0000:0b:00.3
>    0.087500    [D2] - Bus: 006
>    0.087503    [D2] - Bus Port: unknown
>    0.087505    [D2] - Device: 001
>    0.087508    [D2] - Device release number: 0606
>    0.087511    [D2] Trying to match device
>    0.087515    [D2] match_function_subdriver (non-SHUT mode): matching a device...
>    0.087520    [D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
>    0.087523    [D2] Device does not match - skipping
>    0.087649    [D2] Checking device 5 of 14 (0D62/2106)
>    0.095541    [D2] - VendorID: 0d62
>    0.095548    [D2] - ProductID: 2106
>    0.095551    [D2] - Manufacturer: unknown
>    0.095554    [D2] - Product: USB Multimedia Keyboard
>    0.095557    [D2] - Serial Number: unknown
>    0.095560    [D2] - Bus: 005
>    0.095563    [D2] - Bus Port: 001
>    0.095565    [D2] - Device: 003
>    0.095568    [D2] - Device release number: 0450
>    0.095571    [D2] Trying to match device
>    0.095574    [D2] match_function_subdriver (non-SHUT mode): matching a device...
>    0.095580    [D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
>    0.095583    [D2] Device does not match - skipping
>    0.095592    [D2] Checking device 6 of 14 (0557/8021)
>    0.095614    [D2] - VendorID: 0557
>    0.095617    [D2] - ProductID: 8021
>    0.095620    [D2] - Manufacturer: unknown
>    0.095623    [D2] - Product: unknown
>    0.095626    [D2] - Serial Number: unknown
>    0.095628    [D2] - Bus: 005
>    0.095631    [D2] - Bus Port: 004
>    0.095634    [D2] - Device: 002
>    0.095637    [D2] - Device release number: 0100
>    0.095639    [D2] Trying to match device
>    0.095643    [D2] match_function_subdriver (non-SHUT mode): matching a device...
>    0.095647    [D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
>    0.095650    [D2] Device does not match - skipping
>    0.095656    [D2] Checking device 7 of 14 (1D6B/0002)
>    0.095671    [D1] nut_libusb_open: invalid libusb bus number 0
>    0.095805    [D2] - VendorID: 1d6b
>    0.095809    [D2] - ProductID: 0002
>    0.095812    [D2] - Manufacturer: Linux 6.6.83 xhci-hcd
>    0.095815    [D2] - Product: xHCI Host Controller
>    0.095817    [D2] - Serial Number: 0000:0b:00.3
>    0.095820    [D2] - Bus: 005
>    0.095823    [D2] - Bus Port: unknown
>    0.095826    [D2] - Device: 001
>    0.095829    [D2] - Device release number: 0606
>    0.095831    [D2] Trying to match device
>    0.095834    [D2] match_function_subdriver (non-SHUT mode): matching a device...
>    0.095839    [D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
>    0.095841    [D2] Device does not match - skipping
>    0.095849    [D2] Checking device 8 of 14 (1D6B/0003)
>    0.117331    [D1] nut_libusb_open: invalid libusb bus number 0
>    0.117475    [D2] - VendorID: 1d6b
>    0.117479    [D2] - ProductID: 0003
>    0.117482    [D2] - Manufacturer: Linux 6.6.83 xhci-hcd
>    0.117485    [D2] - Product: xHCI Host Controller
>    0.117488    [D2] - Serial Number: 0000:08:00.0
>    0.117491    [D2] - Bus: 004
>    0.117494    [D2] - Bus Port: unknown
>    0.117496    [D2] - Device: 001
>    0.117499    [D2] - Device release number: 0606
>    0.117502    [D2] Trying to match device
>    0.117505    [D2] match_function_subdriver (non-SHUT mode): matching a device...
>    0.117511    [D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
>    0.117514    [D2] Device does not match - skipping
>    0.117573    [D2] Checking device 9 of 14 (1D6B/0002)
>    0.117642    [D1] nut_libusb_open: invalid libusb bus number 0
>    0.117766    [D2] - VendorID: 1d6b
>    0.117770    [D2] - ProductID: 0002
>    0.117773    [D2] - Manufacturer: Linux 6.6.83 xhci-hcd
>    0.117776    [D2] - Product: xHCI Host Controller
>    0.117778    [D2] - Serial Number: 0000:08:00.0
>    0.117781    [D2] - Bus: 003
>    0.117784    [D2] - Bus Port: unknown
>    0.117787    [D2] - Device: 001
>    0.117790    [D2] - Device release number: 0606
>    0.117792    [D2] Trying to match device
>    0.117795    [D2] match_function_subdriver (non-SHUT mode): matching a device...
>    0.117800    [D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
>    0.117803    [D2] Device does not match - skipping
>    0.117829    [D2] Checking device 10 of 14 (1D6B/0003)
>    0.139390    [D1] nut_libusb_open: invalid libusb bus number 0
>    0.139525    [D2] - VendorID: 1d6b
>    0.139529    [D2] - ProductID: 0003
>    0.139532    [D2] - Manufacturer: Linux 6.6.83 xhci-hcd
>    0.139535    [D2] - Product: xHCI Host Controller
>    0.139538    [D2] - Serial Number: 0000:01:00.0
>    0.139541    [D2] - Bus: 002
>    0.139544    [D2] - Bus Port: unknown
>    0.139547    [D2] - Device: 001
>    0.139550    [D2] - Device release number: 0606
>    0.139552    [D2] Trying to match device
>    0.139556    [D2] match_function_subdriver (non-SHUT mode): matching a device...
>    0.139561    [D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
>    0.139564    [D2] Device does not match - skipping
>    0.139699    [D2] Checking device 11 of 14 (1050/0407)
>    0.150000    [D2] - VendorID: 1050
>    0.150008    [D2] - ProductID: 0407
>    0.150011    [D2] - Manufacturer: Yubico
>    0.150014    [D2] - Product: YubiKey OTP+FIDO+CCID
>    0.150017    [D2] - Serial Number: unknown
>    0.150019    [D2] - Bus: 001
>    0.150022    [D2] - Bus Port: 006
>    0.150025    [D2] - Device: 003
>    0.150028    [D2] - Device release number: 0512
>    0.150030    [D2] Trying to match device
>    0.150034    [D2] match_function_subdriver (non-SHUT mode): matching a device...
>    0.150039    [D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
>    0.150042    [D2] Device does not match - skipping
>    0.150051    [D2] Checking device 12 of 14 (0B05/1868)
>    0.248019    [D2] - VendorID: 0b05
>    0.248027    [D2] - ProductID: 1868
>    0.248030    [D2] - Manufacturer: unknown
>    0.248033    [D2] - Product: unknown
>    0.248036    [D2] - Serial Number: unknown
>    0.248038    [D2] - Bus: 001
>    0.248041    [D2] - Bus Port: 002
>    0.248044    [D2] - Device: 002
>    0.248047    [D2] - Device release number: 0001
>    0.248050    [D2] Trying to match device
>    0.248053    [D2] match_function_subdriver (non-SHUT mode): matching a device...
>    0.248059    [D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
>    0.248062    [D2] Device does not match - skipping
>    0.248071    [D2] Checking device 13 of 14 (0B05/1867)
>    0.265047    [D2] - VendorID: 0b05
>    0.265055    [D2] - ProductID: 1867
>    0.265058    [D2] - Manufacturer: AsusTek Computer Inc.
>    0.265061    [D2] - Product: AURA Custom Human interface
>    0.265063    [D2] - Serial Number: 00000000001A
>    0.265066    [D2] - Bus: 001
>    0.265069    [D2] - Bus Port: 011
>    0.265072    [D2] - Device: 004
>    0.265075    [D2] - Device release number: 0200
>    0.265077    [D2] Trying to match device
>    0.265081    [D2] match_function_subdriver (non-SHUT mode): matching a device...
>    0.265093    [D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
>    0.265096    [D2] Device does not match - skipping
>    0.265105    [D2] Checking device 14 of 14 (1D6B/0002)
>    0.265126    [D1] nut_libusb_open: invalid libusb bus number 0
>    0.265302    [D2] - VendorID: 1d6b
>    0.265307    [D2] - ProductID: 0002
>    0.265310    [D2] - Manufacturer: Linux 6.6.83 xhci-hcd
>    0.265313    [D2] - Product: xHCI Host Controller
>    0.265315    [D2] - Serial Number: 0000:01:00.0
>    0.265318    [D2] - Bus: 001
>    0.265321    [D2] - Bus Port: unknown
>    0.265324    [D2] - Device: 001
>    0.265327    [D2] - Device release number: 0606
>    0.265329    [D2] Trying to match device
>    0.265332    [D2] match_function_subdriver (non-SHUT mode): matching a device...
>    0.265337    [D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
>    0.265340    [D2] Device does not match - skipping
>    0.265348    [D2] libusb1: No appropriate HID device found
> Network UPS Tools - Generic HID driver 0.53 (2.8.2)
> USB communication driver (libusb 1.0) 0.47
>    0.265353    libusb1: Could not open any HID devices: insufficient permissions on everything
>    0.265356    No matching HID UPS found
>    0.265365    upsnotify: notify about state 4 with libsystemd: was requested, but not running as a service unit now, will not spam more about it
>    0.265370    upsnotify: failed to notify about state 4: no notification tech defined, will not spam more about it
> ------ end of full upsdrvctl debug output
>
> _______________________________________________
> Nut-upsuser mailing list
> Nut-upsuser at alioth-lists.debian.net
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20250325/ca4d0b67/attachment-0001.htm>
    
    
More information about the Nut-upsuser
mailing list